Why does the high voltage side of transformers tend to burn out first?

In summary: He also told me that the fuse usually blows first on the high voltage side of a transformer, not the low voltage side. Apparently, the fuse is designed to blow before the transformer itself fails. The fuse usually blows first on the high voltage side of a transformer, not the low voltage side.This makes sense. If there's a short on the high voltage side of the transformer, the fuse will blow first, and if there's a short on the low voltage side of the transformer, the transformer will probably still work.
  • #1
fourthindiana
162
25
In residential split-system air-conditioners and heat pumps, there are transformers inside both the condenser and the air-handler that step the voltage down from 220/230/240 volts to 24 volts. Someone once told me that in residential air-conditioners/heat pumps, the high voltage side of a transformer tends to burn out more often than the low voltage side of a transformer. Both the high voltage side and the low voltage side of a transformer deal with the (approximately) same amount of wattage. The low voltage side of a transformer has lower current, and the high voltage side of a transformer has higher voltage. Is higher voltage more likely than high current to cause a transformer to burn out?
In a residential air-conditioner/heat pump, why does the high voltage side of the transformer tend to burn out more often than the low voltage side of the transformer?
 
Engineering news on Phys.org
  • #2
Interesting question. It would be better if we had some articles or links to places that claim this, instead of just your friend saying this. But if he is a tradesperson who works with those kinds of systems, it might be valid information.

Since such transformers are generally monolithic, how can you tell if one side is "burned out" versus the other? With resistance checks on the windings (looking for opens or inter-winding shorts)?

We can discuss the theoretical reasons for such a phenomena (I can think of several reasons it might be true), but in the end it would depend on the wire gauge sizes used and transformer construction and a number of other things that the manufacturers control beyond any transformer theory.
 
  • Like
Likes CWatters, fourthindiana and gneill
  • #3
berkeman said:
But if he is a tradesperson who works with those kinds of systems, it might be valid information.

The guy who told me this is an expert HVAC technician.

Since such transformers are generally monolithic, how can you tell if one side is "burned out" versus the other? With resistance checks on the windings (looking for opens or inter-winding shorts)?

He told me about this, but I was not taking notes or anything, so I cannot be 100% sure what he said.

However, I'm 99% sure that he checks if one side is "burned out" by checking the resistance of the wires coming out of the transformer, not the windings inside the transformer.

We can discuss the theoretical reasons for such a phenomena (I can think of several reasons it might be true), but in the end it would depend on the wire gauge sizes used and transformer construction and a number of other things that the manufacturers control beyond any transformer theory.

He told me that the wires on the low voltage side are bigger (as in thicker) than the wires on the high voltage side because the low voltage side wires carry a higher current. My impression is that manufacturers of residential HVAC transformers universally choose to make transformers with thicker wires on the low voltage side to accommodate the higher current on the low voltage side. That is probably the key characteristic of residential HVAC transformers that the manufacturers control beyond any transformer theory.

You said that you can think of several reasons that it might be true. That is the key to answering this thread. Assuming that the manufacturers of residential HVAC transformers universally make the transformers with thicker wires on the low voltage side of the transformer (to accommodate the higher current on the low voltage side), why does the high voltage side of the transformer burn out first?
 
  • #4
fourthindiana said:
The guy who told me this is an expert HVAC technician.
Awesome, my wife talks with these folks every day to help resolve issues. :smile:
fourthindiana said:
However, I'm 99% sure that he checks if one side is "burned out" by checking the resistance of the wires coming out of the transformer, not the windings inside the transformer.
Well, sorry, that kind of doesn't make any sense. If you could ask him what he checks in his failure analysis, that would be a big help in answering your question. And does he have specifications from the manufacturer on what the winding resistances should be for a good transformer? At my work, we publish those specs.
fourthindiana said:
He told me that the wires on the low voltage side are bigger (as in thicker) than the wires on the high voltage side because the low voltage side wires carry a higher current.
Yeah, that follows directly from how a transformer works.

Probably your question will boil down to which side of a practical power transformer will fail first given an output fault (short?). I would probably design my transformers to fail equally likely on primary or secondary to minimize the cost of the transformer, but maybe some of our experts like @anorlunda can offer other insights. :smile:

EDIT / ADD -- And the fuse or breaker should fail before the transformer fails That is their purpose...
 
  • Like
Likes fourthindiana
  • #5
berkeman said:
Well, sorry, that kind of doesn't make any sense. If you could ask him what he checks in his failure analysis, that would be a big help in answering your question.

I thought about this. You're right. What I wrote there does not make sense. If he checks the resistance by connecting the leads of his multimeter to the wires coming out of the transformer, that will automatically check the resistance of the windings.

Let me rephrase this. I'm 99% sure that he checks the resistance of the windings by connecting the leads of his multimeter to the wires coming out of the transformer. The wires coming out of the transformer are connected to the windings, so this checks the resistance of the windings as well.

And does he have specifications from the manufacturer on what the winding resistances should be for a good transformer? At my work, we publish those specs.

I doubt he or any other HVAC technician keeps written specifications from the manufacturer on what the winding resistance should be for a good transformer. I believe what he does is that he knows what a ballpark figure of what the resistance should be and compares the resistance figures to that. For instance, it might be the case that the resistance should be something like, say, 0.2 ohms, and if his multimeter says something like "OL" for open line or if it says infinite resistance, he knows that it's a defective transformer.

I would probably design my transformers to fail equally likely on the primary or secondary to minimize the cost of the transformer...

Perhaps you would, but most or all residential HVAC transformer manufacturers don't.

EDIT/ADD---And the fuse or breaker should fail before the transformer fails That is their purpose...

I agree, but in the real world what should happen is not always what happens.
 
Last edited:
  • #6
Yeah, if the fault is open circuit on a winding, that's easy to check for. Shorted windings usually just lower the winding resistance, so unless you have typical winding resistance specification from the manufacturer, that's harder to isolate.

Do you know which it was? Can you say which unit it was? Even if it's not available via a regular internet search, my wife my have access to the specs via her work...
 
  • #7
berkeman said:
Yeah, if the fault is open circuit on a winding, that's easy to check for. Shorted windings usually just lower the winding resistance, so unless you have typical winding resistance specification from the manufacturer, that's harder to isolate.

Do you know which it was? Can you say which unit it was? Even if it's not available via a regular internet search, my wife my have access to the specs via her work...

I just texted him about this. This is how he tests a transformer when the air-conditioner/heat pump is turned off: First, he tests the resistance of each wire to ground (ground being the metal casing of the transformer). When he tests the resistance of each wire to ground, he gets an "OL" (open line or open circuit) reading if the transformer is good. If he gets any reading other than OL, the wires are touching the casing and the transformer is bad.

Next he uses his ohm meter to check the resistance of the secondary side and the primary side. If he gets an OL reading, the winding is open (meaning the wire is broken or burnt and there is no path). If he gets resistance on both, then he ensures that the primary has more resistance than the secondary. If the primary has more resistance than the secondary, the transformer is good. If the secondary has more resistance than the primary, then the transformer has a shorted primary winding or he has a step up transformer rather than a step down transformer.
--------------------------------------------------------------------------------------------------------------------------------------------

So does that tell you why the high voltage side of the transformer tends to burn out first?
 
  • #8
Some small transformers such as these have an internal fuse or thermal overload in the primary side. This is done more often with enclosed transformers but I have seen some open-frame transformers with them as well. The fuse or overload is at or near the outer surface of the primary, with another layer of paper covering; so even if present you won't see them.

First of course is the smell test. If it smells burned, get rid of it.

Under the special conditions of a tripped thermal overload due to a temporary fault, sometimes it can be reset by spraying it with Freeze Spray, available at electronic supply stores. But considereing the cost of a service call, you are probably ahead to just replace the transformer and check for overloads or shorts.

(the resettable thermal overloads {not all are resettable} are a snap-action thermostat with a wide deadband. barring physical damage, get them cold enough and they switch back on.)

Cheers,
Tom
 
  • Like
Likes dlgoff and davenn
  • #9
Tom G, what are you saying? That the residential HVAC transformers tend to burn out on the primary side because they usually have a fuse on the primary side? If not, I don't understand your post.
 
  • #10
fourthindiana said:
Tom G, what are you saying? That the residential HVAC transformers tend to burn out on the primary side because they usually have a fuse on the primary side? If not, I don't understand your post.
Yup.
An open fuse or tripped thermal overload in series with the primary is electrically identical to an open winding.
 
  • Like
Likes davenn
  • #11
fourthindiana said:
This is how he tests a transformer
That was a big help: I could identify what's this about. Guess you are asking about this type of small (few VA) transformers, correct?

These cheap, small ones has a big contact area inside the primary winding, all covered with only a thin layer of insulation, almost always heated up. Also, the wire of the primary is really thin, almost like the wire in a small amp fuse. A shorted turn can easily cause enough current to break the wire, an due the cheap, high turn count winding it is easy to get a shorted turn when the insulation gets worn down by the heat.
 
  • #12
Tom.G said:
Some small transformers such as these have an internal fuse or thermal overload in the primary side. This is done more often with enclosed transformers but I have seen some open-frame transformers with them as well. The fuse or overload is at or near the outer surface of the primary, with another layer of paper covering; so even if present you won't see them.

fourthindiana said:
Tom G, what are you saying? That the residential HVAC transformers tend to burn out on the primary side because they usually have a fuse on the primary side? If not, I don't understand your post.
Internal fuses are very common in transformers and I in personal experience have found many failed transformers because of the fuse blowing ... resulting in an open circuit primary
( ALL on the primary side)
 
  • Like
Likes dlgoff
  • #13
So a typically "HVAC" transformer will be from Line to some lower ( often control voltage) - but I would agree the High side of transformers probably do have a higher failure rate:

1) Higher voltage stress on the insulation. The insulation on the high side will typically be closer to the "spec" - for example a 480 VAC primary, will be 600V Class... guess what the insulation class of a 120/240 LV side is? Typically still 600V... Even for control power transformers, like 24V - there will be a lot of margin in the insulation since there is little savings in using the minimum.

1A ) Affect of line disturbances on the primary windings. All of the disturbances coming in the facility from the utility connection, switching events, lightning, voltage dips & the associated recovery, and then even just the turning on and off of the transformer locally, stress the primary windings much more than the secondary. ( Both result in both over voltage and higher frequency elements)

2) Overloading - will cause the overall unit to heat up, what does heat do to a transformer do? It ages the insulation faster. But there can definitely some hot-spot issues that can occur on the LV side - I^2*R type issues, become more prevalent if the unit is frequently overloaded, or it was marginally sized. ( Also note - as the low side leads to much of the heating, the windings are often built with a little better spacing, for cooling, but this also helps reduce insulation stress - I have seen secondary faults become re-energized and "live" - but never a primary.)

But.. this leads many lay-persons astray... a majority of these issues lead to insulation failure, leading many to "blame" the insulation, the transformer, and thus the manufacturer. But a lot of the stress can be outside of the design parameters, or the transformer is not applied or protected properly. Still - in a mass produced consumer / commercial products like HVAC transformer, I'll bet your customer knows some brands that fail more frequently than others...

The question for him is -- when he has to replace a transformer, does he use the better brand - or the lesser one for "job security"?? (;-)
 
  • Like
Likes DaveE and rbelli1
  • #14
I think the answer to his question is
"the smaller primary wire acts like a fuse"
I've opened many "Wall Wart" transformers and found the primary open right where it solders to the transformer connector tab.
I suspect (but do not know for certain) that manufacturers of inexpensive consumer equipment use small fragile wire there as a 'fusible link'.

I have noticed high end consumer and industrial manufacturers are more likely to protect their transformers with a fuse.
I guess that's a tradeoff - protect the transformer or eliminate a failure point ?
As a DIY'er i'd vote to protect the transformer
but a business analysis might justify saving the cost of a fuse and a service call to replace it .
 
  • Like
Likes Wrichik Basu, davenn and dlgoff
  • #15
Yes, what Windadct said.
Regardless of the preceding events most transformer "burn-outs" end with breakdown of insulation allowing an arc to form where it shouldn't, then really bad things happen fast. The higher voltage side of the transformer is more prone to insulation failures under stressful conditions (like overheating).
 
  • #16
Transformer shorted twice, in three years old Lenox forced air unit. Each time due to power outage. Primary side of transformer does not have power surge protector, like secondary side. Planing to install all house surge protector to resolve this problem, if not practical, I will install one in the unit itself to prevent future loss of heating system. It can be very cold here. Utility power distribution system is not reliable to say the least.
 
  • #17
Niko Obrad said:
Planing to install all house surge protector to resolve this problem
That sounds like a good choice.
 
  • #18
fourthindiana said:
In residential split-system air-conditioners and heat pumps, there are transformers inside both the condenser and the air-handler that step the voltage down from 220/230/240 volts to 24 volts.
This is all very interesting as there's a lot of info that I've never read before. But why is 24V used for high power circuits? (If it's for low power circuits then why would transformers fail?) Is it to do with the design of motors that have to deal with high startup loads? That's the only reason I could think of.
 
  • #19
sophiecentaur said:
This is all very interesting as there's a lot of info that I've never read before. But why is 24V used for high power circuits? (If it's for low power circuits then why would transformers fail?) Is it to do with the design of motors that have to deal with high startup loads? That's the only reason I could think of.
Control circuits.
 
  • #20
Averagesupernova said:
Control circuits.
A reasonable answer but I have had washing machines for years and they work on mains volts. Is a compressor that much different from a tub full of wet towels?
I won’t be upset if someone tells me why. 🙂
 
  • #21
Central air/heat pump units as well as air handlers use low voltage control circuits. The contactor for the compressor has a 24 volt coil. The compressor runs on 240 volts. The thermostat is also low voltage. Everything in a gas furnace that is a control is low voltage. The combustion blower as well as the room air circulation blower run on 120 volts in the USA but the controls are low voltage. The ignition source now is typically a hot surface ignitor and it also runs on 120 volts. All the sensors that sense if the combustion blower is running are on low voltage circuits. A typical gas furnace furnace has several sensors that sense a slight vacuum in the combustion chamber as well as the slight pressure in the exhaust. There is a flame sensor that senses the presence of the flame by the ever so slight conductivity of a flame. Think of an ohmeter between the probe and the metal that is in contact with the flame. This requires solid state electronics which will have to run on reduced voltage. Usually the transformer and power supply is on a control circuit board and all the sensors, etc. connect to this board.
 
  • #22
Averagesupernova said:
Usually the transformer and power supply is on a control circuit board and all the sensors, etc. connect to this board.
Well, that's not very impressive. Is it just cheapo engineering?
 
  • #23
My 50 year old gas furnace uses 24 VAC as the working voltage. All solenoids and relays have 24 VAC coils but the blower runs on mains power. The (formerly electromechanical) thermostat sees only isolated 24VAC from the furnace and central air unit. So my guess is that the 24 volt standard is mostly a legacy
 
  • #24
hutchphd said:
My 50 year old gas furnace uses 24 VAC as the working voltage. All solenoids and relays have 24 VAC coils but the blower runs on mains power. The (formerly electromechanical) thermostat sees only isolated 24VAC from the furnace and central air unit. So my guess is that the 24 volt standard is mostly a legacy
Of course, I accept that control voltages can be low (often 5V DC). My problem is with the idea that the transformers in the systems being discussed seem to have a reputation for blowing up. If I got that right then it's crazy for a moderately priced low voltage, low power supply.

Or perhaps the reported statements were just a personal reflection of one particular serviceman.
 
  • Like
Likes hutchphd
  • #25
sophiecentaur said:
Well, that's not very impressive. Is it just cheapo engineering?
You haven't noticed that everything built is basically becoming cheaper?
 
  • #26
sophiecentaur said:
My problem is with the idea that the transformers in the systems being discussed seem to have a reputation for blowing up. If I got that right then it's crazy for a moderately priced low voltage, low power supply.
I don't think people are expected to keep a furnace past about 15 years. Some of the guys I've had experience working with concerning service on a gas furnace can't troubleshoot their way out of their own living room. They were ready to replace my furnace when it was something very simple. Mine is about 35 years old now.
 
  • Like
Likes sophiecentaur
  • #27
DaveE said:
Regardless of the preceding events most transformer "burn-outs" end with breakdown of insulation allowing an arc to form where it shouldn't, then really bad things happen fast. The higher voltage side of the transformer is more prone to insulation failures under stressful conditions (like overheating)
The arc will usually happen during a dynamic voltage event (like a sudden failure or spike ). The highest potential difference will occur between subsequent layers of the coil (and be proportional to the number of turns per layer) or on the line going from one terminal to the coil center. The voltage caused by these transients will be proportionately worse on the higher voltage coils (and the distances smaller so fields are even higher) therefore they will fail first. This seems pretty obvious to me, but I am educable.
Of course life gets worse as the enamel ages.
 
  • Like
Likes DaveE
  • #28
sophiecentaur said:
But why is 24V used for high power circuits?

Averagesupernova said:
Control circuits.
Yup.
The 24V is a low enough voltage to qualify as a Class II (?) circuit. The NEC (National electrical Code) allows the wiring to be a cheap and simple multiconductor cable without being further physically protected, or installed by a licensed electrician, when used in buildings, that is: no conduit required.

24V is also a low enough voltage to be non-lethal when you get ahold of it. There is an upper limit on the total energy available though, so it doesn't start a fire when short-circuited.

Cheers,
Tom
 
  • #29
Averagesupernova said:
You haven't noticed that everything built is basically becoming cheaper?
But that doesn't explain why the transformer would be the weak link. Ah - wait a bit; Wound Components.
 
  • #30
sophiecentaur said:
But that doesn't explain why the transformer would be the weak link. Ah - wait a bit; Wound Components.
The transformer is also the front end interface to the power grid. The transformer helps to filter spikes protecting the rest of the circuitry on the low side.
 
  • #31
Averagesupernova said:
You haven't noticed that everything built is basically becoming cheaper?
What matters here (by my opinion) is, that control circuits needs less and less power, so the originally robust (few dozen VA) transformers feeding it started to shrink (few VA). With that, they got thinner and thinner wire on the primary. So thin that a few second more soldering could thin them further: so thin, that a few mm in free air could work as a fuse.

The introduction of small scale SMPS circuits was a real blessing and had a definitive impact on reliability.
 
  • #32
anorlunda said:
The transformer is also the front end interface to the power grid. The transformer helps to filter spikes protecting the rest of the circuitry on the low side.
It's not the size of the job that counts, it's how it's achieved. You can't really 'excuse' bad transformers once their requirements have been specified and they have been specified for a hundred years or more.
Where would we be if that was the attitude with modern solid state devices? One place we wouldn't be is talking to each other via PF.
 
  • #33
sophiecentaur said:
It's not the size of the job that counts, it's how it's achieved.
I think you're misunderstanding. Suppose we have a voltage surge from the power system. A spike high enough to damage equipment. So given any complex electrical device, how would you guess which component fails? Wouldn't it be the component electrically closest to the mains?

Sometimes we use a MOV, metal oxide varistor, closest to the mains to make a sacrificial surge suppressor. It is shown as VAR in the circuit below. So if VAR is missing, what else would you expect to fail first?

1639924544602.png
 
  • #34
Also recognize that you can often avoid putting a fuse in your circuit if you design (and test) the transformer to fail safely. This is done by melting the primary windings. So, it's not always the transformers fault.
 
Last edited:
  • #35
anorlunda said:
I think you're misunderstanding.
No. It is you who is misunderstanding my questions and comments. I am well aware of possible failure modes and possible causes and I think you know the engineering is not the issue.

It is possible to transport a take a drone to Mars and to fly it on the surface of Mars many times. If it failed to take off then would there be any use in explaining to me that a component failed because it had not been suitably specified and built? My question was about the choice of a manufacturing system that (so the story goes) delivers faulty / inadequate transformers for equipment. We all know that one could be made to last for hundreds of years under almost any conditions.

We all have the right to moan and complain about shortcomings in equipment and that's what I am doing. Could I do better? Yes - given time and a suitable price.
 

Similar threads

Replies
3
Views
1K
  • Electrical Engineering
Replies
18
Views
2K
  • Electrical Engineering
Replies
7
Views
6K
Replies
26
Views
2K
  • Electrical Engineering
Replies
21
Views
4K
  • Electrical Engineering
Replies
11
Views
1K
  • Electrical Engineering
Replies
10
Views
2K
Replies
70
Views
9K
  • Electrical Engineering
Replies
2
Views
1K
Replies
62
Views
3K
Back
Top