Using the thermosyphon effect for a floor water heating system

In summary, the grid power often dies, so the homeowner needs a backup power source and heat source. They think of installing water tubes in the floors and building a wood-burning water heater in a "stove house" down the hill from the house. This would be made so that the water circulates from the thermosyphon effect, without any pump. The stove house would be at 16m from the house, and it would be smart to put a couple CO detectors in the home.
  • #1
petterg
162
7
I've moved to a "new" house - built about 350-400 years ago. Firewood in a stove kind of works for heating a few rooms, but not the full house. So far it seems like the grid power tends to die about twice a month. Temperatures is expected to reach -25C (-13F) for the coldest couple of weeks every winter. Hence I need some kind of backup power and heat source.

The house is located in a small hill side, facing south-west. From about 15th of November some near by mountains is blocking the sun, so solar energy will be zero for at least 2 months/year.
On the property trees grow faster than I'll ever be able to burn them, so there is unlimited access to firewood.

Energy required to heat the house seems to be about 3kw at 0C outside. That should indicate the need for 7kw for the coldest days.

I have an idea: What if I install water tubes in all floors and build a wood burning waterheater in a "stove house" somewhere down hill from the house. Could this be made in such way that water will circulate from thermosyphon effect, without any pump (needs to work even when grid power dies). A convenient place to put the stovehouse will be 16m from the house. Then the base of the stove will be 5,5m below the floorlevel. Could this be enough to make the thermosyphon work? Will it be able to transport 7kw of heat? (What is required in order to make such system work?)

I'm thinking of making the stovehouse burn logs, maybe 2m long, maybe some kind of autofeed. Also I'm thinking of storing logs on top of the stovehouse to let the waste heat help to dry the logs. Hence the time consumed to deal with firewood should be minimized.
 
Last edited by a moderator:
Physics news on Phys.org
  • #2
In the 90s, there was a surge in popularity of external wood-burning boilers. They burned logs, and piped steam to the house for heating. I believe that they used the circulation from steam pressure rather than electric pumps or fans, but I may be wrong. My neighbor had one.

But their popularity declined because they created so much smoke and localized air pollution, that many towns changed the rules to forbid them. On some days with temperature inversions, my neighbor's boiler blanketed the neighboring farms with smoke.

Be advised that designing a boiler is no DIY project. There are many codes and laws because of numerous boiler explosions in the past that kill people within a large radius. To do that, you must buy a boiler certified to meet all applicable codes.

My father in law once built a 3 story house with hot water heating and baseboard radiators. The water circulation was done entirely by "natural circulation", no pumps. A google search for natural circulation hot water heating provides lot of hits.
 
  • Like
Likes Dale, trurle, Klystron and 1 other person
  • #3
In theory, this should work. There is just one practical issue: since this method of heating is a bit out of being common right now, I guess it will be a bit difficult to find somebody who can and: will build it...

Masonry heaters, thermal mass stoves, rocket mass heaters has a big popularity these days, maybe it would be better to look into them instead.
 
  • #4
petterg said:
What if I install water tubes in all floors and build a wood burning waterheater in a "stove house" somewhere down hill from the house. Could this be made in such way that water will circulate from thermosyphon effect, without any pump (needs to work even when grid power dies). A convenient place to put the stovehouse will be 16m from the house.
One other safety consideration is being sure that carbon monoxide from the combustion will not gather in your home. Is the breeze typically downhill during the times when you will be doing the most burning (I would guess so, given your description of the cold hillside environment without much sunlight). 16m sounds like a good separation, and it may help to be sure that any air inlets into the home are on the uphill side, away from the stove house. It may also be smart to put a couple CO detectors in your home, just to be sure. They are inexpensive and run on 10 year life batteries.
 
  • Like
Likes Klystron
  • #5
Given that OP wants to use the floor as a heating surface I don't think there is much reason to worry about boilers and steam o0)
 
  • #6
Rive said:
Given that OP wants to use the floor as a heating surface I don't think there is much reason to worry about boilers and steam o0)
Because that would burn their feet?
 
  • #7
The system can be unpressurized water to avoid hazards associated with pressure, but I see some difficulties:

7kW seems low, though it would depend on the size of the house. My townhouse has a 20kW heater.

Circulation by convection is unlikely to work for this application. for one thing, you need the water to circulate relatively fast for even heating.
 
  • #8
With the original questions answered above about heating, consider alternate power sources.

Create a local grid node. Store electrical energy similar to how you store dry wood for burning. Consult local electricians. Monitor usage; estimate future requirements. Filter house electricity through a UPS (uninterruptible power supply) system. Batteries in the UPS supply power during municipal lows. If you add a generator, an automatic transfer switch (ATS) can sense prolonged outages, start the generator, and switch to the local grid.

Design your electrical upgrdes to favour critical systems in emergencies such as communications, pumps, refrigeration. If and when you add power sources such as windmill, solar, biomass; you can combine these sources with municipal. In western USA where the sun shines bright <humor>, smaller households equipped with passive solar panels generate enough electricity during a summer day to charge their UPS and trickle power back to municipal; with the inevitable corollary that the household must be air-conditioned.
 
  • #9
russ_watters said:
7kW seems low, though it would depend on the size of the house. My townhouse has a 20kW heater.
That's an often missed point. The peak power of a heating system is not based on the ability to keep an acceptable temperature on the expected coldest day, but on the ability to heat up the house within acceptable time on the coldest day. Quite the difference I would say...

russ_watters said:
Circulation by convection is unlikely to work for this application.
These kind of heating systems can work, but careful engineering is needed. In the house of my parents we had one such system with ~4m distance between the hot and the cold pipe. The main pipe was 2.5" in diameter. It took an hour for the radiators to get warm. (Yes, it was an 'open' system on atmospheric pressure.)
Pairing this kind of setup with floor heating... Well, I would not do that.
 
Last edited:
  • Like
Likes Klystron and russ_watters
  • #10
Rive said:
That's an often missed point. The peak power of a heating system is not based on the ability to keep an acceptable temperature on the expected coldest day, but on the ability to heat up the house within acceptable time on the coldest day. Quite the difference I would say...
Yeah, mine is definitely sized for rapid warm-up, but even then it's probably 50-100% extra, so still a lot more than the OP. And my house is relatively new, well insulated and only has 3 walls and not many windows.

...for AC, they don't generally oversize, and mine takes forever to cool.
 
  • #11
7kw is the required constant heat radiation inside the house.

16m from the house is actually more than the distance to the neighbors chimney. Although I'm not planning to build the stove house as high as the neighbors house. I'm not too worried for the smoke as I'm thinking of using a stove that burns hot and clean. They say a perfectly designed rocket mass heater emits only CO2. How hard can it be to make it perfect? (Probably extremely hard)

"natural circulation" was a nice term to search. Actually better than "thermosyphon".

I'm thinking of designing the stove similar to a rocket mass heater - let water be the mass. I have to build it my self, as such thing cannot be bought in Norway (where I live). That (fire) is also one of the reasons for having this in a building some distance from the house rather than in the basement. (Ease of loading the logs, bugs that might live in the logs, no need to carry logs up the hill, are other reasons for not bringing the stove into the house.

I was considering steam, but I don't want to create local steam clouds. I want this all to be a closed loop system. So, IF I'd go with steam, it would have to condensate back to water somewhere. The steam route would first power a steam engine. Steam engine exhaust then goes into coil inside a large water tank inside the house. Here the steam should condensate and return to the boiler. The steam engine should power a pump that circulates the water from the tank into the floor heating pipes. I think this would turn out quite expensive, and steam is a significantly higher risk level than hot water. The steam system would have a major advantage though - it would generate electricity. I could cancel the grid power!

The hot water thermosyphon approach seems safer and way cheaper. The only major risk, as I see it, would be if the water circulates too slow, or circulation stops for some reason, it will boil. This system will require a pressure valve that will let water/steam out if boiling happens. From how I understand thermosyphon the circulation will be faster the more heat/cooling is applied to the loop. I can apply more cooling to the loop by letting it run outdoors with little or no isolation. In my mind it all comes down to scaling the various parts of the loop properly. How to scale them, I have no idea.
 
  • Like
Likes Klystron
  • #12
I once helped a friend design a heating system that transferred heat from the wood fired boiler to an open storage tank by thermosyphon. The storage tank held 1100 gallons of water. That was the amount that would allow him to build a fire in the evening, and heat the house until the next evening at 0 deg F. At design temperature of -20 deg F, he had to build a smaller fire in the morning. The wood burner was located next to the tank as shown in the simplified sketch below.
PC100049A.jpg

Unfortunately, he chose to build the tank from concrete block and seal the inside with epoxy. He had to fill the tank three times and drain it twice to find and fix the leaks, but finally got it to hold water. He then learned that the thermosyphon effect stops when the bottom level of the hot water in the tank gets down to the level of the heat exchanger in the boiler. The top half of the tank was hot, the bottom half stayed cold. He only had 50% usable heat storage. The next learning experience was that hot concrete blocks expand, cold concrete blocks do not, and the cold concrete blocks at the hot/cold water interface fail in tension, causing cracks and new leaks. The tank was insulated on the outside. He fixed the leaks (third drain down, fourth fill) and added a circulating pump. The rest of the four zone hydronic system worked properly. The gas fired backup boiler worked properly.

The maximum water temperature in an open system is about 210 deg F. When the tank reaches that temperature, there will be evaporation. The top of the tank needs to closed tight against vapor, but such that it will not hold against pressure, along with an open vent to atmosphere.

The usable heat storage is the total amount of water times the maximum temperature difference. The maximum temperature is 210 deg F. The minimum temperature is the minimum temperature that heats the house on the coldest day. Most hydronic systems are designed for a water temperature of 180 deg F. A hydronic system designed for 180 deg F water would have a maximum temperature difference of only 30 deg F, while a hydronic system designed for 120 deg F water would have a maximum temperature difference of 90 deg F.

Thermosyphon flow can be calculated. Start with the supply side temperature and the estimated return temperature. The density difference between the two temperature times the vertical distance gives you the total head (pressure difference). From that, you can calculate the flow rate. The heat transferred is calculated from the temperature difference and flow rate. The return temperature is calculated by standard heat transfer calculations. Iteration is necessary.
 

Attachments

  • PC100049A.jpg
    PC100049A.jpg
    16.3 KB · Views: 1,355
  • Like
Likes russ_watters and berkeman
  • #13
Don't forget antifreeze in the system, otherwise you can't leave for a couple days without draining the whole system.
 
  • Like
Likes OmCheeto, nsaspook and russ_watters
  • #14
petterg said:
How to scale them, I have no idea.
These kind of systems with natural circulation phased out exactly because they are hard to design (properly) and they requires too much material (pipe diameters are usually several times larger than for new systems with forced circulation).
Floor heating systems requires careful design and control to be effective and comfortable.
You want to pair them together, without real control (so it can be operated without electricity).
I think this project (as it is now) is just 'asking for trouble'.
 
  • Like
Likes russ_watters
  • #15
I kind of know how to make trouble. I'm asking for control ;)

Jrmichler, your experience is valuable. Did your friends system not create steam in the boiler?

Delta T in the loop can possible be quite large. If the loop is created like this: Coil around the stove - isolated pipe to the house - coil in hotwater tank located high up inside the house - floor heating - outside driveway heating (the driveway has a 21% slope at the steepest and a sharp turn) - return to the stove. This loop should make it possible to have a delta-T maybe as large as 80C (176F). With the hot water tank high up in the house, the total high difference should be near 10m, although the return path from the lowest part of the driveway to the stove will need to go 3m up, 20m horizontal, 3m down.

I guess some kind of control could be added - battery powered. Then, how much energy will a pump require? (How to calculate?)
 
  • #16
petterg said:
I kind of know how to make trouble. I'm asking for control ;)
In case you can't stop immersing yourself in dubious DIY projects around floor heating, then you would do better with a diesel based heatpump system. Might be hooked as an emergency generator and by utilizing the waste heat it is possible to aim for a nominal 100+ % efficiency.
Still plenty of weak points, but at least there is hope.
 
  • Like
Likes russ_watters and Klystron
  • #17
Heatpump (air - air or air - water) doesn't work well with outside temps below 15C (5F). That is, you get a COP<=1. If you're lucky the generator provides 30% of the diesels energy as electricity. You would be better of circulating the engines coolant via the house than using the electricity it produces. Or even better, put a diesel driven heater in the house.

Half the purpose of this project is to make use of the resources that exists on this property. I also was thinking of making a water driven generator. It would probably work very well, except the the water also stops moving in these temperatures.
 
  • #18
petterg said:
Firewood in a stove kind of works for heating a few rooms, but not the full house.

If you're really interested in the simple solution; multiple wood stoves. But is sounds like you're not searching for heat, you're searching for a big project.
 
  • #19
petterg said:
[snip]...
Half the purpose of this project is to make use of the resources that exists on this property. I also was thinking of making a water driven generator. It would probably work very well, except the the water also stops moving in these temperatures.

When I posted about battery backup and local power sources, water generation was the first method I considered after diesel. It seems an ancient even medieval method, but when the water motion generates electricity instead of grinding flour or pounding ore...

Wind turbines or old-style windmills could add another unpredictable weather-dependent source to your energy independence.
 
  • #20
Rive said:
In case you can't stop immersing yourself in dubious DIY projects around floor heating, then you would do better with a diesel based heatpump system. Might be hooked as an emergency generator and by utilizing the waste heat it is possible to aim for a nominal 100+ % efficiency.
Still plenty of weak points, but at least there is hope.
I don't know how long these power outages go, but a battery operated pump might get him through. If not, a small gas generator would be enough for a pump and to keep the lights on in the house.

So yeah, the intermittent power is the problem I'd try to solve, not the loss of pump problem.
 
  • Like
Likes CWatters, Rive and Klystron
  • #21
petterg said:
That is, you get a COP<=1.
Could you please give us a source about that? As far as I know typically it would be around COP=2 for -15degC to 35degC. But even for 50degC output it is around 1.6 (measured, not some AD-value).

With a 22hp diesel at peak power and COP=2 ( -15C to 35C) it is ~ 30kW heat from the environment. The diesel also contributes ~ 30kW waste heat.
If the system eats up a few hp for generating electric power for the pumps (and maybe for the house) then it is a bit less, but if you can't warm up with this much heat then ...

For this kind of purpose the diesel usually directly driving the heat pump and electricity generation is just an auxiliary task. The waste heat of the engine is often 'recycled' into the heating (up to various levels).

This might work.
Non-working solutions cannot be considered as 'making use of resources' by my humble opinion.
 
  • #22
russ_watters said:
my house ... only has 3 walls and not many windows

Something like this, Russ? :eek:
tetrahedron.jpg
 

Attachments

  • tetrahedron.jpg
    tetrahedron.jpg
    6.9 KB · Views: 1,280
  • Like
Likes russ_watters
  • #23
gmax137 said:
Something like this, Russ? :eek:
View attachment 235624
That's four walls and no roof. My house has a roof and three walls. :biggrin:
 
  • #24
petterg said:
Did your friends system not create steam in the boiler?

He built the boiler also. I sized the heat exchanger, it was a number of (I forget how many) 2" Sched. 40 pipes fire tube design. He built a front access panel so he could drill out the creosote with a 2" twist drill on an extension. He had a lot of creosote because he burned green wood, and also because he liked to fill the fire box with wood and walk away. And the heat exchanger was sized to take most of the heat out of the hot gases. Also, there was no provision for secondary combustion air during the pyrolysis stage.

He had 3" lines between the boiler and the heat storage tank. Good circulation was not a problem.
 
  • Like
Likes jim hardy
  • #25
petterg said:
I have an idea: What if I install water tubes in all floors and build a wood burning waterheater in a "stove house" somewhere down hill from the house. Could this be made in such way that water will circulate from thermosyphon effect, without any pump (needs to work even when grid power dies).

certainly sounds plausible.
Thermosiphons need a high point vent because liquid side flow is usually not enough to sweep out gas bubbles.

Around here people use an old automobile or truck radiator to move heat from the liquid into the air for the house.
A big truck radiator has low wet side pressure drop, has plenty of heat transfer area and includes a built in high point vent.
But they need a fan to move air through the radiator fins.
If you have central heat or airconditioning you might be able to shoehorn a car radiator into the return air plenum and just run the fan.
 
  • Like
Likes Tom.G
  • #26
Rive said:
Could you please give us a source about that? As far as I know typically it would be around COP=2 for -15degC to 35degC. But even for 50degC output it is around 1.6 (measured, not some AD-value).

Thats what people (including resellers) say around here. COP around 4 at +7C outside, COP near 1 at -15C outside. I guess they expect inside temp around +22C. Heating the inside air requires the hot side of the heatpump to be significantly warmer than the inside temperature. Some heatpumps are marketed with the selling point that they work down to -20C outside.

jim hardy said:
Around here people use an old automobile or truck radiator to move heat from the liquid into the air for the house.
Thats a very good idea.

jrmichler said:
And the heat exchanger was sized to take most of the heat out of the hot gases. Also, there was no provision for secondary combustion air during the pyrolysis stage.
I guess that was a mistake. It will be of major importance to design the stove so that it extracts heat from the burning gasses, not from the gases before they burn.

3" pipes however is far too large to put in the floors. That will be an flow area of about 44cm2. Regular floor heating pipes are 22mm, that's an flow area of about 3cm2. Then I'll need 14 floor circuits in parallel just to get the same flow area. I'll probably need to double that to compensate for pipe friction. Sounds like a battery powered pump will be required.
 
  • #27
petterg said:
That should indicate the need for 7kw for the coldest days.
Wow. That's about 50 kg of wood per day.
Thank god I don't live in Norway.

Btw, It's been "Norway cold" at my house for the last two weeks(0-4°C), so I've been doing thermal experiments, and I discovered that my house has almost the same thermal loss rate as yours: 170 watts/(°C differential temp).

Glad to see you've dropped the idea of a thermosyphon. I looked at the variables involved with just the flow, and said to myself; "petterg can do the maths. That is a stupid amount of variables..."

https://www.lmnoeng.com/HazenWilliamsDesign.php
Variables:
A = Pipe cross-sectional area, ft2 or m2.
C = Hazen-Williams pipe roughness coefficient. See table below for values.
D = Pipe diameter, ft or m.
Driving Head (DH) = left side of the first equation (or right side of the equation), ft. This is not total dynamic head.
g = acceleration due to gravity = 32.174 ft/s2 = 9.8066 m/s2.
hf = Major (friction) losses, ft or m.
hm = Minor losses, ft or m.
Hp = Pump head (also known as Total Dynamic Head), ft or m.
k = unit conversion factor = 1.318 for English units = 0.85 for Metric units
Km = Sum of minor loss coefficients. See table below.
Pump Power (computed by program) = SQHp, lb-ft/s or N-m/s. Theoretical pump power. Does not include an inefficiency term. Note that 1 horsepower = 550 ft-lb/s.
P1 = Upstream pressure, lb/ft2 or N/m2.
P2 = Downstream pressure, lb/ft2 or N/m2.
Q = Flow rate in pipe, ft3/s or m3/s.
S = Weight density of water = 62.4 lb/ft3 for English units = 9800 N/m3 for Metric units
V = Velocity in pipe, ft/s or m/s.
V1 = Upstream velocity, ft/s or m/s.
V2 = Downstream velocity, ft/s or m/s.
Z1 = Upstream elevation, ft or m.
Z2 = Downstream elevation, ft or m.

And that's just for steady state.
 
  • #28
I live in one of the warmest areas in Norway. My 3 coldest days is like the average over 3 month for those living in the north or away from the coast.
I bet your house is not 400 years old. My thickest wall is 40cm thick. What's inside the wall is unknown. Today I finally found the moving box where my thermal leak detector was located. Now I'll just need a cloudy day without any wind to figure where the heat leaks. I'm expecting the windows leaks alot. Even though the windows are just 16 years old, they try to much to look like the old style windows. Energy efficient old-style windows are full size glass, with a frame of wood on both sides that makes them look like 6 small windows. These windows are actually 6 small windows. That makes them have a lot of edges. Edges makes most of the thermal leak in a window.

Math is simple. Figuring out the numbers and the formula to use is worse. I just have no clue how (to calculate) much energy is required to circulate water in a closed loop, or how strong the thermosyphon effect is. Any real world experience from this is valuable.
 
  • #29
petterg said:
I live in one of the warmest areas in Norway. My 3 coldest days is like the average over 3 month for those living in the north or away from the coast.
I bet your house is not 400 years old. My thickest wall is 40cm thick.
My house is 70 years old and has 13 cm thick exterior walls.
What's inside the wall is unknown. Today I finally found the moving box where my thermal leak detector was located. Now I'll just need a cloudy day without any wind to figure where the heat leaks. I'm expecting the windows leaks alot. Even though the windows are just 16 years old, they try to much to look like the old style windows. Energy efficient old-style windows are full size glass, with a frame of wood on both sides that makes them look like 6 small windows. These windows are actually 6 small windows. That makes them have a lot of edges. Edges makes most of the thermal leak in a window.
All but one of my windows are the original single pane units that came with the house. I've added shrink film to the insides.
Math is simple. Figuring out the numbers and the formula to use is worse. I just have no clue how (to calculate) much energy is required to circulate water in a closed loop, or how strong the thermosyphon effect is. Any real world experience from this is valuable.
I did a solar-thermal experiment with a pump and some black hose a few years ago. The pump was rated at 24 watts and pumped 0.1 kg/sec. From that I determined that was 3 times the flow you would need. But that was at steady state, and at optimal conditions.

Interestingly, I just calculated how long my trees would last. I have 4 x 30 meter tall Douglas Fir trees on my property. They would last me 10 years if I heated my home exclusively with wood. Seems like a lot of work. I would have needed to burn 30 kg yesterday.
 
  • #30
Yes, firewood is a lot of work. Thats why I want some kind of system that accepts 2m (6ft) logs with some kind of auto gravity feeder. The idea is to cut the logs into some easy to handle length, load them into the stove feed using a tractor and leave the stove burning unattended for a few days. Then there is no need to cut the logs to short lengths, no need to split the wood, no need to stack all the firewood for drying (just the few logs), no need to carry the firewood indoors, no need to load a bunch of small pieces of firewood into a indoor stove every hour, no cold house in the morning, no spill around the stove. Basically a huge outside stove saves a lot of work.
The stove design need to combine the Swedish "long log fire" with a rocket mass heater with a water based radiant heating system.
The auto feeder will be a challenge as well.
 
  • #31
petterg said:
load them into the stove feed using a tractor

petterg said:
The auto feeder will be a challenge as well.

The external boilers I've seen allow 24 hours supply of 6' logs to be loaded at once with a tractor. That eliminates the need for an auto feeder. Remember the KISS principle.

The radiant heat is a separate problem. The logical way to proceed is
  1. Determine the heat load of your house in all conditions to determine the heating system requirements. As part of that, you may consider different insulation options.
  2. Design the radiant heat system, and from that determine the requirements of the external heat source, power, flow rate, temperature, etc. Circulation pumping is part of that.
  3. Select the external heat source, boiler/water-heater/furnace that meets the requirements.
 
  • #32
petterg said:
Heatpump (air - air or air - water) doesn't work well with outside temps below 15C (5F).
You seem to have dropped a minus sign on that 15C. Possibly that is why you had an objection to the apparent claim about COP=1 at 15C.
 
  • #33
jbriggs444 said:
You seem to have dropped a minus sign on that 15C. Possibly that is why you had an objection to the apparent claim about COP=1 at 15C.
You're right. At least I got the 5F right.

anorlunda said:
The external boilers I've seen allow 24 hours supply of 6' logs to be loaded at once with a tractor. That eliminates the need for an auto feeder. Remember the KISS principle.

The radiant heat is a separate problem. The logical way to proceed is
  1. Determine the heat load of your house in all conditions to determine the heating system requirements. As part of that, you may consider different insulation options.
  2. Design the radiant heat system, and from that determine the requirements of the external heat source, power, flow rate, temperature, etc. Circulation pumping is part of that.
  3. Select the external heat source, boiler/water-heater/furnace that meets the requirements.

I started with 1, Calculated that new 3-glass windows will save 10% on the heating bill. Material cost will make this pay back in 225 years at the current electricity cost, with 0% interest rate and cost=0 for the work. And it won't keep the house warm when power goes out.

To dimension this for electrical heating just to calculate how much is required of the stove seems like a waste of work and money.

I'd rather go the other way around - build a small scale stove for the planned green house (planning to build) and/or for the barn (planning to make a workshop in there). With that experience, I hope to be able to build it right for the house.
 
  • Like
Likes anorlunda
  • #34
petterg said:
With that experience, I hope to be able to build it right for the house.
How will you know it is right for the house plus greenhouse?

Prudent engineers always work in this order.
  1. Requirements
  2. Design
  3. Construction
  4. Operation.
You're free to do it any way you want, but don't expect engineers to advise other than requirements first.
 
  • Like
Likes Klystron
  • #35
Requirement is 7kw continues inside the house. Which means the stove will need to be 7kw + waste
Design is probably rocket mass heater or similar
Construction will follow some plans for rocket mass heater (unless something better turns up). There are lots of plans out there.
When a green house / barn model is build, I will have an idea of what needs to be improved.

Installing the floor tubing is a project that needs to be done step by step. One floor at the time. As thermosyphon effect seems to not do the job, floors can be designed as regular heat pump driven floor heating. That is a topic where there are lots of local knowledge. Whats experimental here is how much energy the pump will need - so I may have to upgrade the pumps battery.
 

Similar threads

  • DIY Projects
2
Replies
36
Views
8K
Replies
3
Views
2K
Replies
3
Views
2K
Replies
11
Views
3K
Replies
18
Views
3K
  • General Engineering
Replies
25
Views
7K
Replies
8
Views
6K
  • General Engineering
Replies
14
Views
2K
Replies
16
Views
2K
Replies
10
Views
2K
Back
Top