Why Ground Split Phase Residential?

  • Thread starter Thread starter Averagesupernova
  • Start date Start date
  • Tags Tags
    Ground Phase Split
Click For Summary

Discussion Overview

The discussion centers on the grounding of electrical systems, particularly the practice of grounding the neutral at the transformer in residential settings. Participants explore the implications of grounding for safety, fault conditions, and the potential dangers of ungrounded or improperly grounded systems. The conversation touches on various grounding methods, including the use of driven ground rods and concrete-encased electrodes, as well as the risks associated with floating systems.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • Some participants argue that solidly earthing the transformer's secondary is crucial for safety, as it ensures that primary fault currents can flow to Earth, preventing high voltages from entering homes.
  • Others highlight the importance of maintaining a proper grounding connection to prevent loss of continuity, especially in cases where plumbing systems are altered.
  • There is mention of the increasing use of concrete-encased electrodes as a primary grounding method in new constructions.
  • Concerns are raised about the dangers of a floating system, where an Earth fault could lead to dangerous voltage levels on the ungrounded side.
  • Some participants question the potential hazards associated with fault currents traveling back to substations and the effects on the environment, such as impacts on soil organisms.
  • One participant shares a personal anecdote about the dangers of live power lines and the risks of electric shock when near them.

Areas of Agreement / Disagreement

Participants express a range of views on grounding practices, with some supporting the necessity of grounding while others raise concerns about specific methods and potential risks. There is no consensus on the best approach to grounding or the implications of various systems.

Contextual Notes

Participants note limitations in grounding practices, such as the reliance on specific materials (e.g., plastic pipes) and the potential for changes in infrastructure to affect grounding effectiveness. The discussion also reflects a variety of local codes and practices that may influence grounding methods.

Averagesupernova
Science Advisor
Gold Member
Messages
4,894
Reaction score
1,556
http://forums.mikeholt.com/showthread.php?t=162981

I thought this would be a link worth sharing here on pf. We seem to have heated arguments going on this forum from time to time about which country has the best electrical system. There are some interesting things to read in the above link. I do not post nor am I a member on mikeholt.
 
Last edited by a moderator:
Engineering news on Phys.org
Interesting discussion there. I'm not a member at Mike Holt either , but i do like his explanations of code and have occasionally quoted him .

I didn't see in it though what i believe is the reason we Earth the house side neutral at the pole:

Should a fault connect the transformer's primary(several KV) to its secondary(240V) you want something to disconnect primary power, else you'll have kilovolts floating around inside a residence that's only insulated for hundreds not thousands of volts.
That fault might be a broken primary distribution wire falling onto a secondary
or it might be a transformer internal fault
or it might be a neighborhood cat who got across the terminals while investigating a bird's nest up there.

Solidly earthing the transformer's secondary assures that should it get a dose of several KV from primary side a lot of primary current will flow into Earth opening a primary side fuse, which removes those kilovolts from inside your home.
The reason primary current will flow to Earth is:
the substation transformer feeding the primary line is also earthed back at the substation. So primary fault current flows into Earth and back toward the substation without having to enter your house.

That's why it is important to call the electric company when neighborhood urchins steal that copper wire coming down your pole. It goes from the top where it ties into transformer secondary centertap all the way to bottom of the pole where it's wound into a spiral for good Earth contact. It does double duty - it's also a lightning rod.
If it's not there primary voltage and lightning can get to your house.

I looked for a photo of a pole bottom, to no avail. Take note of next pole you see on a truck - bottom end has that coil of earthing wire.
good pictures here, though
http://science.howstuffworks.com/environmental/energy/power9.htm

power-parts.gif


power-ground.jpg


That little bare wire coming down the pole is more important than you might think. Keep an eye on yours.
old jim
 
Last edited:
Was doing some work (residential) the other day, and some ones main ground from the panel wasn't going to the main water shutoff of their house (only determined because house was undergoing major renovations and it was accessible). It was connected to a random part of the water line which is against code, since if any part of the water pipes are removed you lose your main ground, for the reasons that Jim illustrated (you lose continuity to that bare ground wire coming down the pole)
 
With more and more water companies going to plastic pipe...
I like a driven ground rod .
 
The big deal now seems to be concrete encased electrodes for the main ground. I am coming up to speed on a new house construction these days and that is the only ground required at the building.
-
Back to the main discussion about a grounded system vs. a completely isolated system, it was mentioned in the link that it is impossible to guarantee that all parts of a large system will always remain isolated. Jim Hardy, your example of primary to secondary shorts is a perfect example of this that would have horrible consequences.
 
No one on this thread seems to have mentioned the danger, without a centre earth, that an Earth fault on one side will suddenly double the volts on the other side (assuming they were floating fairly symmetrically about Earth potential to start with). It's clearly a good idea to avoid a floating system, in any case. You could imagine all sorts of nasty high volts situations when there are capacitors and switches involved.
 
sophiecentaur said:
No one on this thread seems to have mentioned the danger, without a centre earth, that an Earth fault on one side will suddenly double the volts on the other side (assuming they were floating fairly symmetrically about Earth potential to start with). It's clearly a good idea to avoid a floating system, in any case. You could imagine all sorts of nasty high volts situations when there are capacitors and switches involved.

Didn't think it was necessary to repeat what was already said in the link I provided.
 
The reason primary current will flow to Earth is:
the substation transformer feeding the primary line is also earthed back at the substation. So primary fault current flows into Earth and back toward the substation without having to enter your house.


Are there dangers/accidents that can occur from this current as it flows along a path back to the substation?
Is it possible for the current to travel along other paths on the way? Doesn't something get toasted along the way? worms, etc?
 
foolios said:
The reason primary current will flow to Earth is:
the substation transformer feeding the primary line is also earthed back at the substation. So primary fault current flows into Earth and back toward the substation without having to enter your house.


Are there dangers/accidents that can occur from this current as it flows along a path back to the substation?
Is it possible for the current to travel along other paths on the way? Doesn't something get toasted along the way? worms, etc?

Yes. This is why when a person is very near down power lines that are still live you can get shocked just by walking. There is a voltage between your feet. If it is imperative that you move you are supposed to hop with both feet close together or run in such a way so that only one foot is on the ground at a time. Realize this raises the risk of tripping or falling which could give you a shock hand to foot.
-
As far as the worms go, I have pulled nightcrawlers (large earthworms used for fishing) out of the ground in this manner. They don't like it and come to the top.
 
  • #10
thank u for the explanations
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
Replies
7
Views
3K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 13 ·
Replies
13
Views
7K
Replies
12
Views
5K
  • · Replies 4 ·
Replies
4
Views
4K
Replies
47
Views
11K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 16 ·
Replies
16
Views
4K