Can anybody help with this power question?

  • Thread starter bear820301
  • Start date
  • Tags
    Power
In summary, In order to correct the power factor on a circuit with a power factor of 0.8, a capacitor must be added in series with the circuit.
  • #1
bear820301
1
0
Hi Guys,

This is my first post here. I am preparing for the EIT exam in October. I came across this practice problem during my review.

Question:
The circuit shown has a power factor of 0.8. What size capacitor must be added to this circuit to correct the power factor to 0.9?

Drawing1.jpg


(A) 10 kVAR in series
(B) 10 kVAR in parallel
(C) 13 kVAR in series
(D) 13 kVAR in parallel

It is easily calculated that the needed reactive power is ~13kVAR. However,the questions is about how to connect it: series or parallel.

I think 13kVAR shall be connected in parallel to ensure that the existing load still draws 50kW at 0.8pf (by maintaining the terminal voltage, given the load is a constant impedance). However, the answer provided is (C). I can see the point of choosing (C) if the load is a constant KVA load. But if this is true, (D) is also a a correct answer isn't it?

Let me know what you guys think.
 
Physics news on Phys.org
  • #2
I think 13kVAR shall be connected in parallel to ensure that the existing load still draws 50kW at 0.8pf (by maintaining the terminal voltage, given the load is a constant impedance).

Yes, you are correct. I can't imagine why the supplied answer was "C", other than a typo.
 
  • #3
It could be argued that the inductance in the circuit causing the power factor reduction, is in series with the resistance so the capacitance that must be added must also be in series. Another reason is that adding capacitance in parallel, but not enough to bring the power factor to unity, will raise the impedance, not lower it, reducing the power to the load.
 
  • #4
skeptic2 said:
Another reason is that adding capacitance in parallel, but not enough to bring the power factor to unity, will raise the impedance, not lower it, reducing the power to the load.

No, not really. When the supply is a voltage source (or at least approx a VS) then the load power is unchanged by the addition of a parallel capacitor. Yes the overall impedance is increased and the reactive power reduced, but that's kind of the point of PFC.
 
  • #5
After doing a little complex arithmetic, I must change what I posted earlier.

Adding -j13.3 in parallel to a series 50 + j12.5 (for pf = 0.8) results in an impedance of 3.53 - j13.2 or a magnitude of 13.7 KVA with a pf of 0.26.

So contrary to my earlier post the impedance goes down because the capacitance overwhelms the inductance. This means the KVA would increase, not decrease.
 
  • #6
skeptic2 said:
After doing a little complex arithmetic, I must change what I posted earlier.

Adding -j13.3 in parallel to a series 50 + j12.5 (for pf = 0.8) results in an impedance of 3.53 - j13.2 or a magnitude of 13.7 KVA with a pf of 0.26.

So contrary to my earlier post the impedance goes down because the capacitance overwhelms the inductance. This means the KVA would increase, not decrease.

My calculations are a little different.

For V=480 and P=50 kW at PF=0.8, I calculate Z = 2.949 + j 2.212 ohms for the initial load impedance.

For Q=13 KVAR I calculate the required parallel capacitor impedance is Zc = -j 17.72 ohms.

For the combined parallel impedance of the above I get, Zt = 3.716 + j 1.821 ohms.

As you can see the magnitude of the impedance has increased and it's angle has decreased (such that cos(phi) is now approx 0.9).
 
  • #7
A reactive current is not necessarily the inductive - it may be capacitive as well. There is nothing said also whether the active power should stay the same.
The reactive (supposedly inductive) power is now 12.5 kVar (50/80 X 100 = 62.5 - 50 = 12.5) slightly less than the capacitive power (from the possibly right C variant) of 13 kVar. Although the capacitor(s) in series with the load will bring its active power drastically down to about 1 tength of what it is now, but, maybe then, the resultant capacitive reactive power will yield the number 0.9?
 
Last edited:
  • #8
Yuri B. said:
A reactive current is not necessarily the inductive - it may be capacitive as well. There is nothing said also whether the active power should stay the same.
The reactive (supposedly inductive) power is now 12.5 kVar (50/80 X 100 = 62.5 - 50 = 12.5) slightly less than the capacitive power (from the possibly right C variant) of 13 kVar. Although the capacitor(s) in series with the load will bring its active power drastically down to about 1 tength of what it is now, but, maybe then, the resultant capacitive reactive power will yield the number 0.9?

No. You can't calculate the reactive power by just subtracting the real power from the apparent power like that.

It's VAR = sqrt(VA^2 - P^2), which give 37.5 KVAR reactive power!
 
  • #9
Yes, it is vector sum. (For PF 0.9 the reactive power here should be about 21kVAR).
 
Last edited:
  • #10
uart said:
My calculations are a little different.

For V=480 and P=50 kW at PF=0.8, I calculate Z = 2.949 + j 2.212 ohms for the initial load impedance.

For Q=13 KVAR I calculate the required parallel capacitor impedance is Zc = -j 17.72 ohms.

For the combined parallel impedance of the above I get, Zt = 3.716 + j 1.821 ohms.

As you can see the magnitude of the impedance has increased and it's angle has decreased (such that cos(phi) is now approx 0.9).

For V=480 and P=50 kW at PF=0.8, I calculate Z = 2.949 - j 2.212 ohms for the initial load impedance. 480^2 / [50000 + j37500] please note change in sign of reactance.

For Q=13 KVAR I calculate the required capacitor reactance is Zc = -j 17.72 ohms.

For the combined parallel impedance of the above I get, Zt = 2.281 - j 2.304 ohms. Calculation was done in Excel using the formula IMDIV(IMPRODUCT(COMPLEX(2.949,-2.212),COMPLEX(0,-17.72)),IMSUM(COMPLEX(2.949,-2.212),COMPLEX(0,-17.72))).

This impedance has a magnitude of 3.242 ohms for a total KVA of 71065.

As you can see the magnitude of the impedance has decreased and it's angle has increased (such that cos(phi) is now approx 0.704).
 
  • #11
skeptic2 said:
For V=480 and P=50 kW at PF=0.8, I calculate Z = 2.949 - j 2.212 ohms for the initial load impedance. 480^2 / [50000 + j37500] please note change in sign of reactance.

For Q=13 KVAR I calculate the required capacitor reactance is Zc = -j 17.72 ohms.

For the combined parallel impedance of the above I get, Zt = 2.281 - j 2.304 ohms. Calculation was done in Excel using the formula IMDIV(IMPRODUCT(COMPLEX(2.949,-2.212),COMPLEX(0,-17.72)),IMSUM(COMPLEX(2.949,-2.212),COMPLEX(0,-17.72))).

This impedance has a magnitude of 3.242 ohms for a total KVA of 71065.

As you can see the magnitude of the impedance has decreased and it's angle has increased (such that cos(phi) is now approx 0.704).

OK, granted that the question didn't explicitly say that the initial 0.8 PF was lagging.

However, given that the question say's that the power factor is to be corrected with the addition of a capacitor, is there some particular reason why you chose to assume that the initial PF was leading?
 
  • #12
I believe an inductive load does cause a lagging power factor.

480^2 / (50000 + j37500) = 2.949 - j2.212 The sign of the imaginary part changes when divided into a positive real.
 
  • #13
skeptic2 said:
The sign of the imaginary part changes when divided into a positive real.

Yes exactly, that's why we need a +ive imaginary part of the impedance (eg 2.949 + j2.212) to give rise to a lagging current.

Your load impedance of 2.949 - j2.212 corresponds to a leading current and hence a capacitive load.

The actual load in this question however is clearly NOT capacitive. The question clearly tells us that the addition of more capacitance will correct the power factor, not make it worse.
 
  • #14
"C" is typo as has been mentioned.

Reactive current now at 0.8 PF is 77A.
Reactive current at 0.9 will be 50A.
13 kVAR capacitor provides 27 A reactive.
Connecting the cap in parallel will bring the reactive current to 50 A and the PF to 0.9.
 

1. Can you explain the concept of power in scientific terms?

Power is defined as the rate at which work is done or energy is transferred. It is measured in watts (W) and is calculated by dividing the work done (in joules) by the time it takes to do the work (in seconds).

2. How does power differ from energy?

Power and energy are related concepts, but they are not the same. Energy is the ability to do work, while power is the rate at which energy is used or transferred.

3. How does power relate to force and velocity?

The relationship between power, force, and velocity is described by the equation P = F x v, where P is power, F is force, and v is velocity. This means that power can be increased by either increasing the force or increasing the velocity.

4. What are some real-life examples of power?

Some common examples of power include the power generated by a car engine, the power used by a light bulb, and the power produced by a wind turbine. Human activities, such as walking, running, and lifting objects, also require the use of power.

5. How can power be calculated or measured in a scientific experiment?

In a scientific experiment, power can be calculated by measuring the amount of work done in a given time period. This can be done by measuring the force applied and the distance over which the force is applied. Power can also be measured using specialized equipment, such as a power meter, which measures the rate of energy transfer.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
5K
  • Engineering and Comp Sci Homework Help
Replies
18
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
16K
  • Engineering and Comp Sci Homework Help
Replies
13
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Electrical Engineering
Replies
8
Views
1K
Back
Top