The discussion centers on the confusion surrounding horsepower ratings for air conditioning units, specifically those from manufacturers like Carrier and Panasonic. It highlights a discrepancy where a 1.5 horsepower air conditioner is listed with a cooling output of 13,000 KJ/h, equivalent to 12,000 BTU/h, yet calculations suggest it should have a higher horsepower rating of 4.7. Participants clarify that the 1.5 horsepower refers to the input mechanical work, not the cooling output, which can be expressed in various units like watts or BTUs. The conversation also addresses concerns about energy conservation, explaining that the input electrical energy is not the sole energy source for cooling. Ultimately, the discussion emphasizes the importance of understanding the difference between input power and cooling output in HVAC systems.
riezer
Messages
58
Reaction score
0
A manufacturer like Carrier or Panasonic listed their 1 Horsepower Aircon as having 9,500 KJ/h and 1.5 Horsepower Aircon as 13,000 KJ/h. But it doesn't tally with the BTU conversion.

1 ton refrigeration = 12000 Btu/Hour = 12,661 kJ/Hour = 3.517 kW

now 1 watt = 0.00134102209 horsepower therefore 3.517 kW = 4.7 Horsepower!

But the Carrier/Panasonic manufacturer listed 1.5 Horsepower Aircon has having 13,000 KJ/hour which is equivalent to 12000 Btu/Hour or 1 ton. Yet calculation of this data show 4.7 Horsepower. Why did Carrier/Panasonic, etc. listed them as 1.5 Horsepower Aircon?

I've been searching in net for this for hours but can't find the reason. Anyone got any idea why?
 
Engineering news on Phys.org
1.5 hp is the input mechanical work, not the cooling output.
 
russ_watters said:
1.5 hp is the input mechanical work, not the cooling output.

You mean 3517 Watts (equivalent to 4.7 Hp) is the cooling output? Can you use watts as cooling output (the input being 1.5 hp as you mentioned)?
 
Yep. And power is power - you can use watts, horsepower, btu/hr, tons etc.
 
If the input is 1.5 HP (1200 watts) and the output is 4.7 HP (3517 watts). Doesn't it violate law of conservation of energy because the output is greater than the input?
 
No. The input electrical energy isn't the only energy input. Please read Chris's link...
 