Delta motor behaviour on loss of phase

Click For Summary

Discussion Overview

The discussion revolves around the behavior of delta-connected motors when one phase is lost, either due to a broken winding connection or a broken supply connection. Participants explore the implications of these scenarios on motor current, torque distribution, and protection mechanisms, with a focus on both theoretical and practical aspects of motor protection schemes.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant describes the effects of losing a phase via a broken winding connection, noting that unbalanced voltage lowers the speed-torque curve and results in increased current draw from the remaining phases.
  • Another participant adds that if a motor loses a supply connection, it will operate in a single-phased condition, leading to audible complaints and a decrease in torque, requiring the other motor to compensate.
  • It is mentioned that the motors connected by a gearbox will not share torque equally due to the fault, with the faulted motor behaving like a lightly loaded motor.
  • One participant suggests that DOL overload relays typically include phase loss protection, which would activate if the phases are not carrying equal current.
  • Another participant references an article discussing the behavior of currents in delta-connected motors during phase loss, highlighting that the vector current addition changes and may lead to decreased supply line currents in certain scenarios.

Areas of Agreement / Disagreement

Participants express varying views on the implications of phase loss, with some focusing on the technical details of current behavior and protection mechanisms, while others emphasize the operational impacts on the motors. No consensus is reached on the overall effects or best practices for addressing these scenarios.

Contextual Notes

Participants note the complexity of the interactions between the motors and the gearbox, as well as the limitations of existing protective measures. There are references to specific technical documents that may provide further insights, but the discussion remains open-ended regarding the best approaches to motor protection in these situations.

Who May Find This Useful

This discussion may be of interest to electrical engineers, motor protection specialists, and those involved in the design and maintenance of motor control systems, particularly in industrial applications.

herban
Messages
1
Reaction score
0
Hi all,
I am trying to develop a motor protection scheme for the following scenario.
There are two 3.3kV 250kW delta connected motors close coupled to a gearbox driving a crusher.
Both have separate DOL starters and protection systems.
What happens to the motor current in a motor that loses a phase (1) via a broken winding connection and (2) via a broken supply connection.
I know what happens for a single motor in both of these situations but am not sure in a situation where the rotor of the motor is being driven by the other motor via the close coupled gearbox.
 
Engineering news on Phys.org
No suggestions yet ?

You probably have more expertise than me, so i'll only venture a qualitative guess.

herban said:
What happens to the motor current in a motor that loses a phase (1) via a broken winding connection

Unbalanced voltage lowers the speed-torque curve.

So in both cases the faulted motor will slow down a little. .
And the remaining phases will draw more current.
But you knew that already.
As the system slows, the good motor's operating point moves up its torque curve so it'll draw more current because it's delivering the lion's share of the total torque.
(2) via a broken supply connection.
Wow now that motor is single-phased. It should really complain audibly...
Likewise its torque will go down and the other motor will have to make up the slack...

This article has interesting explanation of what happens to currents in a delta connected motor when a phase opens either internally or externally.
I think that was your original question...
Though the individual motor winding currents increase, the vector current addition is no longer 120 degrees.
For the internal open phase, current in the supply lines may actually go down ...
Look at the section "Thermal protection and operation in case of phase loss", starting at page 32(of document, 33 of PDF file) here:
http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/5e6a1c128ae4fab1c1257b490033f301/$file/1SDC007106G0201.pdf

now to your real question:
The motors being connected by a gearbox just locks their speed. One with the fault experiences a downward shift of its speed-torque curve, the other does not. So they no longer share torque equally. So the faulted motor will behave like a faulted motor that's lightly loaded.

I'm not a relay guy. The reading i did tells me they use negative sequence to protect against phase loss, which makes perfect sense. One of the items i stumbled across was a Westinghouse instruction brochure for their offering... can't seem to find it again, but here's a GE introductory leaflet:

https://www.gedigitalenergy.com/multilin/family/motors/principles4.htm
Unbalance Protection
Unbalanced load in the case of AC motors is mainly the result of an unbalance of the power supply voltages. The negative-sequence reactance of the three-phase motor is 5 to 7 times smaller than positive-sequence reactance, and even a small unbalance in the power supply will cause high negative sequence currents. For example for an induction motor with a staring current six times the full load current, a negative sequence voltage component of 1% corresponds to a negative sequence current component of 6%. The negative-sequence current induces a field in the rotor, which rotates in the opposite direction to the mechanical direction and causes additional temperature rise. Main causes of current unbalance are: system voltage distortion and unbalance, stator turn-to-turn faults, blown fuses, loose connections, as well as faults.

any help? You already knew all the above , i'll wager.

old jim
 
Last edited by a moderator:
I don't think you need to worry about the motor, all you need to know is only two phases will be carrying current in both scenarios. Most DOL overload relays have a feature called phase loss protection. The DOL overload relay should trip/activate if the 3 phases are not carrying equal current.
 

Similar threads

Replies
12
Views
4K
  • · Replies 4 ·
Replies
4
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 6 ·
Replies
6
Views
4K
Replies
5
Views
6K
Replies
1
Views
8K
  • · Replies 8 ·
Replies
8
Views
11K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 12 ·
Replies
12
Views
5K