Do you mean that you have a load that requires 27kW for 3 hours continuous? (I will assume a yes)
So the load demand that you are talking about is 27X3 = 81kWh
Alternator will supply 700 X 4 = 2800W, doesn't it? (2.8kW)
How many hours at 2.8kW is needed to charge a 60kWh battery bank? (60/2.8=21.4 hours : almost a day) The Batteries will last for 60/27 = 2.22 hour
You then need a source of 27kW for the remaining time and you only have 2.8kW from the alternator.
So, if that's you actual problem, it won't work.
Perhaps you meant something different from what I have understood. Where have I lost you in the above set of musings?
PS Battery and alternator connections needs to be right for the required load voltage. If the load takes 12V then the alternators need to be in parallel (and synchronised!) If they deliver DC then they will need to be regulated / matched fairly well.