How Does a Step Up Transformer Illustrate the Conservation of Energy?

  • Thread starter Thread starter XPTPCREWX
  • Start date Start date
  • Tags Tags
    Transformer
AI Thread Summary
A step-up transformer illustrates the conservation of energy by converting input voltage into higher output voltage while maintaining power balance, where energy out is always less than energy in due to inherent losses. The transformer operates by changing the load impedance through its turns ratio, affecting the current and voltage relationship. In a 1:2 step-up transformer, the output load impedance is transformed to an equivalent lower impedance at the input, requiring increased input current to maintain power equivalence. This results in higher voltage and lower current at the output, demonstrating that energy cannot be created from nothing. The discussion emphasizes the importance of understanding these principles, especially in contexts like superconductors, where traditional resistance concepts may differ.
XPTPCREWX
Messages
101
Reaction score
0
It is understood that you cannot have something from nothing, but how is this the case with a step up transformer? It seems that stepping up the voltage is stepping up the potential energy and since more windings actually increase the resistance there will be lower current which is how most people explain the conservation of energy in this situation, however what would happen in the case of a superconducter?
 
Engineering news on Phys.org
You step up voltage not energy. Energy out is always less than energy in.
 
XPTPCREWX said:
It is understood that you cannot have something from nothing, but how is this the case with a step up transformer? It seems that stepping up the voltage is stepping up the potential energy and since more windings actually increase the resistance there will be lower current which is how most people explain the conservation of energy in this situation, however what would happen in the case of a superconducter?

Just to add a little to Pumblechook's answer... In the case of the step-up transformer, the signal source driving the transformer "sees" the output load impedance attached to the transformer, but it sees it through a ratio related to the transformer turns ratio.

So say you have a 1:1 transformer, with a signal source (and source impedance) connected to the input of the transformer, and a load impedance Z connected to the transformer output. The signal source is driving the magnetizing inductance of the transformer, in parallel with the load Z, because for the 1:1 transformer, the output load is transformed to an equivalent input parallel load directly by that 1:1 ratio.

But if you use a 1:2 step-up transformer, the load impedance Z is transformed across to an equivalent load of Z/4 in parallel with the input of the transformer (the load transforms across by the square of the turns ratio). So if the signal source has a low enough output impedance compared to that load impedance, it will drive about 4X the current through that equivalent load, in order to be able to support twice the output voltage at twice the output current (4X the power). So if you want to get twice the voltage out of a transformer (which also doubles the current through the load Z), you need to drive more input current, and hence the input and output powers are the same (actually less at the output for a real transformer with losses).

The more traditional way of stating all of this is to make the load lighter for the 1:2 step-up case (Z --> 4*Z) , and then you can say that you have twice the output voltage (compared to a 1:1 transformer), and half the current. That is the equivalent power case.
 
Last edited:
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...