Short circuit calculation small network: gen motor transformer cables

Click For Summary
SUMMARY

The forum discussion focuses on performing short circuit calculations for a small electrical network involving a generator, motor, transformer, and associated cables. The user has calculated peak currents for the generator (28.5 kA) and motor (8.2 kA), as well as the resistance (R) and reactance (X) for various cables. The calculations were verified against simulation results from SKM PowerTools for Windows, achieving a close match with a 1% error margin. The user seeks assistance in completing the calculations, particularly for the transformer and additional points in the network.

PREREQUISITES
  • Understanding of IEC 61363 standards for electrical installations
  • Knowledge of short circuit current calculations and electrical parameters
  • Familiarity with SKM PowerTools for Windows simulation software
  • Basic electrical engineering concepts including resistance (R) and reactance (X)
NEXT STEPS
  • Learn detailed methodologies for short circuit calculations using IEC 60909
  • Explore advanced features of SKM PowerTools for Windows for simulation accuracy
  • Study transformer impedance calculations and their impact on short circuit analysis
  • Research techniques for calculating short circuit currents in multi-conductor systems
USEFUL FOR

Electrical engineering students, professionals involved in power system analysis, and anyone engaged in short circuit current calculations for electrical networks.

Luc
Messages
3
Reaction score
0
Hello guys,
I have to make a short circuit calculation for school but I am a bit lost.. I have a copy off the IEC61363 and internet connection as my help lines.


Homework Statement


The network consists of a generator feeding to switchboard A with a cable in between, on the same switchboard is a motor connected with another cable and there is a transformer connected to the switchboard (see image in attached file). There are also other motors on the switchboard but they can’t feed into the short circuit. I have marked the points where I want to calculate the short circuit current in the image in the attached file.


Homework Equations


I have no idea how I am going to put all those calculations in here, I've read the guidelines but I have to put this in a word document or else nobody is going to make sense of it anyway. In the file are the equations I used to calculate what I've done so far.


The Attempt at a Solution


I have calculated the following things:
Generator has a peak current of 28.5kA
Motor has peak current of 8.2kA calculations in attached file.

The 25 meter cable has R=0.206 and X=0.075 per 1000 meters and have 8 conductors in parallel per phase. For 25m this is R=0.00515 and X=0.001875
The 10 meter cable has R=0.206 and X=0.075 per 1000 meters and have 5 conductors in parallel per phase. For 10m this is R=0.00206 and X=0.000750
The 22 meter cable has R=0.206 and X=0.075 per 1000 meters and have 1 conductors in parallel per phase. For 22m this is R=0.004532 and X=0.00165
I assume I have to divide the R and X of each cable by the number of conductors in parallel.

I have tried adding the resistance and reactance of the 25 meter cable to the generators Ra and Xd (I thought I might be able to do this because the cable is parallel with the generator) but the answer I got wasn’t even close to the answer I got with my simulation software (SKM PowerToolsforWindows).
The peak current off generator and cable is 27136A
When I turn on the motor the peak current is 35218A
The current at the transformers secondary’s with both generator and motor on is 5972A.
The answer I got for the generator and cable with hand calculation is 28.4k just a smudge less then without the cable..

What is given about the transformer: 3 phase, S=125kVA, Uprim=690V, Usec=400V, Isec=180,5A, Uk=4%, F=50Hz.

I have also calculated the R and X of the transformer (calculation in attached file). The Rt=0,03 and the Xt=0,149 but same deal as with the cables I do not know how to go on nor can I find it on the internet.

When I started with this problem I thought I’ll have it done in under 1 hour but I was very wrong, I’m not even been able to solve it on my own so far.

The calculations of the transformer, generator and motor are in the attached file.

EDIT: I had been looking for the format for 'how to make a post' in this section for about 10 minutes, when I decided not to go by the format I found it when I opened the window for making a new thread.
 

Attachments

  • Short circuit calculations small network.docx
    Short circuit calculations small network.docx
    20 KB · Views: 347
  • Small network.png
    Small network.png
    13.3 KB · Views: 576
Last edited:
Physics news on Phys.org
After some trial and error I decided I would try to calculate the drop in short circuit current using a version of (I^2)*R. I used S=(I^2)*Z*Root(3).
Those answers I got with that formula came really close to what my simulation says (error is about 1%).
So now I have calculated:
A=28542A
B=8124A
C=27141A
D=8051A
E=35192A
F=20198A

G I still do not know, so if anyone did not reply because they only knew G then this is your time to shine ;)
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 20 ·
Replies
20
Views
5K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K