Calculating Temp Rise in Conductor after Time t

AI Thread Summary
To calculate the temperature rise in a conductor after passing a current for a specified time, one must first determine the conductor's resistivity and cross-sectional area to find its resistance. The total energy dissipated can be calculated using the formula (current squared) multiplied by resistance. Knowing the heat capacity of the conductor allows for the estimation of temperature rise using the relationship between mass, specific heat, and total heat exchange. However, many factors, including surrounding temperature and proximity to other objects, can complicate accurate temperature calculations. For precise results, direct measurement is recommended, while simplifications can provide preliminary estimates.
Mahadev
Messages
12
Reaction score
0
I am passing Xamps thru a Ylenth of conductor for time t sec. can anybody suggest me how to calculate temperarure rise in the conductor after time tsec in a conductor
 
Engineering news on Phys.org
Sorry if I'm wasting your time but you can determine the resistivity of the conductor based on those factors.

Normally what i have seen are graphs of various materials vs power dissipation.

Here's info on a thermistor in the meanwhile. http://en.wikipedia.org/wiki/Thermistor
 
If you know the resistivity of the conductor,alongwith the cross sectional area,you can find the resistance as (resistivity)*length/area,then the total energy dissipated is (current)squared * resistance.

does that help?
 
lala_alak said:
If you know the resistivity of the conductor,alongwith the cross sectional area,you can find the resistance as (resistivity)*length/area,then the total energy dissipated is (current)squared * resistance.

does that help?

In addition, by knowing the heat capacity of the conductor we can calculate the temperature rise of the conductor from the dissipated power.

aaNg
 
Realistically temperature can only be calculated in ideal and over simplified situations. There are many factors which effect the final temperature so it is very difficult to consider them all. A very large factor in the temperature of any object is the the temperature of the surroundings and the proximity of other objects. You can calculate accurately total energy loss or gain, but that does not automatically get you temperature.

The best way to find the temperature of a system is to measure it.
 
lala_alak said:
If you know the resistivity of the conductor,alongwith the cross sectional area,you can find the resistance as (resistivity)*length/area,then the total energy dissipated is (current)squared * resistance.

does that help?


Sorry,
this gives only power loss. how you can calculate a temperature rise after some time t?
Mahadev
 
Integral said:
Realistically temperature can only be calculated in ideal and over simplified situations. There are many factors which effect the final temperature so it is very difficult to consider them all. A very large factor in the temperature of any object is the the temperature of the surroundings and the proximity of other objects. You can calculate accurately total energy loss or gain, but that does not automatically get you temperature.

The best way to find the temperature of a system is to measure it.

But ... engineering works by simplifying situation. Otherwise, we will never arrive anywhere :-)
 
Actually i am designing a new trip coil for MCB so i want to know the temperature rise.
thank you
 
I think the simplification can be used as a first/preliminary estimation.

We can calculate the estimated dissipated heat, then we can find the temperature rise if we know the heat capacity of conductor.

That's the estimation.

To refine the result, used experiment :-)

aaNg
 
  • #10
So once you multiply the power with time,you are left with the total energy,now you'll need the heat capacity of the material,i believe the overall relation is:

mass*specificheat*temperaturerise = total heat exchange.

I guess now you should be able to calculate the rise in temperature.
 
Back