Dehumidifier from a walk-in freezer unit?

  • Thread starter Thread starter makeitshine2
  • Start date Start date
  • Tags Tags
    Dehumidifier Unit
AI Thread Summary
Using a freezer compressor and condenser for a dehumidification kiln is feasible but presents challenges due to the system's temperature dynamics. The evaporator typically operates at very low temperatures, making it prone to frosting, which can hinder performance. Balancing airflow is crucial to ensure sufficient cooling for condensation without freezing the water on the coils. Incorporating a defrost cycle could enhance functionality, while utilizing the condenser heat for warming the kiln may improve overall efficiency. Access to the system's operating points and design pressures is essential for optimizing performance.
makeitshine2
Messages
2
Reaction score
0
I have 2 each 1-1/2 ton refrigeration units for a walk-in freezer. I would like to build a dehumidifation kiln to dry lumber. Each unit would freeze an 8' x 10' freezer to -20 degrees.

How hard would it be to use a freezer compressor and condensor as a dehumidifier? How would it work?

Thanks for your help!

Bill
 
Engineering news on Phys.org
Welcome to PF.

The difficulty here is that the temperatures generated at each coil are largely a function of the physical properties of the refrigeration system: the refrigerant, its pressure and the compression ratio. As a result, your evaporator is going to "want" to be at -30 or so and it will be very hard for you to keep it from frosting over.
 
Russ,

The condensor for a freezer has heat strips built-in and will run a defrost cycle as programmed. Would this be enough?

I also have a condensor that is refrigeration. (for a walk-in refrigerator) Perhaps I could match that with the compressor unit!

Thank You,
Bill
 
What is the operating temperature of this "kiln" going to be? It would be a balancing act, but it may be possible for this to work if you have enough airflow and temperature to keep the leaving refrigerant temperature high and the condensation from getting too cold. You'll want to strike a balance, having little enough airflow that it gets cooled enough to condense water but enough airflow that it doesn't freeze the water on the coils.

Are you using this system as the only source of heat/dehumidification for the system? Ie, are you using the condenser heat to warm the "kiln" while using the evaporator to dehumidify it?

A periodic defrost cycle would certainly help.

Whatever parts you use, do you have access to the operating points of the cycle, meaning the design pressures? That would help a lot in figuring out how to make the performace work.
 
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...