Determine air conditioning cooling time

Click For Summary

Discussion Overview

The discussion focuses on calculating the time required for an air-conditioning unit to cool a room from 30 degrees Celsius to 22 degrees Celsius. Participants explore various parameters affecting this calculation, including room dimensions, heat load, and air exchange rates.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant requests a formula and the principle of calculation for cooling time, indicating a desire to simplify the problem by ignoring other parameters.
  • Another participant suggests that the rate at which the air conditioner removes energy and the volume of air in the room are critical for calculating cooling time, and offers to assist if specific numbers are provided.
  • Room specifications, including dimensions and heat load, are provided by a participant, along with airflow metrics and chilled water flow rate.
  • Concerns are raised about the specifications of the air conditioning unit, noting that the efficiency of the unit is an important factor in the cooling process.
  • Another participant emphasizes the significance of internal heat load and heat transfer from outside, suggesting these factors may greatly influence the cooling time.
  • A detailed calculation is presented, converting heat load into energy removal rate and estimating the time required to achieve the desired temperature drop, while noting assumptions made in the calculation.
  • A participant clarifies the meaning of heat load, indicating it includes heat added by electrical devices and occupants in the room.

Areas of Agreement / Disagreement

Participants express varying views on the factors influencing cooling time, with no consensus reached on a single method or formula for calculation. Multiple competing perspectives on the importance of different parameters remain evident.

Contextual Notes

The discussion includes a mixture of units and assumptions about optimal airflow and heat removal efficiency, which may affect the accuracy of the calculations presented.

cktan22
Messages
5
Reaction score
0
how can i calculate the require time for an air-conditioning unit to cool from 30 degree celsius to 22 degree celsius? others parameter can be ignore, i would like to know the formula used and the principal of calculation. thanks
 
Science news on Phys.org
cktan22 said:
how can i calculate the require time for an air-conditioning unit to cool from 30 degree celsius to 22 degree celsius? others parameter can be ignore, i would like to know the formula used and the principle of calculation. thanks
You have to find out the rate at which the air conditioner removes energy from the room and the volume of air in the room. You will also have to factor in the rate at which air in the room is exchanged. You can then work out the time. If you provide those numbers we can help you calculate the time.

AM
 
room size : 3 m x 7 m, height 3 m
heat load : 10000 btu/h
cfm : 644
velocity: 6 m/s
temperature : from 30 celsius to 22 celsius
chilled water flow rate : 30.8 liter/minute
altitude : sea level
 
But what about the spec of the A/C unit? That's a very important factor.
An Air Con is a heat pump which will shift heat at a certain rate, depending upon the Power of the motor. They vary greatly in (what we could loosely call) efficiency.
Look up "Heating Seasonal Performance Factor" and "Coefficient of Performance".
 
Also, internal heat load and heat transfer from outside may play a significant role.
 
cktan22 said:
room size : 3 m x 7 m, height 3 m
heat load : 10000 btu/h
cfm : 644
velocity: 6 m/s
temperature : from 30 celsius to 22 celsius
chilled water flow rate : 30.8 liter/minute
altitude : sea level
Ok. You have a mixture of units so I will use the MKS units. 10000 BTU/h = 2.9 kW = 2900 J/sec.

I am not sure what the heat load means but since I asked for the rate at which energy is removed from the room, I will assume that this is that rate.

Volume of air in room = 63 m3;
Pressure = 1 atm = 101325 Pa;
Initial T =303K
number of moles of air in room = n = PV/RT = 2534 mol.

The heat capacity of air at constant pressure is Cp = 7R/2 = 29 J/mol K

So to reduce the temperature of that room of air by 8 degrees you have to remove:

Q = 29nΔT = 29 x 2534 x 8 = 588,000 Joules

Since the air conditioner removes 2900 Joules/sec. you would need 588000/2900 = 203 seconds or about 3.5 minutes to cool that room.

I take it that you wanted a ballpark figure. The above assumes that the air flow through the cooling coils of the air conditioner is optimal, ignores the slight increase in mass of the room air as temperature decreases at constant pressure, and ignores the need to remove heat from that extra mass.

AM
 
  • Like
Likes   Reactions: Alessandra Buso
Heat load is the heat added to the room by electrical devices and people(etc) in it.

...I missed that it was provided in a follow-up.
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 12 ·
Replies
12
Views
1K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 29 ·
Replies
29
Views
2K
Replies
8
Views
3K
  • · Replies 5 ·
Replies
5
Views
942
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 30 ·
2
Replies
30
Views
4K
  • · Replies 23 ·
Replies
23
Views
2K