Green Liquid Leaked from CT Secondary Terminal Board of 132 kV GIS

AI Thread Summary
A thick, sticky green liquid was discovered leaking from two feeders of a 132 kV switchgear, raising concerns about its origin. Previous issues with cracks in the CT secondary terminal board led to replacements six to seven years ago, prompting speculation that similar damage may have occurred. Some participants suggested the liquid could be insulating oil mixed with preservatives or a reaction between vinyl insulation and copper, resulting in a dark green substance. The potential presence of polychlorinated biphenyls (PCBs) in the liquid raises toxicity concerns, emphasizing the need for testing before any contact. Caution is advised in handling the substance due to its hazardous nature.
Suri
Messages
1
Reaction score
0
Hye everyone!

An unknown thick-and-sticky green liquid was found leaked from 2 out of 9 feeders, of our 132 kV Switchgear. The liquid was leaked through the cable gland that connected to the Secondary Terminal Board insulating cap of the Current Transformer, at the GIS.

I had done:
1) gas leak test - no gas leakage detected
2) hotspot test using thermography camera - no hotspot.

According to our chargeman, around 6-7 years ago, there is a case when they found out that inside the CT secondary terminal board, there was cracks. And all CT secondary board for all feeders was then replaced.

I just wondered if the same thing happened. Or the green liquid was just a kind of grease or softener for the cable.

Hopefully someone can help me. Thank you!
 
Engineering news on Phys.org
It is probably insulating oil with some kind of preservative.
 
I have had cases where the vinyl or plasticizers reacted with the copper and created a dark green sticky substance. In one case it was clear insulation and I could see the fouling all along the cable.

BoB
 
  • Like
Likes Asymptotic
rbelli1 said:
I have had cases where the vinyl or plasticizers reacted with the copper and created a dark green sticky substance. In one case it was clear insulation and I could see the fouling all along the cable.
I have also experienced that corrosion in ordinary lamp cord with clear vinyl insulation. Annoying!
 
I would be careful. Polychlorinated biphenyls (PCBs) were widely used as insulating fluids in electrical equipment for many years. Wikipedia says, "One estimate (2006) suggested that 1 million tonnes of PCBs had been produced. 40% of this material was thought to remain in use. Another estimate put the total global production of PCBs on the order of 1.5 million tonnes. The United States was the single largest producer with over 600,000 tonnes produced between 1930 and 1977. The European region follows with nearly 450,000 tonnes through 1984."

These things are toxic. I would get it tested before you come in contact with it, if it's not too late.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top