Selection of multi-pin connector for power lead cables

In summary: There is no need to disconnect the plug with power ON. All phases are the same (230VAC).The disconnection will take place once a week.
  • #1
AligatorAmy
28
1
Hi,
I have 6 cables. Each cable has 3 wires: zero, phase, earth.
Each cable supplies 320W 230VAC heater (I have 6 heaters).

I am looking for 1 multi pin connector for all these cables for quick plug in/out.
Link to example connectors:
https://www.aliexpress.com/cheap/cheap-multi-pin-connectors.html

I wonder how many pins my connector must have. I have 18 wires in 6 cables (6xZero, 6xPhase, 6xEarth).
Does it mean that I need at least 18 pin connector or can I have the Earth wires connected together?

Also I have calculated that each heater draws approx. 1.4A (320W, 230VAC). Therefore, when I multiply 1.4A by 6 heaters my amperage is 8.4A. Sellers state the amperage for the multi pin connector. I understand that this is maximum load that the connector can take?
In my case should I then look for minimum 10A connector?

Please help.
Regards
 
Engineering news on Phys.org
  • #2
AligatorAmy said:
Hi,
I have 6 cables. Each cable has 3 wires: zero, phase, earth.
Each cable supplies 320W 230VAC heater (I have 6 heaters).

I am looking for 1 multi pin connector for all these cables for quick plug in/out.
Link to example connectors:
https://www.aliexpress.com/cheap/cheap-multi-pin-connectors.html

I wonder how many pins my connector must have. I have 18 wires in 6 cables (6xZero, 6xPhase, 6xEarth).
Does it mean that I need at least 18 pin connector or can I have the Earth wires connected together?

Also I have calculated that each heater draws approx. 1.4A (320W, 230VAC). Therefore, when I multiply 1.4A by 6 heaters my amperage is 8.4A. Sellers state the amperage for the multi pin connector. I understand that this is maximum load that the connector can take?
In my case should I then look for minimum 10A connector?

Please help.
Regards
What country are you in? In the US, you would need to consult the NEC (National Electric Code) standard to figure out what the spacings should be between the pins in the connectors, and what size wire you need to use.

How long are the cable runs? Is this in a factory? What building inspections and insurance inspections will be involved in getting this new electrical installation approved?
 
  • #3
One thing to watch out for is Tin plated or solder coated contacts. For some reason, perhaps oxidation, many such contacts have or develop a high resistance connection. This results in poor electrical contact, higher temperature, rapid oxidation/corrosion of the contacts, and failure. If you must use Tin or solder contacts use at least a 60% current derating. Even if this is in an office or home environment or similiar, do not use Tin or solder contacts for any significant current, they fail.
 
  • #4
It's a rather badly specified problem. As far as I can see you may only need three pins on the connector (Phase, Neutral & Earth) and perhaps some junction box(es).

Some C13 IEC connectors (aka Kettle leads) will handle 15A.
http://cpc.farnell.com/c/cable-leads-connectors/connectors/power-connectors/iec-connectors

However that could be totally inappropriate depending on other factors.

Do you want to be able to disconnect the connector with the power ON?
Are all the phases the same phase?
How frequently will it be connected disconnected?
 
  • #5
Is each of the six heaters individually controlled as one of your previous questions suggests they may be?

Several approaches exist each with their own set of pros and cons.
 
  • #6
CWatters said:
Do you want to be able to disconnect the connector with the power ON?

I would suggest avoiding this situation if possible even for live power rated connectors. Even though many mains connectors are often used for connect and disconnect under load it is not an optimal situation. It is just a potentially dangerous historical foible.

BoB
 
  • Like
Likes CWatters
  • #7
Thank you for your answers.
@berkeman
I live in the EU.
Each cable is 5meters long.
This is the factory (production).
Electrician with appropriate certificates is authorised to approve the installation.

@CWatters/Asymptotic
Each heater is controlled individually by the PLC (through feedback from its TCK). Therefore, each heater requires separate wires.
There is no need to disconnect the plug with power ON.
All phases are the same (230VAC).
The disconnection will take place once a week.
 
  • #8
If you are stuck with the 6 separate cables I think it will be difficult to find an 18 pin connector pair to do this job reliably. Mainly because the strain relief on the majority of connectors is intended for one 18 way cable not six 3 way cables. You would probably need to strip the cables and reassemble the 18 individual wires into one 18 way cable using heat shrink sleeving. To do a neat job would require the cables to be disconnected at the heater end to slip the heat shrink over the bundle. Possible but not ideal.

Do both halves of the connector have to be "in-line" or can one be panel mounted? In some connector ranges you can only connect a cable mounted connector to a panel mounted connector, You can't connect cable mounted to cable mounted. If you can disconnect at a panel then that might give you more options.

If you can rewire then speak to the electrician about the number of wires/cores he thinks are needed. I guess it could be as few as 8?...

6 phase
1 Neutral (10A)
1 Earth

In which case perhaps look at the Bulgin Buccaneer Series of connectors which go up to 10 way. I think they have cable to cable versions but I haven't checked.

http://uk.rs-online.com/web/p/industrial-automation-circular-connectors/0575715/
http://docs-europe.electrocomponents.com/webdocs/0c63/0900766b80c63e01.pdf

These are plastic connectors so not really suited to places where they might get stepped on/driven over although they are pretty robust. Metal connectors will be quite a bit more expensive.

Your electrician should really be sorting this for you.
 
  • #9
AligatorAmy said:
Thank you for your answers.
@berkeman
I live in the EU.
Each cable is 5meters long.
This is the factory (production).
Electrician with appropriate certificates is authorised to approve the installation.

@CWatters/Asymptotic
Each heater is controlled individually by the PLC (through feedback from its TCK). Therefore, each heater requires separate wires.
There is no need to disconnect the plug with power ON.
All phases are the same (230VAC).
The disconnection will take place once a week.

I've used this type of connector in similar applications with good results.
Multipole_power_connector.jpg

They are available through several different manufacturers. Here is the AutomationDirect https://www.automationdirect.com/adc/Overview/Catalog/Wiring_Solutions/Multi-Wire_Connectors,_Heavy-Duty_(ZP-MC_Series) because they've done a good job at simplifying the selection of which parts go with what, but the ones I used were mostly by Thomas & Betts, and a German company whose name escapes me at the moment.

To use this option:
1. Mount an appropriately sized steel enclosure to the device the heaters are used in, and route the six heater cables into it.
2. Mount a grounding bar in the enclosure. Terminate the the heater ground wires to it, and run a wire from it to the ground tab of the plug.
3. Mount the connector body (the part with the swing arm clamp) onto the enclosure. Use the male connector block in this body. and wire the heater power wires to it.
4. Wire the plug body and female connector block to the heater power controllers.

AligatorAmy said:
Also I have calculated that each heater draws approx. 1.4A (320W, 230VAC). Therefore, when I multiply 1.4A by 6 heaters my amperage is 8.4A. Sellers state the amperage for the multi pin connector. I understand that this is maximum load that the connector can take?
In my case should I then look for minimum 10A connector?

The question is, "how much current runs through each pin"?
6 heaters, 12 pins, 1.4A per pin. (assuming 230V line-to-line).

10A will certainly do. However, another consideration is whether you plan on using them elsewhere. The cost difference between 10A and 16A isn't much, and 16A gives the flexibility to use the same connector over a wider range of projects while eliminating the need to maintain both 10A and 16A parts in emergency stock.

Run this past your electrician.
 
  • #10
Thank you All for the answers.
@Asymptotic
This is exactly the same multi pin connector which I would like to use.
Also, the solution you had suggested is the same scenario as I planned.
Indeed, there is no harm to use pins rated for 16A.
As soon as I have the pricings from the potential suppliers I will talk with the electrician.
Thank you for your clarifications in regards to the pins number and the grounding solution.
I am grateful.
 
  • #11
Socapex 19 pin connectors as used in stage lighting systems might be useful. They're generally used for six separate circuits - three each of line, neutral and Earth with an additional overall Earth connection.

See: - http://www.adena.co.nz/theatre/tech-reference/datasheets/cables/power/ca000003.pdf
 

1. What factors should be considered when selecting a multi-pin connector for power lead cables?

When selecting a multi-pin connector for power lead cables, it is important to consider the voltage and current requirements of the application, the environmental conditions the connector will be exposed to, the number of pins needed, and the type of connection (e.g. soldered, crimped, etc.). It is also important to ensure that the connector is compatible with the power source and the cable being used.

2. How do I determine the appropriate size and type of multi-pin connector for my power lead cables?

The size and type of multi-pin connector needed will depend on the voltage and current requirements of the application. It is important to consult the manufacturer's specifications and choose a connector that can handle the required voltage and current. The type of connection (e.g. circular, rectangular, etc.) will also depend on the specific needs of the application.

3. Can I use a multi-pin connector for both power and data transmission?

Yes, there are multi-pin connectors available that can handle both power and data transmission. These connectors are designed to have separate pins for power and data, allowing for safe and efficient transmission of both types of signals.

4. What is the maximum current rating for multi-pin connectors?

The maximum current rating for multi-pin connectors varies depending on the specific connector and its intended use. It is important to consult the manufacturer's specifications to ensure that the connector can handle the required current for your application.

5. How do I ensure a secure and reliable connection with multi-pin connectors?

To ensure a secure and reliable connection, it is important to properly crimp or solder the pins onto the power lead cables. It is also important to choose a connector with a secure locking mechanism to prevent accidental disconnection. Regular maintenance and inspection of the connectors can also help to ensure a reliable connection over time.

Similar threads

Replies
37
Views
3K
Replies
6
Views
1K
Replies
19
Views
2K
Replies
8
Views
2K
Replies
5
Views
497
  • Electrical Engineering
Replies
14
Views
13K
  • DIY Projects
Replies
5
Views
2K
Replies
17
Views
12K
Replies
6
Views
2K
  • Electrical Engineering
Replies
10
Views
6K
Back
Top