Alternator in parallel new critical clearing time

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
1 reply · 1K views
jaus tail
Messages
613
Reaction score
48

Homework Statement


upload_2018-2-3_9-50-7.png


Homework Equations


critical clearing time proportional to square root of (H / (P times frequency) ) equation 1
Power remains same as alternator at 1p.u
Frequency is also same
H will increase.
It's not given so we can assume machines swing together, so H = H1 + H2 = 2H since they are identical.
If machine wouldn't swing together it'd be H1. H2/ (H1 + H2)

The Attempt at a Solution


So now we get from equation 1 time(clearing) proportional to Square root of H
So 0.4/(new tcr) = (square root of (H/2H) = 0.707
So new tcr = 0.567sec
Answer is D
Book answer is B
How?
 

Attachments

  • upload_2018-2-3_9-50-7.png
    upload_2018-2-3_9-50-7.png
    8.6 KB · Views: 747
Physics news on Phys.org
There's an ambiguity in the problem statement. Are the two generators the same size as the original generator, or are the two both half the size (rating) as the original one? It also doesn't say what the per unit base the 0.5 power is based on, system or generator? System is the usual base.

But with the most likely interpretations, I agree with you: D.
 
  • Like
Likes   Reactions: jaus tail