Calculating Probability of Valve Failure in Q5: Exponential Distribution Model
  • Context: Graduate
  • Thread starter Thread starter abba02
    Failure Probability
The discussion focuses on calculating the probability of valve failure in Q5 using an exponential distribution model. The useful life of the valves is defined as a period from installation to 5 years, with failure rates (_λ) specified as _λ1 = _λ2 = _λ3 = 0.05, _λ4 = 0.267, and _λ5 = 0.189 (in years−1). The calculated probability of a loss of flow from the manifold within the first 3 years is confirmed to be P[F] = 0.08643, derived from the combined failure probabilities of the valves in series and parallel configurations.
  • Understanding of exponential distribution functions
  • Familiarity with probability calculations in reliability engineering
  • Knowledge of series and parallel system configurations
  • Basic mathematical skills for substitution and equation solving
  • Study the application of exponential distribution in reliability analysis
  • Learn about series and parallel system reliability calculations
  • Explore advanced topics in stochastic processes
  • Investigate the implications of failure rates on system design
Engineers, reliability analysts, and anyone involved in the design and maintenance of valve systems, particularly in the context of failure probability assessments and reliability modeling.
abba02
[SOLVED] probability of failure
The performance of the valves in Q5 has been assessed in more detail under conditions
closer to those experienced in-service and the distribution functions of the random time
to failure have been quantified. The useful life period, prior to wear-out, occurs from
installtion to 5years. During this period, all of the distribution functions are modeled
using an exponential distribution function of the form:
FT (t) = 1 − exp[−_λit] where i=1,2,3,4,5
If _λ1 = λ_2 = _λ3 = 0.05; λ_4 = 0.267; λ_5 = 0.189 (all in years−1), calculate the probability
of a loss of flow from the manifold sometime in the period (0,3)years.
ANSWER[P[F]=0.08643]
ATTEMPT
Have tried to substitute .05 for lambada and 3 for t in the given equation but my answer is still very different from the given answer of 0.08643
The attempt at a solution:
V1,V2 AND V3 ARE IN SERIES AND SS1 ARE IN PARALLEL TO V4 AND V5
(PV1 OR PV2 OR PV3) AND PV4 AND PV5
For PSS FT (t) =1- exp [-λ1+λ2+λ3*3] where t=3 = .36237
For PV4, FT (t) =1- exp [-λ4*3]=.55112
For PV5,FT (t) =1- exp [-λ5*3]= .43278
Therefore the probability of loss of flow from the manifold at time 3 years is
PSS1 AND PV4 AND PV5= .36237*.55112*.43278= .08643