Can I twist the Connecting cable with the Connecting pipe?

  • Thread starter Thread starter Shervan360
  • Start date Start date
  • Tags Tags
    Ac Wire
AI Thread Summary
Twisting the electrical wire with the copper pipe for an AC installation is generally not safe and may violate local building codes, particularly if it involves passing through walls or windows. It's crucial to ensure that the wire is rated for outdoor use and can withstand environmental factors like sun exposure and moisture. Proper installation typically requires creating a vacuum in the system, which may necessitate professional help if you lack the necessary equipment. Using a licensed electrician is recommended to ensure compliance with the National Electrical Code and local regulations. Ultimately, investing in a professional installation is more cost-effective than dealing with potential damage or code violations later.
Shervan360
Messages
26
Reaction score
4
Hello,

I bought AC, so I need to connect a copper pipe and electrical wire from the indoor unit to the motor.
Can I twist the connecting cable(electrical wire) with the connecting pipe(copper pipe)?
Is it safe?

ac pipe.jpg


Screenshot 2024-04-03 054431.png
 
Engineering news on Phys.org
Safe? Not particularly.
Legal? Depends on your local building codes.
Passing the wire thru a wall or window as part of a permanent installation? Very likely against the National Electrical Code and the local code without meeting specific requirements and passing inspection.

Recommend you visit your local code enforcement office with photos, some sketches, and the documentation for the air conditioner.

Some things to consider:
Is the wire rated for outdoor use? Sun exposure, ozone, wet environment, local ambient temperature extremes. How will you stop rain from running along the wire and entering either the building or the equipment?

You would also need to pay attention to the temperature rating of the wire and the temperature of that pipe during operation. The pipe will not be at ambient temperature.

Doing it "right" is much cheaper than paying the insurance deductible from any damage!
 
  • Like
Likes dlgoff, berkeman and Shervan360
Tom.G said:
Safe? Not particularly.
Legal? Depends on your local building codes.
Passing the wire thru a wall or window as part of a permanent installation? Very likely against the National Electrical Code and the local code without meeting specific requirements and passing inspection.

Recommend you visit your local code enforcement office with photos, some sketches, and the documentation for the air conditioner.

Some things to consider:
Is the wire rated for outdoor use? Sun exposure, ozone, wet environment, local ambient temperature extremes. How will you stop rain from running along the wire and entering either the building or the equipment?

You would also need to pay attention to the temperature rating of the wire and the temperature of that pipe during operation. The pipe will not be at ambient temperature.

Doing it "right" is much cheaper than paying the insurance deductible from any damage!
Thank you, Our home doesn't have insurance.
 
I can be wrong, but my understanding is that part of the mounting procedure calls for creating a vacuum in the system. That's to make sure the R-whatever agent that will fill the inner volume is as pure as possible, and not mixed with the humid air that is in all tubes right now. At least that's how similar units (two different makes, but apparently the procedure was identical) were mounted at my house. Do you have a vacuum pump to do so? Because if not, it may be better to not install the AC by yourself.
 
As I recall, the mains are supposed to be connected into a separately mounted IP-something level external wiring box which serves the inside-outside connection. To be done by a licenced electrician.

The wire towards the indoor unit can be bundled together with the pipes, but the connection within the units are to be made by the (licenced AC-)tech installing the units and the pipes anyway.

So, actually there is nothing what you should/can do there.
 
Shervan360 said:
Thank you, Our home doesn't have insurance.
Many wealthy people underwrite their own risks (t's the cheaper way, statistically) but do you have enough reserves in your account? Or could you just 'walk away' from a disaster?
Tom.G said:
Passing the wire thru a wall or window as part of a permanent installation? Very likely against the National Electrical Code and the local code without meeting specific requirements and passing inspection.
Every wire / pipe 'goes through' a wall
A suitable sleeve or conduit would take care of this but the regs have to be followed or you could have to rip it all out. You seem to have paid for new equipment so why not get the right guy to do the installation?
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...