Power Distribution Design -- why did the person get shocked?

In summary, the electrical connection diagram of the equipment suggests that there may be a higher voltage present on the construction pedestal than what is documented in the installation drawings. Additionally, the ground rod resistance of the equipment may be low due to a lack of connection between the enclosure and the ground.
  • #1
Derill03
63
0
Hello I am an electrical engineer freshly out of school and i was wondering if anyone could help me reach an answer to this design problem. I am attempting this problem solely for personal knowledge because in school I never took a course on distribution design. I found this problem looking around on google but honestly did not find much more information that seemed relevant. Any help would be appreciated.
You are sent to investigate an incident where someone received a shock from a construction pedestal in

a nearby new underground residential construction area. The area is served at 12.47/7.2 kV primary

underground. The location you are asked to look at has a 50 kVA padmount transformer supplying a

hand hole that has three - three connector bus bars. The transformer is a standard 120/240 low side

center tapped (grounded) connection.

Given:

There is only a temporary metered construction pedestal connected to the hand hole and has three

outlets (GFCI protected) to allow for both 120 volt and 240 volt hand tools and construction power to

the residential home being built there. Two outlets are 120 volts and one is 240 volts. The pedestal has

an installed 5/8” x 8’ ground rod (copper weld) to ground the metal pedestal enclosure.

The shock happened when the person touched the open metal lid on the pedestal after switching the

hand tool plug locations. An offhand comment by someone noted that in using hand tools on the job

site, one outlet seemed to make the tools run much faster.

To Do:

1. Clearly show the electrical connection diagram of what you think happened at the pedestal to

provide the voltage needed for an electric shock? Please draw on a separate piece of paper.

2. What voltage to ground would be present?

3. If the electrical resistivity of the soil at a nearby substation location was measured at 50 ohm-
meters what is the calculated ground rod resistance at the pedestal?
 
Physics news on Phys.org
  • #2
Derill03 said:
Hello I am an electrical engineer freshly out of school and i was wondering if anyone could help me reach an answer to this design problem. I am attempting this problem solely for personal knowledge because in school I never took a course on distribution design. I found this problem looking around on google but honestly did not find much more information that seemed relevant. Any help would be appreciated.
You are sent to investigate an incident where someone received a shock from a construction pedestal in

a nearby new underground residential construction area. The area is served at 12.47/7.2 kV primary

underground. The location you are asked to look at has a 50 kVA padmount transformer supplying a

hand hole that has three - three connector bus bars. The transformer is a standard 120/240 low side

center tapped (grounded) connection.

Given:

There is only a temporary metered construction pedestal connected to the hand hole and has three

outlets (GFCI protected) to allow for both 120 volt and 240 volt hand tools and construction power to

the residential home being built there. Two outlets are 120 volts and one is 240 volts. The pedestal has

an installed 5/8” x 8’ ground rod (copper weld) to ground the metal pedestal enclosure.

The shock happened when the person touched the open metal lid on the pedestal after switching the

hand tool plug locations. An offhand comment by someone noted that in using hand tools on the job

site, one outlet seemed to make the tools run much faster.

To Do:

1. Clearly show the electrical connection diagram of what you think happened at the pedestal to

provide the voltage needed for an electric shock? Please draw on a separate piece of paper.

2. What voltage to ground would be present?

3. If the electrical resistivity of the soil at a nearby substation location was measured at 50 ohm-
meters what is the calculated ground rod resistance at the pedestal?

Please show us your work on this problem so far...
 
  • #3
So far i have deduced that the voltage is somehow higher than 120 in one of the 2 outlets or higher than 240 in the single 240 outlet, it does not specify which outlet the person switched to when he was shocked. So my thoughts so far lead me to believe one of the outlets is wired wrong and giving a higher voltage (hence the clue of the tools running faster).
 
  • #4
I think part 3 should be about 19.94 ohm using formula R= Ro/6.283L*(ln(8L/d)-1).

Unsure how to calculate part 2 at this point still.
 
  • #5
  • #6
Well so let's say the 120v outlets are wired as 220v ok, that would cause the hand tool to run faster i agree but how could that cause a potential to build-up on the chasis and cause a shock?

Another possibility I've thought of is what if the transformer has a bad ground connection, then the 120v outlets would be at some other potential probably lower than 120v since they are not referenced to 0v any longer, but again how would that cause a shock to occur?

Maybe I am missing something because I am not familiar with the pedestal box they are referring to, i assume its wired just like a house would be.
 
  • #7
Could it be that the ground clamp has came loose or not hooked up? This could pose a shock hazard, and it would cause the transformer to have no center tap.
 
  • #8
Derill03 said:
Could it be that the ground clamp has came loose or not hooked up? This could pose a shock hazard, and it would cause the transformer to have no center tap.
yes that's possible. why don't you draw a schematic to prove it?!
 
  • #9
Ok so if this fault condition were true, it could explain the shock that occured, but it seems if you measured across the 120V outlets you would see about 120V-60V = 60V? Hmm I'm not sure that's correct, i know if the transformer is grounded to CT then you get a +120 and a -120 at 180 deg out of phase from one another across transformer coil but if the CT is not grounded would it show 60V or 120V at its center point? I think it has to be 60V at its center with no CT ground

See attached schematics
 

Attachments

  • Normal.pdf
    12.6 KB · Views: 173
  • Fault.pdf
    13.6 KB · Views: 177
  • #10
Derill03 said:
Ok so if this fault condition were true, it could explain the shock that occured, but it seems if you measured across the 120V outlets you would see about 120V-60V = 60V? Hmm I'm not sure that's correct, i know if the transformer is grounded to CT then you get a +120 and a -120 at 180 deg out of phase from one another across transformer coil but if the CT is not grounded would it show 60V or 120V at its center point? I think it has to be 60V at its center with no CT ground

See attached schematics
Hi, I am thinking the neutral and one of the hot line were interchanged.
 
  • #11
In the case of USA distribution, missing from the diagrams shown here is second ground at the meter / panel at a customer site. There's a ground for the center tap of the step down transformer, and there is a second ground at the meter / panel. Three prong electrical outlets within a customer site also have a ground / Earth connection in addition to the neutral wire, and there can be a slight voltage difference between the neutral and ground wire.
 
Last edited:

1. Why did the person get shocked?

There are several possible reasons why a person may get shocked while dealing with power distribution design. Some common causes include coming into contact with a live wire, faulty or damaged equipment, inadequate grounding, or not following proper safety protocols. It is important to always follow safety guidelines when working with electricity to prevent accidents and injuries.

2. What role does power distribution design play in preventing electrical shocks?

Power distribution design is crucial in preventing electrical shocks by ensuring that electricity is distributed safely and efficiently. This includes designing systems with proper grounding, insulation, and protection devices to prevent electrocution. It is also important to regularly inspect and maintain the power distribution system to identify and fix any potential hazards.

3. Can a person get shocked even if they are not directly in contact with electricity?

Yes, it is possible for a person to get shocked even if they are not in direct contact with electricity. This can occur through indirect contact, such as touching a metal object that is in contact with a live wire. It is important to always assume that any object or surface could potentially be energized and take necessary precautions to prevent shocks.

4. How can a person protect themselves from getting shocked when working with power distribution design?

There are several ways to protect oneself when working with power distribution design. These include wearing appropriate personal protective equipment, following safety protocols and guidelines, properly grounding all equipment, and using insulation and protective devices. It is also important to have a thorough understanding of the system you are working with and to never attempt to work on live circuits.

5. What should a person do if they or someone else gets shocked while working with power distribution design?

If someone gets shocked while working with power distribution design, it is important to act quickly and calmly. The first step is to turn off the power source to the affected area. If this is not possible, use a non-conductive object, such as a wooden stick, to move the person away from the source of electricity. Seek medical attention immediately, even if the shock seems minor. It is also important to report the incident and investigate the cause to prevent future accidents.

Similar threads

Replies
13
Views
4K
  • Electrical Engineering
Replies
1
Views
2K
  • Electrical Engineering
Replies
6
Views
9K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
4
Views
14K
Replies
13
Views
2K
Replies
8
Views
884
  • Other Physics Topics
Replies
10
Views
2K
Replies
5
Views
1K
  • Mechanical Engineering
Replies
4
Views
3K
Back
Top