Working out power loss in power lines: Multiple wires

AI Thread Summary
The discussion revolves around calculating power loss in power lines with various wire combinations. Participants clarify the differences between series and parallel configurations, emphasizing that current remains the same in series but divides in parallel. For example, using two Merlins in parallel reduces the current through each wire, leading to lower power loss. The calculations for power loss involve using the formula Ploss = I²R, with participants correcting each other's misunderstandings about current distribution and resistance. Ultimately, the focus is on accurately determining the maximum power loss per kilometer for different wire combinations.
Roynish
Messages
7
Reaction score
0
Hey everyone,

This is quite a simple question, I think I'm just getting confused.

1. Homework Statement

Given Data:
Merlin: Resistance: 2 Ω / km, Maximum Current: 519
Pelican: Resistance: 1.5Ω/km, Maximum Current: 646
Penguin: Resistance: 4 Ω/km, Maximum Current: 357
Sparrow: Resistance: 11Ω/km, Maximum Current: 184
Swan: Resistance: 17Ω/km, Maximum Current: 140
Note: Maximum current that will pass through the wire is 360 A
State the maximum power loss per km for 10 possible combinations of wires.

Homework Equations


Ploss=I²R
Total Resistance = 1/{(1/R1)+(1/R2)+(1/R3)..+(1/Rn)}

The Attempt at a Solution


I'm not sure how current is divided up depending on the combination of wires.
First I tried to do 2x Merlin in parallel
Current is the same in components in parallel so:
Rtotal: (1/2 + 1/2)^-1 = 1
Ploss= I²R
= (360)^2
= 129600
Total Power loss; 129600x2= 259200 W
This is the same as just figuring out Merlin x1. Would I divide the current by 2 if I did 2x Merlin in series?
Also say I tried doing:
1x swan, 1x sparrow, 1x penguin
I have no idea what to do with currents. Add them together? Divide them up?Thanks for your help.
 
Physics news on Phys.org
Hello Roy, welcome to PF :smile: !

For parallel wires, you know that the voltage is the same for each of the two. Uncle Ohm's law gives you the current ratios.

For two Merlins in parallel that means each of the wires carries only 180 Amps ! A lot less max power loss, therefore.[edit] Ah, now I see: combinations in this exercise means parallel combimations !
 
BvU said:
For two Merlins in parallel that means each of the wires carries only 180 Amps ! A lot less max power loss, therefore.

Oh! I thought current is the same in parallel rather than series, sorry my mistake.
BvU said:
Ah, now I see: combinations in this exercise means parallel combimations !
Not necessarily I think. It can be in series.
So: Say I did 1x swan, 1x penguin in series.
Total Resistance: 17+4 = 21 ohms
Current: 360 A
Power loss: I²R
360 x 21
= 7560 Watts
Is this correct? I did not surpass the amount of maximum amount of current for each wire because together they can take a maximum current of 497. Is that correct? ie. if I have 2 wires in series with different max currents do I add them together to get the overall maximum current?
Sorry for the bother!

Thanks for the welcome ^_^

Edit: This is all per km of course
 
Roynish said:
Oh! I thought current is the same in parallel rather than series, sorry my mistake.
From the above statement, if seems that you can answer your own question below.
... ie. if I have 2 wires in series with different max currents do I add them together to get the overall maximum current?
 
So: Say I did 1x swan, 1x penguin in series.
Total Resistance: 17+4 = 21 ohms
Current: 360 A
Swan maximum is 140A, this must not be exceeded
 
NascentOxygen said:
Swam maximum is 140A, this must not be exceeded

oh? I thought that if I put it in series with penguin there will be a net maximum current of 140 + 357(penguin's max currrent) = 497 A

SammyS said:
From the above statement, if seems that you can answer your own question below.

So if current is the same in each point in the series circuit...the overall max current should be the sum of the two wires' max currents...I assume...
I feel like I'm missing something here
 
In a series circuit the same current passes through each, just as water pipes in series carry the same water flow.
 
NascentOxygen said:
In a series circuit the same current passes through each, just as water pipes in series carry the same water flow.

Okay, so the maximum current is different but the current flowing through each wire is the same. Gotcha. Okay say if I instead put Merlin in parallel with say pelican maybe I would not exceed the maximum current if current is split. How would I work out the current flowing through Merlin and in turn pelican? Extra information that probably will be helpful: 330, 000 V is supplied, may use up to 120 MW of power. These are the values I used to get the maximum current running through the wire. (I=P/V, 120 000 000/330 000= 363.6, simplified to 2 sig. figures; 360 A)
Attempt:
Current through Merlin: I = V/R
=330, 000/2
=165 000 A
Obviously this is wrong. Maybe I can use another formula: I = √PR
120 000 000 x 2 = 240 000 000
√240 000 000= 15491.93338
Obviously this is wrong as well. I'm just confusing myself even more now. This is something to do with the resistance since I didn't use resistance to work out the initial maximum current I think.
 
Last edited:
Roynish said:
I think. It can be in series.
So: Say I did 1x swan, 1x penguin in series.
Total Resistance: 17+4 = 21 ohms
Current: 360 A
Power loss: I²R
360 x 21
= 7560 Watts
Is this correct?
Did you forget the 'squared' current? This would be the loss per 2km, so you'll probably express it as per km.

Are you sure you can use Swan in series with Penguin? It won't meet the 360A specification, if I'm reading this correctly.
 
  • #10
The 300kV goes mostly to the distant load, whatever it is, and is not 'used up' by the resistance in these cables. So you don't use that figure to calculate a cable's power losses.

When you have two cables in parallel, their voltage is common, so currents are
I = I1 + I2 = V/R1 + V/R2

and the current sharing can be expressed
∴ I1 / I2 = R2 / R1
 
  • #11
NascentOxygen said:
Did you forget the 'squared' current? This would be the loss per 2km, so you'll probably express it as per km.

Sorry I forget to square it. So the answer would actually be 2721600 Watts. This is per 2km so I divide it by two; 1360800 W/km.

NascentOxygen said:
Are you sure you can use Swan in series with Penguin? It won't meet the 360A specification, if I'm reading this correctly.

Yes that's correct. I'm wrong.

NascentOxygen said:
The 300kV goes mostly to the distant load, whatever it is, and is not 'used up' by these cables. So you don't use that figure to calculate cable power losses.

When you have two cables in parallel, their voltage is common, so currents are
I = I1 + I2 = V/R1 + V/R2

and the current sharing can be expressed
∴ I1 / I2 = R2 / R1

Wow thanks. So can I use the current divider rule: R1 current: Itotal * R2/(R1+R2)??
So again: Merlin in parallel to pelican
Current through Merlin:
360 x 2 / (1.5+2)
=154.3
WHEW it works! Doesn't overcome mass current
SO: Total power loss
I²R Total Resistance: (1/2 +1/1.5)^-1
=6/7
(360)^2 x 6/7
=111085.72
For per km divide by 2:
55542.86 W/km
I hope that's correct.
 
Last edited:
  • #12
I doubt that final divde by 2. Probably leave it as per km of paralleled cable.
 
  • #13
NascentOxygen said:
I doubt that final divde by 2. Probably leave it as per km of paralleled cable.
Okay thank you so much.

Edit: I have to put this on a graph cost per km (data is given) vs power loss per Km. Do I still leave it as power loss per km of paralleled cable or for the sake of comparison change it?
 
Last edited:
  • #14
Roynish said:
Edit: I have to put this on a graph cost per km (data is given) vs power loss per Km. Do I still leave it as power loss per km of paralleled cable or for the sake of comparison change it?
I would leave it as per km of parallelled cable, but it's just a scaling factor so shouldn't complicate comparisons.
 
  • #15
Okay. Will do. Thanks!
 