Current & Potential Polarization for Directional Relays

Click For Summary
SUMMARY

The discussion focuses on the mechanisms of current and potential polarization for directional phase relays, specifically referencing "Power System Relaying" by Stanley H. Horowitz and Arun G. Phadke. It clarifies that the direction of a fault is determined by analyzing the phase difference between voltage and current, rather than instantaneous values. For potential polarization, the zero sequence voltage across a grounded wye-grounded/open-delta voltage transformer indicates fault proximity but not direction. In current polarization, the flow direction is established by the sign of the current in the neutral of a wye-grounded/delta transformer.

PREREQUISITES
  • Understanding of directional phase relays
  • Knowledge of zero sequence voltage in power systems
  • Familiarity with wye-grounded and delta transformer configurations
  • Basic principles of AC current and phase relationships
NEXT STEPS
  • Research the role of zero sequence voltage in fault detection
  • Study phase difference measurement techniques in power systems
  • Explore the implications of current flow direction in AC systems
  • Learn about the design and operation of wye-grounded and delta transformers
USEFUL FOR

Electrical engineers, power system analysts, and professionals involved in relay protection and fault analysis will benefit from this discussion.

jegues
Messages
1,085
Reaction score
3
Hello all,

I've been reading up on both potential and current polarization for directional phase relays in, "Power System Relaying" by Stanley H. Horowitz and Arun G. Phadke and I am confused as to how the direction of the fault (i.e. into or out of the line) is obtained.

In potential polarization they mention how a grounded wye-grounded/open-delta voltage transformer is and the polarization potential is connected across the open-delta.

For a ground fault, zero sequence voltage of 3Eo will be present across the open delta connection, but how does this indicate direction, that is, whether the fault is into our out of the line? The magnitude of the zero sequence voltage will be larger if the fault is closer in, but it still does not tell me on which side the fault resides. How is this deduced?

In current polarization they discuss how they use the current in the neutral of a wye-grounded/delta power transformer. They then go on to say, "If the current is positive, current flows up the neutral; if negative it flows down the neutral."

This is AC current we are talking about right, so it oscillate back and forth at the system frequency right? Are they implying the direction of power flow when they refer to positive or negative current? What is considered positive current and what is considered negative and what is the basis for these designations?

Thanks again!
 
Engineering news on Phys.org
jegues said:
This is AC current we are talking about right, so it oscillate back and forth at the system frequency right? Are they implying the direction of power flow when they refer to positive or negative current? What is considered positive current and what is considered negative and what is the basis for these designations?

Yes the voltages and currents reverse direction every cycle, but the power flow does not. That unambiguously determines direction.

Anyhow, we measure direction of current flow by comparing the phase difference between V and I. We do not look a instantaneous values.
 
  • Like
Likes   Reactions: Asymptotic

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 19 ·
Replies
19
Views
6K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 26 ·
Replies
26
Views
7K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 3 ·
Replies
3
Views
4K