Can Outside Temperature Affect the COP of Air-Conditioning Systems?

  • Thread starter Thread starter rayc
  • Start date Start date
  • Tags Tags
    Cop
AI Thread Summary
The discussion centers on the impact of outside temperature on the coefficient of performance (COP) of air-conditioning systems, particularly in simulated studies for data centers. The user is exploring a modified definition of COP due to the lack of real-world data, raising concerns about negative COP values when outside temperatures drop below indoor temperatures. Responses indicate that a negative COP is not realistic, as no work is required to move heat from a warmer to a cooler environment, suggesting that the air conditioning unit would typically be turned off in such scenarios. Additionally, it is noted that even with a lower outside temperature, practical considerations may require the AC to remain operational if heat cannot escape through other means. The conversation emphasizes the importance of real-world data for accurate modeling of air conditioning performance.
rayc
Messages
2
Reaction score
0
Hi All,

I'm doing a study on effects of outside temperature on the energy efficiency of air-conditioning systems in computer server farms/data centers.

It will be a simulated study so I cannot use the standard definition of COP;

COP = heat removed / work

At the same time I also want to examine the effect of the outside temperature. There for I've been using the following derivable definition for COP;

COP = 1 / (Th/Tl - 1)

where Th = the temperature of the hot, outside environment
and tl is the temperature of the inside. cool environment.

The problem I have is that in certain places, the outside temperature will be lower than the inside temperature, giving me a negative value for COP?? Any comment on this, is a negative COP realistic given that I'm doing work to move heat from a warm environment to a cooler one? or is this incorrect?

any help is appreciated.
 
Physics news on Phys.org
Welcome to PF.
rayc said:
It will be a simulated study so I cannot use the standard definition of COP;

COP = heat removed / work
I don't understand that sentence: what does it being a simulated study have to do with using the definition of CoP?
At the same time I also want to examine the effect of the outside temperature. There for I've been using the following derivable definition for COP;

COP = 1 / (Th/Tl - 1)

where Th = the temperature of the hot, outside environment
and tl is the temperature of the inside. cool environment.

The problem I have is that in certain places, the outside temperature will be lower than the inside temperature, giving me a negative value for COP?? Any comment on this, is a negative COP realistic given that I'm doing work to move heat from a warm environment to a cooler one? or is this incorrect?
If you are doing a study and you want to make the results real-world relevant, I'd take data from a real air conditioner and build a performance model based on its real performance curve.
 
russ_watters said:
Welcome to PF. I don't understand that sentence: what does it being a simulated study have to do with using the definition of CoP?

This means that I cannot use the more atypical definition of COP (heat removed/work) as I have no actual data regarding how much work it takes to remove a given amount of heat for a given AC, under certain conditions.

russ_watters said:
If you are doing a study and you want to make the results real-world relevant, I'd take data from a real air conditioner and build a performance model based on its real performance curve.

It would be excellent to get this data, but I have had no luck locating the data for this, especially one that factors the condenser temperature. Thats why I was trying to base my work on the more general model, with possible rough adjustments to account in some way for
real-world ac's.
 
rayc said:
The problem I have is that in certain places, the outside temperature will be lower than the inside temperature, giving me a negative value for COP?? Any comment on this, is a negative COP realistic given that I'm doing work to move heat from a warm environment to a cooler one? or is this incorrect?
No work is required for heat to move from a warm to a cooler environment. Since the air conditioner would simply be turned off in these circumstances, there is no need or sense in trying to come up with a COP in that situation.

(Unless I am missing something here -- Russ knows this stuff better than I do.)
 
rayc said:
This means that I cannot use the more atypical definition of COP (heat removed/work) as I have no actual data regarding how much work it takes to remove a given amount of heat for a given AC, under certain conditions.

It would be excellent to get this data, but I have had no luck locating the data for this, especially one that factors the condenser temperature. Thats why I was trying to base my work on the more general model, with possible rough adjustments to account in some way for
real-world ac's.
Ok. One assumption that might be useful is that two air conditioners using the same refrigerant will have similar performance curves. The difficulty is in establishing the peak efficiency, but if you know roughly what type of AC unit you are talking about, you can find similar ones online.

I've gone into more detail on the subject recently, in this thread (including links to some manufacturer data and my own analysis): https://www.physicsforums.com/showthread.php?t=379749
 
Redbelly98 said:
No work is required for heat to move from a warm to a cooler environment. Since the air conditioner would simply be turned off in these circumstances, there is no need or sense in trying to come up with a COP in that situation.

(Unless I am missing something here -- Russ knows this stuff better than I do.)
Well, there is a difference is between the theory and the reality. The reality is that if the outside temperature is only a little below the inside temperature, heat won't flow fast enough, so you still may leave the AC on. To be more specific, a typical air conditioner delivers 55F air, so the outside temperature needs to be below 55F to turn off the A/C (assuming the AC unit can use 100% outside air), even though you are only shooting for an inside temperature of 70F.

Also, there may be a situation where there is no path for heat to flow from inside to outside except through the air conditioner (ie, for a network closet the middle of a middle floor of an office building).
 
Thread 'Question about pressure of a liquid'
I am looking at pressure in liquids and I am testing my idea. The vertical tube is 100m, the contraption is filled with water. The vertical tube is very thin(maybe 1mm^2 cross section). The area of the base is ~100m^2. Will he top half be launched in the air if suddenly it cracked?- assuming its light enough. I want to test my idea that if I had a thin long ruber tube that I lifted up, then the pressure at "red lines" will be high and that the $force = pressure * area$ would be massive...
I feel it should be solvable we just need to find a perfect pattern, and there will be a general pattern since the forces acting are based on a single function, so..... you can't actually say it is unsolvable right? Cause imaging 3 bodies actually existed somwhere in this universe then nature isn't gonna wait till we predict it! And yea I have checked in many places that tiny changes cause large changes so it becomes chaos........ but still I just can't accept that it is impossible to solve...