Connecting Two 30x10mm2 Earth Busbars: Min. Conductor Cross Section

AI Thread Summary
The discussion centers on connecting two 30x10mm2 Earth busbars in a switchboard and determining the minimum conductor cross-section required for this connection. It emphasizes adhering to regional codes while suggesting that the conductor should at least match the busbar's cross-sectional area. There is a caution against confusing the Earth busbars with Neutral connections, highlighting that Protective Earth and Neutral should only be connected at a single point in the switchboard. Additionally, the fault rating of the system is questioned, indicating a need for clarity on safety standards. Proper adherence to these guidelines is crucial for ensuring electrical safety and compliance.
Ivan001
Messages
19
Reaction score
0
I have two 30x10mm2 Earth busbars in switchboard, both are placed on insulators, but connected through various parts of switchboard (ground terminal, rails, door, mounting plate...) What is the minimal conductor cross section allowed for connecting this two busbars directly?
 
Engineering news on Phys.org
There may be a regional code for this - but I would use at least the same area as the bus bar.

Also - what is the fault rating of the system.
 
Ivan001 said:
I have two 30x10mm2 Earth busbars in switchboard, both are placed on insulators, but connected through various parts of switchboard (ground terminal, rails, door, mounting plate...)
Are you sure one of them is not a Neutral ?
Do not connect Protective Earth and Neutral except at the one point in the switchboard.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...