Grounding Test: Ordinary Multimeter vs Special Tool?

Click For Summary

Discussion Overview

The discussion centers on the feasibility of using an ordinary multimeter for point-to-point resistance testing of grounding systems compared to using a specialized ground test tool. The scope includes technical considerations related to electrical testing standards and methodologies.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants question whether an ordinary multimeter can effectively perform point-to-point tests for grounding resistance, suggesting that a special ground test tool may be necessary.
  • One participant notes that the NETA value of 0.5 ohm is widely accepted as a standard for grounding resistance.
  • Another participant argues that using an approved tester ensures compliance with national requirements and reduces the risk of misinterpretation of rules and readings.
  • Concerns are raised about the limitations of ordinary multimeters, particularly regarding the added resistance from leads, which could significantly affect measurement accuracy when testing between major electrical frames.
  • A participant explains the operation of a 4-wire "Kelvin" resistance meter, highlighting its advantage in eliminating lead resistance by using separate leads for current supply and voltage measurement.

Areas of Agreement / Disagreement

Participants express differing views on the adequacy of ordinary multimeters for grounding tests, with some advocating for specialized tools due to accuracy concerns. The discussion remains unresolved regarding the best approach for such measurements.

Contextual Notes

Limitations include the potential impact of lead resistance on measurement accuracy and the need for specific testing equipment to meet regulatory standards. The discussion does not resolve the technical requirements for grounding tests.

Royherd27
Messages
11
Reaction score
0
Can the point to point test, (to determine the resistance between the main grounding system and all the major electrical frames, system neutral, etc) be made with an ordinary multimeter or does it need a special ground test tool?
The NETA value of 0.5 ohm is widely accepted?
 
Engineering news on Phys.org
The advantage of an approved tester is that it is consistent with your country's requirements, and doesn't depend on you interpreting the rules and the readings and correctly applying the correct stimulus.
 
Royherd27 said:
Can the point to point test, (to determine the resistance between the main grounding system and all the major electrical frames, system neutral, etc) be made with an ordinary multimeter or does it need a special ground test tool?
The NETA value of 0.5 ohm is widely accepted?

The basic problem with ordinary multimeter is that its leads will add resistance in series. You will need long leads if you are probing between major electrical frames, the lead resistance will probably be orders of magnitude more than the bonding resistance you are trying to measure.

You need a 4 wire "Kelvin" resistance meter (previous posters provided links). Here is how they work:

2 leads supply a constant controlled current source through the ground structure under test (lead resistance not an issue here since it is a current source). The other two leads measure voltage across the current source. The voltage measurement leads draw very low leakage current so lead resistance here is not an issue.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 83 ·
3
Replies
83
Views
8K
  • · Replies 53 ·
2
Replies
53
Views
7K
  • · Replies 13 ·
Replies
13
Views
7K
  • · Replies 38 ·
2
Replies
38
Views
8K
  • · Replies 7 ·
Replies
7
Views
12K
  • · Replies 105 ·
4
Replies
105
Views
13K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 12 ·
Replies
12
Views
17K
Replies
12
Views
3K