Greetings,

I’m looking at the output of an electronic 3-phase meter.

I have 2 “snapshots” from the meter.

In one snapshot I can make sense of most of the data presented.

The output gives me Va, Vb, Vc, Ia, Ib, Ic, and their angles, a single power factor, watts, VA, and VAR.

When I built my power triangle I almost agree with the outputted VA, watts, and VAR. I am within a little on some and right on it on other numbers.

For this snapshot – there was “load” - current in all 3 phases is around 1.1A.

The meter also provides “Harmonics VA and Harmonic pf” I did not use these 2 numbers in my power triangle.

My next snapshot was without load.

I am given the exact same data – current is around 0.1 in all 3 phases.

I cannot get any where close to the power triangle – meaning using the same procedure above – (Vrms)(Irms) – VA, VA(cos()) = watts and so on. I do not get the outputted watts, VA and VAR. The outputted powers are quite a bit higher.

One thing that stands out is that in this snapshot (no load) my harmonics VA and harmonics pf are quite a bit larger than the loaded snapshot.

With load: harmonics VA = 25.7 and harmonics pf = 0.069.

With no load: harmonics VA = 493.965 and harmonics pf = 0.30.

Here is all of the data for the no load:

Va = 113.336, Ia = 0.087: Ia lags Va by 15.86 degrees
Vb = 112.676, Ib = 0.136: Ib leads Vb by 21 degrees
Vc = 113.512, Ic = 0.158, Ic lags Vc by 10 degrees

Watts = 710.078
VArms = 1644.563
VAtd = 1568.625
VAR = 1398.719
Pf = 0.432

Harmonics VA = 493.965
Harmonics pf = 0.3

Can you show me how to get the (above) watts, VA rms, and VAR from the provided currents and voltages?

How do I use the provided harmonic data in power calculations?

Thanks
Sparky
 

Answers and Replies

  • #2
32
1
keep in mind what you have involved in the load, a sure mix of inductors and capacitors which can balance you pf. why your b phase is capacitive without load i am not sure, but it is to be expected inductive. remember your power is coming from a transformer, an inductive coil.

Here is all of the data for the no load:

Va = 113.336, Ia = 0.087: Ia lags Va by 15.86 degrees
Vb = 112.676, Ib = 0.136: Ib leads Vb by 21 degrees
Vc = 113.512, Ic = 0.158, Ic lags Vc by 10 degrees

Watts = 710.078
VArms = 1644.563
VAtd = 1568.625
VAR = 1398.719
Pf = 0.432

is this data the data your meter provided?
 
  • #3
223
4
Hey Sparkey

yes that is data straight from the meter. Again in the first snapshot - I could reproduce the Watts, VA, and VAR (which were provided from the meter) by using the provided currents and voltages and their angles.

In this snapshot the same calculation method does not work and I noticed that my harmonic VA and pf harmonics stand out when compared to the first snapshot. I did not use these 2 pieces in my first calculations and my gut says they are needed here. I just don't know how to use these two numbers nor what they are telling me.

Thanks
-Sparky
 

Related Threads on Harmonics in power calculations

  • Last Post
Replies
16
Views
2K
  • Last Post
Replies
3
Views
7K
Replies
12
Views
5K
Replies
3
Views
565
  • Last Post
Replies
6
Views
10K
  • Last Post
Replies
5
Views
6K
Replies
1
Views
569
  • Last Post
Replies
4
Views
20K
  • Last Post
Replies
1
Views
3K
  • Last Post
Replies
24
Views
2K
Top