Motor wiring - will phases be unbalanced?

Click For Summary

Discussion Overview

The discussion revolves around the implications of connecting a single-phase load to one of the phases of a three-phase motor circuit, particularly focusing on potential imbalances and the protective role of miniature circuit breakers (MCBs). The scope includes theoretical electrical concepts and practical considerations regarding motor operation and load management.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant suggests that connecting a single-phase load to one of the motor feed phases could cause an imbalance in the motor, potentially leading to damage, especially during surges when the MCB may not provide adequate protection.
  • Another participant argues that according to Kirchhoff's law, the motor would remain balanced as it would draw the same current, with any excess current going to the additional load, and the MCB would trip if the current exceeds 10A.
  • A participant questions whether connecting a load across one phase could lead to a voltage drop on that phase, which might unbalance the motor, although they acknowledge this could apply to both circuit configurations discussed.
  • Another response indicates that if the supply is from a grid, the load is unlikely to significantly affect the voltage on one phase, but acknowledges that cable length and current could contribute to phase imbalance.
  • One participant notes that aside from line resistance issues, the MCB functions as a short circuit when operational, suggesting that the additional load on one phase should not affect the motor, although a smart MCB might react to differing currents by tripping.

Areas of Agreement / Disagreement

Participants express differing views on whether connecting a single-phase load to one phase of a three-phase motor will cause an imbalance or damage. There is no consensus on the implications of this connection, and the discussion remains unresolved.

Contextual Notes

Limitations include assumptions about the electrical supply and the characteristics of the MCBs involved, as well as the potential impact of line resistance and cable length on phase balance.

Who May Find This Useful

Individuals interested in electrical engineering, motor control systems, and circuit protection may find this discussion relevant.

BMcN
Messages
11
Reaction score
0
Ok an easy post to settle a discussion. I have posted two rough diagrams below. One shows a 3 phase motor connected directly to the supply through a 10Amp MCB for protection and a second single phase load connected via an MCB again.

Now in theory if I was remove the 2nd MCB and connect the single phase load to one of the motor feed phases after the MCB - what impact would this have?


One person says that it will cause an imbalance on motor and potentially damage it. It may also damage the motor during a surge as the MCB would not protect it properly.

Other theory is that the motor will remain in balance due to Kirchhoff law, so the motor will still draw exactly the same current and the remainder of the current will go to the second load if connected. If the current on any phase exceeds 10A the MCB will trip and protect both device.


Please note this is purely a theory based question, not a regulations one as these may differ from place to place.

s6nkzt.jpg


m9yjow.jpg
 
Engineering news on Phys.org
Electrically, MCBs are nothing more than a short when they are in operation. So, electrically, both diagrams are exactly the same. Only, the protection part is compromised in the second diagram.
Overloading or shorts in the motor will not only shut down the motor but also the 'Load'. And the reverse is also true. If you can compromise that, nothing is wrong.
 
Thanks.

Would it be correct to say that connecting a load across one phase could cause a volt drop on that phase, which would unbalance the motor, however this would be true in both versions of the circuit shown?
 
Assuming that your supply comes from a grid then your load isn't likely to pull down the voltage on one phase. However depending on the current and length of cable from your incoming JB and the point that you take the load off you might get a phase imbalance.
 
Except for line resistance issues, the MCB is a short (unless is pops!), so having the extra load on one leg won't bother the motor one bit. The only issue (other than imbalanced line resistance) is that a smart MCB may think something is fishy about the different current on one leg and decide to pop, anyway.

As always, never alter or access electrical equipment without professional understanding of all safety issues.
 

Similar threads

Replies
28
Views
4K
Replies
2
Views
5K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 6 ·
Replies
6
Views
8K
Replies
4
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 14 ·
Replies
14
Views
7K
  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 41 ·
2
Replies
41
Views
19K