Why do AC motors pull high amps when they go bad?

In summary, an AC motor will pull excessively high amps when it goes bad due to a short circuit or bearing failure.
  • #1
timmeister37
124
25
TL;DR Summary
Why do Alternating Current motors pull high amps when they go bad?
I used to work in HVAC. There are three main types of alternating current (AC) motors in residential air-conditioners and heat pumps: outdoor fan motors, compressors, and indoor blower motors. All three types of AC motors have the maximum number of amps stated on the nameplates of the units. When any of these three types of AC motors used in residential HVAC go bad, the AC motors start pulling higher amps than the maximum number of amps on the nameplate of the unit.

Why do AC motors start pulling excessively high amps when they go bad?
 
Engineering news on Phys.org
  • #2
timmeister37 said:
Why do AC motors start pulling excessively high amps when they go bad?

I am not familiar with AC motors.

Is it possible that the rotation speed is reduced or even stopped due to excessive rotational friction, which causes the current to rise as the back EMF decreases? 🤔
 
Last edited:
  • Like
Likes russ_watters and timmeister37
  • #3
Some possibilities:

Disassemble a failed AC motor and look closely at the stator winding for signs of a short circuit. The stator winding for each pole consists of a number of coils placed in successive stator slots. These coils are connected in series, and overlay each other. One coil can short to the next coil. This reduces the total number of turns for that pole winding, which increases the current.

A single phase motor can have a starting switch or starting winding fail. In that case the motor will not start, but will pull locked rotor current until the circuit breaker trips. Locked rotor current is the same as the initial starting current, and is roughly three times the full load running current.

Bearing wear or failure causing the rotor to drag on the stator, overloading the motor.

A normal AC induction motor will deliver up to about three times its rated full load power, but only for a short time until it overheats. The full load power rating is the maximum power at which it will not overheat.

I had a summer job out of high school in an electric motor rebuild shop and saw many failed motors.
 
  • Like
  • Informative
Likes anorlunda and russ_watters
  • #4
alan123hk said:
I am not familiar with AC motors.

Is it possible that the rotation speed is reduced or even stopped due to excessive rotational friction, which causes the current to rise as the back EMF decreases? 🤔
That sounds plausible. I wish an EE here would verify it though.
 
  • #6
The most common failure is a short circuit between two turns of one coil. That changes a winding designed to be an electromagnet, into an autotransformer with a short circuited secondary.

Since the resistance of the shorted secondary is very low, a large current flows, that heats the wire and causes more shorts to occur. The current drawn by the motor rises rapidly once the first shorted turn occurs.

The number of primary turns and the inductance of the coil is reduced by the short, so the primary current increases. That is even without the primary current needed to support the shorted secondary current.
 
  • Informative
Likes Tom.G
  • #7
alan123hk said:
I am not familiar with AC motors.

Is it possible that the rotation speed is reduced or even stopped due to excessive rotational friction, which causes the current to rise as the back EMF decreases? 🤔

Would the decreasing of the back EMF directly cause the current to increase?
 
  • #8
timmeister37 said:
Would the decreasing of the back EMF directly cause the current to increase?
That would be true of any AC winding.

These AC motors are induction motors. They employ fixed field coils that generate a rotating magnetic field, which drags the rotating conductive armature around with the field. Those motors are designed to have a slip under load, of about 5% below synchronous speed.

Excessive rotor friction due to bearing problems, will increase the power consumption. But the extra power consumed will be dissipated in the bearings leading to mechanical failure. Where bearing failure allows the poles of the field to contact the rotor, the field can be heated through friction with the rotor. The mechanical vibration can then damage the field windings.

A shorted conductive turn in the field allows an equal and opposite current to flow in that turn. That current causes an equal and opposite magnetic field that cancels the wanted field. The reduction of magnetic field reduces the available motor power and heats the field windings further.

As motor current begins to increase, a cascade of catastrophic failures follow, that quickly destroys the motor.
 

1. Why do AC motors pull high amps when they go bad?

When an AC motor goes bad, it means that there is a problem with the internal components of the motor. This can include issues with the wiring, bearings, or other mechanical parts. As these components start to fail, they can cause an increase in resistance, which leads to the motor pulling higher amps in order to maintain the same level of power output.

2. Can high amps be a sign of a failing AC motor?

Yes, high amps can be a clear indication that an AC motor is starting to fail. As mentioned before, an increase in resistance due to faulty components can cause the motor to pull higher amps. This can also lead to overheating and other issues, which can further damage the motor.

3. How can high amps affect the performance of an AC motor?

High amps can have a negative impact on the performance of an AC motor in several ways. Firstly, it can cause the motor to overheat, which can damage the internal components and reduce its overall lifespan. It can also lead to a decrease in efficiency, as the motor has to work harder to maintain the same level of power output.

4. What are some common causes of high amps in AC motors?

There are several potential causes of high amps in AC motors. These can include issues with the wiring, such as loose connections or damaged insulation, as well as problems with the bearings, such as lack of lubrication or wear and tear. Other common causes can include a faulty capacitor, a damaged rotor, or a malfunctioning control circuit.

5. Is it possible to prevent AC motors from pulling high amps?

While it may not be possible to completely prevent an AC motor from pulling high amps, there are steps that can be taken to minimize the risk. Regular maintenance and inspections can help identify and address any potential issues before they escalate. It is also important to ensure that the motor is properly sized for the intended application, as an undersized motor may be more prone to pulling high amps.

Similar threads

  • Electrical Engineering
Replies
21
Views
3K
Replies
28
Views
1K
Replies
33
Views
3K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
9
Views
1K
Replies
16
Views
3K
  • Electrical Engineering
Replies
19
Views
3K
  • Electrical Engineering
Replies
4
Views
1K
Replies
15
Views
3K
Replies
4
Views
2K
Back
Top