Equivalent impedance per phase (3 Phase balanced systems)

  1. May 8, 2013 #1
    Hi, if a load is given in MVA and I work out the Real and reactive power, is the equivalent complex impedance per phase the values of real and reactive power divided by three in the following form:

    Z (per phase) = Real power/3 + j Reactive power/3

    Im not sure how to work out whether the complex number should be real term ± imaginary term? Thanks
     
  2. jcsd
  3. May 8, 2013 #2
    RLC parallel circuits?
     
  4. May 9, 2013 #3
    The RHS is the per-phase complex power for a balanced load. Since the LHS should be in units of ohms, you should reexamine what lead you to this equation.

    Consider an impedance Z with known complex power S delivered to it:
    [tex]
    \mathbf{Z} = \frac{\mathbf{V}}{\mathbf{I}} \\
    \mathbf{S} = \mathbf{V} \mathbf{I}^*
    [/tex]
    where V is the voltage across the impedance and I is the current through it.

    This is 2 equations in 3 unknowns. This should tell you that you need more information to uniquely determine Z.

    Since the angles of Z and S are equal, you could determine Z if you knew the magnitude of either V or I.
     