As for Q1 -- I am not sure what is meant by "IT", and I am assuming by "bipolar" you mean the circuit breaker has 2 contacts, therefore these are connected to two phases (energized legs) & NOT one Phase Leg and Neutral...? A diagram would help clarify your questions. If the load is connected to two energized phases - you need to disconnect both phases from the load - even though this uses two phases it is still referred to as a single phase load.
What I mean is one phase and neutral.
IT is a type of earthing system. In IT, you have an unearthed neutral, so in a occurrence of a first line to ground fault, it is hard to detect the fault location, since the current has no path to return by. But in the occurrence of a second line to ground fault, a closed path for current would be created by the other faulty equipment. What I don't understand is why we have to disconnect both phase and neutral in this situation.
2) Earthing is its own specialty but you need to know this in this fields, even if for your own personal safety, but the point of earthing being that all parts of the system that are earthed should be safe to touch ( zero potential) at all times including during faults and mis-operaitons, anywhere that current flows during a fault can result in lethal voltage, so each location should have it's own conductor to the earthing point, to reduce the possibility of voltage at that point. ( Earthing is not about load current)
In the case of a fault, if your protective device does not operate, you'll have lethal voltage in equipments even if they're connected to earth. Earthing also has to do with the availability that the process being fed requires. For example, in an IT system, the first line to ground fault won't cause any harm, but the second fault will (but you have more system availability here). In TN systems, the first fault will already be dangerous, but it will be much easier to be detected (but you have less availability). My question is more about the definition of TN and TT systems, which I don't fully understand.
3) Because the phase imbalance (current from the single phase load) causes current in the neutral resistor. This is not a case IMO of "not recommended" -- this should not be allowed.
Are you sure? The current will flow from phase to neutral, but I think that there will be no current in the neutral resistor (unless there is a fault, but that's the intention), since the resistor is connected between neutral and earth.
4) Potential (voltage) Transformer ? or Power Transformer? Ether way -- CBs are about defining zones of protection. The CB on the Line side transformer - is primarily there to "protect" the transformer, and the Load side to protect the downstream "load" devices ( cables, bus, additional transformers etc.) If the real load is too much for the cables to supply - the LOAD side breaker should trip. The LOAD side breaker will also protect the transformer from overload, but the "problem " is still the load. The Load side breaker in these cases should always trip before the Line side breaker(or fuses) - this is called coordination of protection.
Thanks, you answer clarified it for me.
Are you in field service? I can then understand the people often not knowing the why ( but someone should be able to answer these questions for you) - if you are working in an engineering office - then you are not talking to the right people ( keep asking - do not accept "that is how it is done"). Lastly - physically working on these devices ( touching them) you must know these things - you can not THINK something is safe you have to KNOW - and if you do not understand these concepts - then it is impossible for you to KNOW you are safe..
I was an FSE for ABB In the US for 8 years ( 3 years before that with a private testing co.) - where are you located?
I haven't been to field yet (except for some factory inspections). Maybe there is someone in the office that knows these things, but I can't think of who. The questions 1) and 3) I've had for some time, but no one could answer me. They always have the answer: "we always did it like this". Btw, the 3rd question is about a situation that is actually occurring in a current project, but I don't know how to explain to everyone why we should not do it, I just remember that I read it somewhere more than once.
I am from Brazil, currently in my second year working at ABB as an engineer. Before that I was an intern. Anyway, thanks for your answers! I won't stop until I am convinced of everything