Surprising HVAC Lesson: Air Conditioning Costs in Philly vs. Vegas

AI Thread Summary
Air conditioning costs in Philadelphia are significantly higher than in Las Vegas due to differences in enthalpy and humidity levels. In Philadelphia, the design conditions result in an enthalpy of 39.0 btu/lb, while in Las Vegas, it is lower at 33.0 btu/lb, indicating that it is 18% hotter in Philly on a typical August day. This difference means that cooling requires 57% more energy in Philadelphia compared to Las Vegas. The closer the dry and wet-bulb temperatures are, the more energy is needed for conditioning. Understanding these factors is crucial for HVAC system design and energy cost calculations.
Messages
23,695
Reaction score
11,137
One of the guys I work with is taking a course in HVAC and since my boss used to teach it, we got a little lesson today (helping with the homework). The result of the conversation was the realization that it costs significantly more to air condition a building in Philadelphia than it does in Las Vegas. Surprising, huh? Here's the math though:

Indoor design conditions are for 75F and 50% relative humidity. That corresponds to an enthalpy of about 28.5 (btu/lb). In Philly, the design conditions (from NOAA data) are 92F dry bulb and 75F wet bulb (that's about 48% relative humidity). That corresponds to an enthalpy of 39.0. In Vegas, the conditions are 112F wb and 68F db (about 8% rh). Thats an enthalpy of about 33.

So the difference between the two enthalpies means its 18% hotter! in Philly than in Vegas on a typical August day and requires 57% more energy (10.5 vs 4.5 btu/lb of air) to cool outside air (your house is more complicated since much of the load is actually solar).
 
Engineering news on Phys.org
Not bad on your explanation. When I design systems and calculate annual energy costs, a good rule of thumb to use is the closer the dry and wet-bulb temperatures are to each other, the more energy you'll use to condition the space. Air conditioning systems cool 'sensibly' first, ie they change the dry bulb temperature. The last thing that they do is remove moisture, ie they drastically change the enthalpy, humidity, etc. Here in Houston, the design dry bulb is 96 and the wet bulb is 79 (depending on the source)--a resulting enthalpy over 42 btu/lbm!

Let me know if you have any further questions on the matter. The subject is still pretty fresh in my mind--I just took my Mechanical PE exam a few months ago.
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...