Buckling of column connected to beam

Click For Summary
SUMMARY

The discussion focuses on the buckling behavior of a column connected to a beam, emphasizing the calculation of the moment of inertia (Ixx and Iyy) for the column rather than the beam. It is established that the beam provides lateral support at the midpoint of the column, effectively reducing its length against weak axis buckling to 3000 mm, while the major axis buckling remains at 6000 mm due to lack of support. The critical load for buckling is determined by the lesser of two calculated values, with the major axis buckling controlling due to a higher length-to-radius ratio.

PREREQUISITES
  • Understanding of column buckling theory
  • Knowledge of moment of inertia calculations (Ixx and Iyy)
  • Familiarity with axial load applications in structural engineering
  • Concept of effective length in buckling analysis
NEXT STEPS
  • Study the calculation methods for moment of inertia in structural sections
  • Learn about effective length reduction in columns with lateral support
  • Research the differences between weak axis and major axis buckling
  • Explore critical load determination methods for columns under axial loads
USEFUL FOR

Civil engineers, structural analysts, and students studying structural stability and buckling behavior in columns and beams.

foo9008
Messages
676
Reaction score
4

Homework Statement


In this question, we are interested inthe buckling of column, so we should calculate the moment of inertia (Ixx) or (Iyy) at the column,right?

Homework Equations

The Attempt at a Solution


Why the author calculate (Ixx) and (Iyy) using the cross sectional area of beam?
is it wrong?
And for critical load applied at y-axis (Pcr_y) , why the Le used is 3000 , why not 250mm?[/B]
 

Attachments

  • IMG_20160813_225055.jpg
    IMG_20160813_225055.jpg
    17.8 KB · Views: 535
Physics news on Phys.org
The author is using the column cross section in determining the buckling load of the column. The beam in the middle provides lateral weak axis column support at the column mid point.
 
  • Like
Likes   Reactions: foo9008
PhanthomJay said:
The author is using the column cross section in determining the buckling load of the column. The beam in the middle provides lateral weak axis column support at the column mid point.
do you mean the load is applied at the beam to detremine the buckling of column?
Since the column and beam are connected , so , we can use the Ixx or Iyy about the cross sectional area of beam to calculate the buckling of column?
 
Buckling loads in the usual sense are compressive axial loads. This problem asks what is the max compressive axial load that can be applied to the top of the column before it buckles. The cross section of the beam has nothing to do with the buckling of the column. The beams transfer vertical loads to the columns, yes, but the problem example wants to show how beams can reduce the effective length of the column when determining weak axis column buckling
 
  • Like
Likes   Reactions: foo9008
PhanthomJay said:
Buckling loads in the usual sense are compressive axial loads. This problem asks what is the max compressive axial load that can be applied to the top of the column before it buckles. The cross section of the beam has nothing to do with the buckling of the column. The beams transfer vertical loads to the columns, yes, but the problem example wants to show how beams can reduce the effective length of the column when determining weak axis column buckling
is It true that the load is applied in this direction?
uploadfromtaptalk1471131132083.jpg
 
Not true. The solution gives the max vertical load for P applied downward at the top of the column.
 
PhanthomJay said:
Not true. The solution gives the max vertical load for P applied downward at the top of the column.
do you mean the load is applied in this direction ?
 

Attachments

  • 0001.png
    0001.png
    536 bytes · Views: 459
PhanthomJay said:
Yes.
then , why we need to consider the moment of inertia about the cross sectional area of beam ? or i misunderstood something ? the 250mm x300mm is not cross sectional area of beam ?
 
  • #10
That is the cross section of the column, which should have been more clearly shown,
 
  • Like
Likes   Reactions: foo9008
  • #11
PhanthomJay said:
That is the cross section of the column, which should have been more clearly shown,
Can you explain why we need to consider the moment of inertia about the cross sectional area of beam? We are interested in the buckling of column, so we should consider the moment of inertia of the column, right?
 
  • #12
Yes , the dimensions given are for the column. You do not need to consider the cross section of beam.
 
  • Like
Likes   Reactions: foo9008
  • #13
PhanthomJay said:
Buckling loads in the usual sense are compressive axial loads. This problem asks what is the max compressive axial load that can be applied to the top of the column before it buckles. The cross section of the beam has nothing to do with the buckling of the column. The beams transfer vertical loads to the columns, yes, but the problem example wants to show how beams can reduce the effective length of the column when determining weak axis column buckling
why there are two force applied which is 771kN and 2138kN? only 1 force can be applied at the top and bottom portionof the column to determine the critical load of the column,right?
 
  • #14
That is correct. Critical load is determined by using the lesser of the 2 values calculated. In this case, major axis buckling controls due to the higher l/r ratio.
 
  • Like
Likes   Reactions: foo9008
  • #15
PhanthomJay said:
That is correct. Critical load is determined by using the lesser of the 2 values calculated. In this case, major axis buckling controls due to the higher l/r ratio.
can you explain why the Le for Pcr_y is 3000 ? i could only understand the Le for Pcr_x is 6000
 
  • #16
The middle beam provides lateral support at the column mid point on the weak axis direction. That cuts it's effective length in half against weak axis buckling. No such mid point support is provided against major axis buckling by this beam.
 
  • #17
PhanthomJay said:
The middle beam provides lateral support at the column mid point on the weak axis direction. That cuts it's effective length in half against weak axis buckling. No such mid point support is provided against major axis buckling by this beam.
,do you mean the beam divided the column into 2 parts?
 
  • #18
PhanthomJay said:
The middle beam provides lateral support at the column mid point on the weak axis direction. That cuts it's effective length in half against weak axis buckling. No such mid point support is provided against major axis buckling by this beam.
,do you mean the beam divided the column into 2 parts?
 
  • #19
PhanthomJay said:
No such mid point support is provided against major axis buckling by this beam.
you already said that the middle beam provides lateral support at the column mid point on the weak axis direction. That cuts it's effective length in half against weak axis buckling?
Why there's no support provided by this beam?
 
  • #20
The beam is pinned to the column at one end and at the other end of the beam it is connected to a wall or another column which is not shown in the figure. Once again the beam keeps the column from deflecting in the direction of that beam so it cannot bulge out and buckle at that point. But since the beam is pinned to the column at that point, it can't prevent the column from buckling about the major axis since the beam would just rotate and not provide support on that direction, only the other direction along the beam. Assuming ideal pins here. So in reprieve, effective length is 6000 for major
axis buckling and 3000 for minor axis buckling.
 
  • Like
Likes   Reactions: fonseh and foo9008
  • #21
PhanthomJay said:
The beam is pinned to the column at one end and at the other end of the beam it is connected to a wall or another column which is not shown in the figure. Once again the beam keeps the column from deflecting in the direction of that beam so it cannot bulge out and buckle at that point. But since the beam is pinned to the column at that point, it can't prevent the column from buckling about the major axis since the beam would just rotate and not provide support on that direction, only the other direction along the beam. Assuming ideal pins here. So in reprieve, effective length is 6000 for major
axis buckling and 3000 for minor axis buckling.
this seems an interesting topic to learn . You already said that the column cannot bulge out due to the pin . why for the bottom part , you said that the the beam can't prevent the column from buckling about the major axis ?
 
  • #22
PhanthomJay said:
The middle beam provides lateral support at the column mid point on the weak axis direction. That cuts it's effective length in half against weak axis buckling. No such mid point support is provided against major axis buckling by this beam.
The major axis here means the 6m ? We can see that there are 3 beam connected to the column(top , middle and bottom) , why you said that there's no No such mid point support is provided against major axis buckling by this beam?
 
  • #23
fonseh said:
The major axis here means the 6m ? We can see that there are 3 beam connected to the column(top , middle and bottom) , why you said that there's no No such mid point support is provided against major axis buckling by this beam?
Looks like the original posts have been deleted, but the beam provides lateral middle support against weak axis buckling, but about the major axis of the column, it does not, because the beam can rotate out of plane assuming a ball type pin connection, and thus cannot restrain the column in that direction.
 
  • #24
PhanthomJay said:
Looks like the original posts have been deleted, but the beam provides lateral middle support against weak axis buckling, but about the major axis of the column, it does not, because the beam can rotate out of plane assuming a ball type pin connection, and thus cannot restrain the column in that direction.
do you mean the middle beam can only support the weak axis buckling of beam until 3m only ?
So , we need to consider another case ( which is stronger axis buckling) for 6m column ?
 
  • #25
fonseh said:
do you mean the middle beam can only support the weak axis buckling of beam until 3m only ?
So , we need to consider another case ( which is stronger axis buckling) for 6m column ?
yes, correct.
 
  • Like
Likes   Reactions: fonseh

Similar threads

  • · Replies 15 ·
Replies
15
Views
4K
Replies
12
Views
3K
  • · Replies 47 ·
2
Replies
47
Views
27K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
10
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
10
Views
3K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 1 ·
Replies
1
Views
1K