480V Split phase / 400V Threephase (AUS)

In summary: The double delta and high delta produce perfect voltage and phase for household use. They are also very difficult to wire if you don't know exactly which coil is which. Many exciter circuits will not work with them either. Worse of all, they won't work with a 6-wire generator. The final configuration is called a zig-zag, and is most commonly used when residential 120v/240v is needed from a 3-phase generator.
  • #1
Tomu
5
0
HI there,

First post here, I hope I can get out into the forum and provide some answers to you in the future.

I am an Electrician here In Australia and spent my career so far in Industrial.

Currently I have a job which is putting me to the test so I thought someone might be able to offer some advice to me.

The situation:
A customer who is a Hydroponic farmer currently has "2 Phase" "Split phase" (480V) Whichever you like to call it. Three phase isn't available as it's in a rural area and the power is coming in via a SWER line.

He has approx 12Kw of pumps on one of the phases + House. The other phase has the processing machinery (only runs 3 Days a week) and refrigeration,

He approached me to install a three phase generator with auto start on the farm.

I can see installing a 2 phase Genny will come up, But they are expensive compared to a three phase here as 2 phase isn't common at all these days.
So My question for the EE forum so I can proceed with how to design this is.

1 - Is having unbalanced Phases on a generator detrimental to the life of it (30-40kVA)

2- If each phase has to be balanced, How close can they be. ~10-15%

3- What is an acceptable startup current ( imagine 10 Pumps firing up at once)

4- If I need to balance the load out, As processing happens only three times per week, + 1 phase won't even be connected. What can I use- IE just go run a few big resistors to "waste" the power?
Please fell free to ask for more information!
Thanks
 
Engineering news on Phys.org
  • #2
Tomu said:
A customer who is a Hydroponic farmer currently has "2 Phase" "Split phase" (480V) Whichever you like to call it. Three phase isn't available as it's in a rural area and the power is coming in via a SWER line.

He has approx 12Kw of pumps on one of the phases + House. The other phase has the processing machinery (only runs 3 Days a week) and refrigeration,

SWER ?
Single Wire Earth Return (SWER) ?

i guess i don't understand the concept of two phases on as single wire.
 
  • #3
Hi,

Its a 3 wire system. The transformer is centre tapped.

like this.

https://upload.wikimedia.org/wikipedia/en/2/29/Split_phase2.png
 
  • #4
So you want to run a 3 phase generator to supply a split-phase facility. I believe it is done frequently. Are you familiar with a zigzag or double delta connection?
http://www.marathonelectric.com/generators/docs/manuals/SB504.pdf

<Moderator's note: fixed link>
 
Last edited by a moderator:
  • Like
Likes jim hardy
  • #5
I have never heard of either. But I can get a bit of an idea from the link you provided to me. Do you have any experience in doing this?
 
  • #6
I have never made this connection. I have faith though. :smile: The problem you have will be the power derating. You need to size the generator considerably larger than you would for true 3 phase loads. Asking to start 12 HP worth of pumps with a generator is a tough deal to begin with. A good utility will start a 12.5 HP motor with ease but making your own power is always a compromise.
 
  • #7
I'm going to have to break into the circuit and split it with a few contactors and Timers from the PLC.

If I don't need the Potential difference of 480, So Can I use two out of the three phases from the generator? Or do they need to be balanced.
 
Last edited:
  • #8
I would try to better balance it by using the double delta or zigzag. Of course these are not truly balanced but it is better than letting one phase idle. Voltage regulation may be an issue if you let a phase idle. Best to ask the manufacturer of the generator.
 
  • #9
here's a hobbyist's description of doing the ziz-zag
http://www.anoldman.com/strange/re-wiring_a_three_phase_generator
three_to_single_phase.jpg
 
  • #10
So here in Aus, I take it that wiring it like this will give me 240/480?
 
  • #11
Wiring it like what?
 
  • #12
Tomu said:
So here in Aus, I take it that wiring it like this will give me 240/480?

it's exactly same as in the generator manual that Averagesupernova linked to

i never trust that anybody's wire numbering scheme is "standard"

"anoldman" gives a decent tutorial here on why it works
before undertaking it i'd make sure of wire numbers ,, observe his precaution below
http://www.anoldman.com/power_systems/understanding_how_generators_work
The double delta and high delta produce perfect voltage and phase for household use. They are also very difficult to wire if you don't know exactly which coil is which. Many exciter circuits will not work with them either. Worse of all, they won't work with a 6-wire generator. The final configuration is called a zig-zag, and is most commonly used when residential 120v/240v is needed from a 3-phase generator:
...
The hardest part of re-configuring a generator like we've seen above is figuring out which of the wires coming out of the generator head are connected to which coils. Without a manufacturer's documents, your best bet is determining how the generator is currently wired and working backwards from there.

i've never done it , just stumbled across this hobbyist site and thought "That makes sense! "

old jim
 
  • #13
You now have SWER. It is isolated with the transformer to 480VAC split with a centre tap. That provides a neutral and two opposite phases of 240VAC. You can run single phase 240VAC equipment between the neutral and one side of the transformer. You only need both sides if you need more power than is available from one side, or you run a big "two-phase welder". There should be no need to balance the two phases unless power use is above 50%.

A three phase generator with a neutral (earthed) connection obeys the same rules of load sharing. You need to allocate load to three active phases, but do not need to balance load unless you exceed 33% per phase. That does not mean you should not balance when you can. You should not waste energy with dummy loads.

The question then becomes, how do you select subsets of circuits that can be allocated to either a 2 or 3 phase system. The best answer is probably that the change over circuit will switch up to six load circuits. When on the SWER the contactors will balance 3 circuits to each of the 2 phases. When on the 3PH alternator the contactors will allocate 2 circuits to each of 3 available phases. You can use a pair of 3PH contactors to do the changeover.

P.S. For about a decade now, Australia has been standardised on 230VAC, but the voltage does not seem to have changed at my end yet.
 

1. What is the difference between 480V split phase and 400V three phase in Australia?

The main difference between 480V split phase and 400V three phase in Australia is the voltage level. 480V split phase is a single-phase system with a voltage of 480 volts, while 400V three phase is a three-phase system with a voltage of 400 volts. Additionally, split phase systems have two live wires and one neutral wire, while three phase systems have three live wires and one neutral wire.

2. How do the power distribution systems for 480V split phase and 400V three phase differ?

The power distribution systems for 480V split phase and 400V three phase differ in terms of the number of phases and voltage levels. 480V split phase systems typically have one transformer per building or unit, while 400V three phase systems have one transformer per neighborhood or industrial area. This allows for more efficient distribution of power in three phase systems.

3. Which type of power system is more commonly used in Australia?

In Australia, 400V three phase power systems are more commonly used. This is because three phase systems are more efficient and cost-effective for industrial and commercial applications, which make up a large portion of Australia's energy demand.

4. What are the advantages of using 480V split phase over 400V three phase?

The main advantage of using 480V split phase is that it is more cost-effective for smaller residential or light commercial applications. It also allows for easier installation and maintenance since it only requires two live wires instead of three. However, it is not as efficient for larger industrial applications compared to 400V three phase systems.

5. Are there any safety concerns with using either 480V split phase or 400V three phase?

Both 480V split phase and 400V three phase systems have safety concerns that need to be taken into consideration. These include arc flash hazards, the potential for electric shock, and the need for proper grounding and overcurrent protection. It is important to follow all safety regulations and guidelines when working with either type of power system.

Similar threads

Replies
7
Views
1K
  • Electrical Engineering
Replies
17
Views
2K
Replies
19
Views
2K
  • Electrical Engineering
Replies
1
Views
263
Replies
14
Views
5K
  • Electrical Engineering
Replies
5
Views
7K
  • Electrical Engineering
Replies
26
Views
2K
  • Electrical Engineering
Replies
7
Views
2K
Replies
8
Views
984
Replies
1
Views
652
Back
Top