Detection of inter-turn winding-short fault in 1-phase transformer

Click For Summary
SUMMARY

The discussion focuses on the detection of inter-turn winding short-circuit faults in single-phase transformers. It highlights that during such faults, the fundamental component of the no-load current increases while the Total Harmonic Distortion (THD) decreases, indicating an improvement in THD. This phenomenon is attributed to the leakage reactance at harmonic frequencies, which affects the reactance seen by harmonic currents compared to the fundamental current. The relationship between the level of fault and the reduction in no-load current THD is also established.

PREREQUISITES
  • Understanding of single-phase transformer operation
  • Knowledge of Total Harmonic Distortion (THD) in electrical systems
  • Familiarity with leakage reactance and its impact on current
  • Basic concepts of complex permeability in magnetic materials
NEXT STEPS
  • Research "Total Harmonic Distortion (THD) in transformers" for deeper insights
  • Explore "leakage reactance in electrical circuits" to understand its effects
  • Study "complex permeability of magnetic materials" for its role in transformer performance
  • Investigate "inter-turn short-circuit fault detection techniques" for practical applications
USEFUL FOR

Electrical engineers, transformer designers, and professionals involved in fault detection and analysis in power systems will benefit from this discussion.

Shantanav
Messages
9
Reaction score
0
Hi all,

I have simulated (both in software and experimentally) inter-turn winding short-circuit fault in a single-phase transformer (working as a stand alone unit). I have the following observation but don't know the reason behind it:-

The fundamental component in the no-load current is increasing under fault, but all other harmonics (3rd, 5th. 7th etc) remain almost unchanged. So, under fault the Total Harmonic Distortion (THD) of the no-load current is improving i.e. decreasing.

Higher is the level of fault (i.e. number of turns shorted), lower is the no-load current THD.

Any ideas, why this trend is happening ?

Cheers,
Shanto
 
Engineering news on Phys.org
My guess:
Leakage reactance at nth harmonic is nX its line frequency number of ohms. So harmonic currents see more ohms of series reactance than does fundamental current.

What are properties of the iron core at harmonic frequencies?
Try some searches on "complex permeability".
Above some frequency well into audio range the iron no longer has any effective permeability .

http://www.diva-portal.org/smash/get/diva2:125733/FULLTEXT01.pdf

So as frequency goes up, leakage reactance becomes increasingly larger proportion of total because the core acts less and less like textbook iron..

That can't be the whole answer, but hopefully is food for thought.
 
Last edited by a moderator:

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
Replies
2
Views
2K
  • · Replies 3 ·
Replies
3
Views
26K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 4 ·
Replies
4
Views
5K
Replies
1
Views
3K
Replies
4
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
4
Views
10K