The discussion centers around the heat loss in a hot water pipe system, specifically focusing on the thermal dynamics involved in the transfer of heat from a water heater through copper pipes to various taps in a home. Participants explore methods for calculating heat loss, the impact of insulation, and the feasibility of replumbing to reduce heat loss.

Discussion Character

  • Exploratory
  • Technical explanation
  • Conceptual clarification
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests starting with a heat loss calculation along the pipe run, noting the need for inside and outside surface temperatures.
  • Another proposes a simpler energy analysis based on the known input and output temperatures of the water, suggesting measuring the water temperature after sitting for a time.
  • A participant mentions the possibility of neglecting certain heat transfer coefficients due to the high conduction through the pipe wall compared to convection to the air.
  • There is a suggestion to use simplified convective heat transfer coefficients for a rough estimate of heat loss.
  • One participant raises concerns about the labor intensity and cost-effectiveness of rerouting plumbing lines in existing homes.
  • Another advises consulting a specific textbook for detailed treatment of heat transfer through pipelines.
  • Participants discuss the importance of considering both transient and steady-state heat loss in their calculations.
  • One participant mentions the existing insulation on some pipes but notes that there are sections that remain uninsulated, which may affect heat loss calculations.
  • There is a reference to standard temperatures for water heaters and the implications for energy efficiency and safety.

Areas of Agreement / Disagreement

Participants express a range of views on the best approach to analyze heat loss, with some advocating for simpler methods while others suggest more complex calculations. There is no consensus on a single method or solution, and various competing ideas remain present throughout the discussion.

Contextual Notes

Participants highlight the need for specific temperature values and the potential variability in heat loss calculations based on insulation and ambient conditions. The discussion also reflects uncertainty regarding the impact of different materials and configurations on heat transfer.

Who May Find This Useful

This discussion may be useful for homeowners considering plumbing modifications, engineers interested in heat transfer analysis, and students studying thermodynamics and fluid mechanics.

  • #31
Hi

I hope you do not mind me joining this discussion, but I found this thread on a Google search. I have a related problem.

I am thinking of installing a set of Glass tube heat pipe solar pannels to help run my underfloor heating system. My only problem is that they can only be situated about 50 meters from the house, so the flow and return pipes will have to be burried underground. What I would like to know is how much heat loss I can expect in the pipes?

The pipes will be 30 - 40 mm diam Polyethylene water pipe, burried 0.75 m below ground. I am not sure how I could insulate these - I would need some type of waterproof foam plastic lagging as glass fibre would pass ground water. When the system is working (sun shining) the flow temperature will be 40-50 C with a return of 10-20 C lower. When it matters, in the winter, I assume a ground temperature of 2-10 C . This would effectively be a steady state system as the main issue is how much heat can I get during a winterday when the sun is shinning.

Any help or advice would be most welcome.

PJG
 
Engineering news on Phys.org
  • #32
pjgregory said:
Hi

I hope you do not mind me joining this discussion, but I found this thread on a Google search. I have a related problem.

I am thinking of installing a set of Glass tube heat pipe solar pannels to help run my underfloor heating system. My only problem is that they can only be situated about 50 meters from the house, so the flow and return pipes will have to be burried underground. What I would like to know is how much heat loss I can expect in the pipes?

The pipes will be 30 - 40 mm diam Polyethylene water pipe, burried 0.75 m below ground. I am not sure how I could insulate these - I would need some type of waterproof foam plastic lagging as glass fibre would pass ground water. When the system is working (sun shining) the flow temperature will be 40-50 C with a return of 10-20 C lower. When it matters, in the winter, I assume a ground temperature of 2-10 C . This would effectively be a steady state system as the main issue is how much heat can I get during a winterday when the sun is shinning.

Any help or advice would be most welcome.

PJG

Fill the trench around the pipes with perlite insulating concrete.
provides a k factor range of 0.58 to 0.66 Btu-inch/h-ft2-F (0.085 to 0.095 W/m-k).
 
  • #33
Hi Artman

Thank you for your response. Let me see if I understand this.

The heat loss in Watts is

Watts = k * Area * Temperature Differnce / Thickness Material (L)

So assume k for Perlite concrete is 0.09. Then simplifying for one pipe laid in a cylindrical tube of concrete radius 0.25m (L), the area per unit length would be 1.57 so for 50m of pipe and a 40 degree K temperature difference, the loss would be:

Loss = 0.09*1.57*50 *40/0.25 = 1130 watts.

So I will need to add about 1Kwatt to estimated load for the house to compensate for the heat loss in the underground pipes.

I have found a supplier of Perlite products in Italy. Now all I have to do is work out how to explain this to my builder in Italian.

Thanks again

PJG
 
  • #34
Here is another possibility to consider. Preinsulated pipe. I don't know which would be cheaper or easier.

http://www.maxx-r.com/?gclid=CP-Z4IiN3YQCFRs1Swod6jZ6Ww"
 
Last edited by a moderator:
  • #35
copper water interface heat transfer

Hello,

Great discussion. Any references for a similar problem?

Copper pipe is bathed in a hot material.
Copper pipe has cooler water flowing through the pipe.

How to calculate heat flow through the copper pipe to moving water?

Non laminar flow is thought to improve heat transfer to water.
 
  • #36
heatmover said:
Hello,

Great discussion. Any references for a similar problem?

Copper pipe is bathed in a hot material.
Copper pipe has cooler water flowing through the pipe.

How to calculate heat flow through the copper pipe to moving water?

Non laminar flow is thought to improve heat transfer to water.

What you are describing here is a unit called a "heat exchanger". The calculations for a heat exchanger can be rather complex. Dealing with the mediums, the temperature difference entering to leaving of both the transfer medium and the product being heated, the materials used in the exchanger, the insulating/transfer values of the tube side and shell sides. For references to this problem try searching for information on "Copper tube heat exchangers."
 

Similar threads

Replies
12
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 15 ·
Replies
15
Views
4K
Replies
25
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
12K
  • · Replies 7 ·
Replies
7
Views
7K
Replies
1
Views
4K
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
14K