Calculate valve sizing to regulate the flow of natural gas

In summary, the conversation discusses various calculations related to working out and specifically focuses on the equations for x, Fk, xT, and Y. It is determined that the flow through the valve is choked when xT is less than x, and the expansion factor Y is calculated to be 0.623. However, due to the choked flow, a value of 2/3 or 0.667 is used instead. The conversation also mentions the need to find the value for Qm, which is the mass flow rate, in order to incorporate it into the equation for finding the valve flow coefficient.
  • #1
clh99
5
0
Homework Statement
I have the question
A valve is required to regulate the flow of natural gas. Details of the gas are given in table below. It can be assumed that the pipe size and the valve size are the same [i.e. piping geometry does not have to be allowed for].

The chosen valve type is the V250 rotary ball valve by Fisher Controls International [the V250 data sheet is available on Blackboard].

Determine the required valve size in inches from the range of sizes given in the data sheet [the data sheet gives a range of nominal pipe sizes (NPS) in inches].

Estimate the percentage the chosen valve would have to be open to carry the required flow.

Required volumetric flow rate ( at STP) 2.8x10^6 litres per min
Density (at stp) 0.752 kg per m^3
specific heat ratio 1.31
inlet pressure 20bar
outlet pressure 6 bar
inlet temperature 20 degrees Celsius
Relevant Equations
Cv = alternative flow coefficient (gallons/min)
Kv = flow coefficient (M^3h^-1)
Y = expansion factor
Qm = mass flow rate (kg/hour)
xT = critical pressure differential ratio
x = pressure differential ratio
Fl= liquid pressure recovery coefficient
Fk = specific hear ratio factor
k = specific heat ratio

x=(p1-p2)/p1

xT = Fk * x

xT < x

Y = 1 - x/( 3 x Fk x xT )

Kv= Qm / ((2/3) x 31.6 x √ Fk x xT x P1 x p1)
Working out as follows

x= (20-6)/20 = 0.7

Fk = k / air specific heat ratio

Fk = 1.31/1.4
Fk = 0.94

xT = Fk * x
0.94 x 0.7 = 0.658

because xT < x = 0.658<0.7 flow through the valve is choked

Expansion factor Y

Y = 1 - x/( 3 x Fk x xT )

Y= 1- 0.7/( 3 x 0.94 x 0.658)

Y = 0.623

Although this is the expansion factor because the flow is choked a value of 2/3 or 0.667 is used.

I am now struggling to kind a value for Qm which is mass flow rate. I believe once i have this value i can then incorporate it into Kv= Qm / ((2/3) x 31.6 x √ Fk x xT x P1 x p1) to find the valve flow coefficient
 
Last edited by a moderator:
Physics news on Phys.org
  • #2
Hi, where did you get the calculation for xT from?
 

1. How do you calculate the valve sizing for natural gas flow regulation?

The valve sizing for natural gas flow regulation can be calculated using the following formula:
Valve Sizing = (Flow Rate x Specific Gravity) / (Cv x Pressure Drop)

2. What is the purpose of valve sizing in regulating natural gas flow?

The purpose of valve sizing is to ensure that the valve is able to handle the desired flow rate of natural gas while maintaining a specific pressure drop. This helps to regulate the flow and prevent any potential damage to the system.

3. How does specific gravity affect valve sizing for natural gas flow regulation?

Specific gravity is the ratio of the density of a substance to the density of a reference substance. In the context of valve sizing for natural gas flow regulation, it is used to account for the varying density of natural gas at different pressures and temperatures. A higher specific gravity will result in a larger valve size being required to achieve the desired flow rate.

4. What is Cv and how does it impact valve sizing for natural gas flow regulation?

Cv, or flow coefficient, is a measure of the valve's ability to control the flow of fluid. It is a standardized value that takes into account the valve size, shape, and flow characteristics. A higher Cv value indicates a larger flow rate for a given pressure drop, and therefore a smaller valve size may be needed for the desired flow rate.

5. Are there any other factors that should be considered when calculating valve sizing for natural gas flow regulation?

In addition to flow rate, specific gravity, and Cv, other factors that should be considered include the type of valve (e.g. globe, ball, butterfly), the material and size of the valve, and the operating conditions (e.g. pressure, temperature). It is important to carefully consider all of these factors to ensure accurate valve sizing and proper regulation of natural gas flow.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
1
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
2K
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
3K
  • Mechanical Engineering
Replies
3
Views
959
  • Engineering and Comp Sci Homework Help
Replies
8
Views
5K
  • Mechanical Engineering
Replies
4
Views
19K
Replies
2
Views
2K