Calculating Total Power and Power Factor for Parallel Loads in an AC Circuit

  • Thread starter Thread starter ridemx
  • Start date Start date
Click For Summary

Discussion Overview

The discussion revolves around calculating the total apparent power (S), real power (P), reactive power (Q), and power factor (PF) for three parallel loads connected to an AC source. The context includes homework-related problem-solving in electrical engineering, specifically focusing on power calculations in AC circuits.

Discussion Character

  • Homework-related
  • Mathematical reasoning
  • Technical explanation

Main Points Raised

  • The first participant outlines the problem and provides calculations for each load's S, P, and Q, noting a discrepancy when summing the total values.
  • Another participant introduces the concept of a Power Factor Triangle and questions the effect of adding a capacitor to an inductive load on the power factor.
  • A subsequent reply suggests that adding a capacitor will decrease the total reactive power (Q) and proposes a new total Q based on the individual loads' contributions.
  • One participant confirms the corrected total apparent power calculation, indicating a minor typographical error in the previous message.

Areas of Agreement / Disagreement

The discussion contains some agreement on the calculations after corrections, but there remains uncertainty regarding the initial summation of powers and the implications of adding capacitive loads to the circuit.

Contextual Notes

Participants express uncertainty about the correct method for summing the powers of different loads in parallel and the impact of reactive power adjustments on the overall circuit calculations.

Who May Find This Useful

This discussion may be useful for students and professionals interested in electrical engineering, particularly those studying AC circuit analysis and power factor correction techniques.

ridemx
Messages
5
Reaction score
0

Homework Statement



3 loads are connected to a source (1000Vrms, 60hz, 1 phase) in parallel
load 1:Inductive, 125kva, .28pf lagging
load 2:capacitive, 10kw, 40 kvar
load 3:resistive, 15kw

Find total S, P, Q, PF

Homework Equations



S=apparent (VA)
P=real (W)
Q=reactive (VAR)

S^2=P^2+Q^2
PF=P/S

The Attempt at a Solution



Using the above equations, I found the S,P,Q for all 3 loads as follows,

Load 1:
S=given=125kva
P=(125kva)(.28)=35kw
Q=sqrt[(125kva^2)-(35kw^2)]=120kvar

Load 2:
S=sqrt[(10kw^2)+(40kvar^2)]=41.23kva
P=given=10kw
Q=given=40kvar

load 3:
S=sqrt[(0^2)+(15kva^2)]=15kva
P=given=15kva
Q=0 since resistive

I added up all the P's Q's and S's to get

S=181.23kva
P=60kw
Q=160kvar

but then I checked myself using S^2=P^2+Q^2 and it doesn't work out

sqrt[(60kw^2)+(160kvar^2)]=170.9kva not 181.23kva

where did I screw up, can you not just add the loads?
 
Physics news on Phys.org
If you have an inductive load and you draw the Power Factor Triangle for it, and then you want to improve the Power Factor by adding in a capacitor, what will happen to the Power Factor Triangle?
 
Adding a capacitor to and inductive load, it will decrease total Q, I guess I never thought of it that way for some reason, but in that case would the Q's be

Load 1: 120kvar
Load 2: -40kvar
Load 3: 0

which gives a total of 80kvar, so:

circuit totals are
P=60kw
Q=80Kvar
S=sqrt[(60^2)+(80^2)]=100VA

Is this at all correct?
 
You mean S=sqrt[(60k^2)+(80k^2)]=100kVA, and yes this looks correct.
 
yep, that's definitely what I meant, more of just a typo. Thank a lot for the help!
 

Similar threads

  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
4K
Replies
8
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 8 ·
Replies
8
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K