Heat pump COP theoretical maximum

Click For Summary
SUMMARY

The forum discussion centers on the theoretical maximum of the Coefficient of Performance (COP) for heat pumps, specifically addressing the misconception that COP values can exceed 2 for air-to-air heat pumps. Participants clarify that COP values greater than 2 violate the second law of thermodynamics, particularly when heat is pumped from a colder reservoir to a hotter one. The correct formula for COP is established as COP = Thot / (Thot - Tcold), emphasizing that the temperature difference between reservoirs is crucial in determining COP values. Misinterpretations of COP calculations can lead to misleading expectations regarding heat pump efficiency.

PREREQUISITES
  • Understanding of thermodynamics, specifically the first and second laws.
  • Familiarity with heat pump operation principles and terminology.
  • Knowledge of the Coefficient of Performance (COP) and its significance in energy efficiency.
  • Basic mathematical skills for manipulating thermodynamic equations.
NEXT STEPS
  • Research the Carnot efficiency and its implications for heat pump performance.
  • Study the impact of temperature differentials on COP in various heat pump configurations.
  • Learn about real-world factors affecting heat pump efficiency, such as installation and environmental conditions.
  • Explore advanced thermodynamic calculations related to heat transfer and energy conservation.
USEFUL FOR

Engineers, HVAC professionals, and anyone involved in the design or optimization of heating systems will benefit from this discussion, particularly those seeking to understand the limitations and efficiencies of heat pumps.

Thermolelctric
Messages
28
Reaction score
0
Hello everybody.

I have trouble of proving the theoretical maximum of heat pump coefficient of Performance.
The thing I'm trying to calculate is for heat pump pumping heat from colder reservoir to the hotter reservoir:
COP=Qh/W
Qh - heat supplied to the hot reservoir(output)
W - mechanical work consumed by the pump(input)

The formulas in the wikipedia seems to be wrong and I want to derive the correct formulas from the thermodynamic laws. With current Wikipedia formula it is normal to get COP >2. Search wikipedia:coefficient of Performance.

As I calculate the heat balance of the basic air to air heat pump, any COP values above 2 will violate the second law of the thermodynamics, and therefore make perpetual motion machine possible.

So is what is the correct formula and what is the way to prove it?

I argued a lot with my friend about that, when he wanted to buy the heat pump to heat his office. Eventually he still bought the pump because I could not provide the calculation and he decided to believe what the sales man told him (COP=3 or something). But now he do not seem very happy with the electricity bill.

Thanks in advance.
 
Science news on Phys.org
The formulas in the wikipedia seems to be wrong
I don't think so.

A COP>2 is possible, if the temperature difference is not too large. Looks like you have some error in your calculations.
 
According to my understanding COP >2 is not possible for air to air heat pump. Based on assumption that heat from the building is lost to the same air (cold reservoir) from where it is pumped to inside the building (hot reservoir).

The COP>2 is possible for land to air pump, when the cold reservoir is hotter than the air aruond the building to where the heat is lost. But not for the air to air.

The formula COP=Thot/(Thot-Tcold) maybe it is for calculating the possible improvment over air to air pump. Thot being the Earth and Tcold being the air around the building. The common miscontseption being that using Tcold = outside temp, and Thot = temp inside building. While should be Tcold =outside temp, and Thot = Earth (or other heat) source temperature.

Huge amount of people are scammed with this false calculation!
 
OK, let me put it that way:

Can anyone prove that COP>2 is possible, based on thermodynamic laws and other postulates?
Conditions: pumping heat from cold reservoir(Tcold) to the hot reservoir(Thot). Tcold<Thot.
 
Thermolelctric said:
OK, let me put it that way:

Can anyone prove that COP>2 is possible, based on thermodynamic laws and other postulates?
Conditions: pumping heat from cold reservoir(Tcold) to the hot reservoir(Thot). Tcold<Thot.
Q_h: heat pumped into the building
Q_c: heat taken from outside the building
W: electrical energy used by the heat pump
T_h: temperature inside the building
T_c: temperature outside the building

1st law: Q_h = W + Q_c

Therefore \mathrm{COP} = \frac{Q_h}{W} = {Q_h}{Q_h - Q_c} = \frac{1}{1 - Q_c/Q_h} &gt; 1

2nd law: \frac{Q_h}{T_h} \ge \frac{Q_c}{T_c} therefore 1 - \frac{T_c}{T_h} \le 1 - \frac{Q_c}{Q_h} for which we get \mathrm{COP} \le \frac{1}{1 - T_c/T_h} = \frac{T_h}{T_h - T_c}
There is no fundamental reason why the COP cannot be greater than 2.

Thermolelctric said:
According to my understanding COP >2 is not possible for air to air heat pump. Based on assumption that heat from the building is lost to the same air (cold reservoir) from where it is pumped to inside the building (hot reservoir).
I don't see how any losses from the building come into play in the calculation of the COP of heat pump itself.
 
Thanks DrClaude.
DrClaude said:
Q_h: heat pumped into the building

Therefore \mathrm{COP} = \frac{Q_h}{W} = {Q_h}{Q_h - Q_c} = \frac{1}{1 - Q_c/Q_h} &gt; 1
Can you explain more how you get this?

DrClaude said:
Q_h
I don't see how any losses from the building come into play in the calculation of the COP of heat pump itself.
For building heating, this is the main goal to determine most economic way to get the energy needed to maintain the temperature inside the building above the ambient. So naturally one wants to compare how much heating energy he gets using different apparatus. Correct understanding of the COP of the heat pump is needed for those calculations.

There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.
 
Thermolelctric said:
There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.
Please show your calculations for this claim.
 
Thermolelctric said:
Thanks DrClaude.
Can you explain more how you get this?

Sorry, a part of the equation didn't come out right. \mathrm{COP} = \frac{Q_h}{W} = \frac{Q_h}{Q_h-Q_c} = \frac{1}{1-Q_c/Q_h} &gt;1 I hope it is now clear.

Thermolelctric said:
For building heating, this is the main goal to determine most economic way to get the energy needed to maintain the temperature inside the building above the ambient. So naturally one wants to compare how much heating energy he gets using different apparatus.
Yes, but this can be made independent of the COP of the pump, by assuming that you have a desired indoor temperature, for a given outdoor temperature. Of course, if your goal is to maintain an indoor temperature relative to the outside, it becomes more complicated. Note also that actual COPs are usually given for a standard pair of indoor and outdoor temperatures, and are mostly useful in comparing one pump with another. If you want to calculate the actual energy needed over a year, including variations of the outside temperature, you would need measured COPs as a function of inside/outside temperatures.

Thermolelctric said:
There must be error in those calculations, because when simple heat pump has a COP of over 2, it is possible to reheat the input with the energy from the output and with that increase the COP infinetly resulting in infinite COP -- the mashine that pumps heat from cold reservoir to hot reservoir without needing any additional energy to run.
No error, it is just how the COP is defined. Infinite COP will only occur for T_h=T_c, in which case the pump is not doing anything, so indeed it doesn't need any energy to run! Event for finite but huge COPs, they correspond to extremely small differences in temperatures that are not realistic in real world applications. And it is just an inequality: for real heat pumps \mathrm{COP} = \eta \frac{T_h}{T_h-T_c} with \eta &lt; 1 and itself a function of T_h and T_c.
 
DrClaude said:
No error, it is just how the COP is defined. Infinite COP will only occur for T_h=T_c, in which case the pump is not doing anything, so indeed it doesn't need any energy to run! Event for finite but huge COPs, they correspond to extremely small differences in temperatures that are not realistic in real world applications. And it is just an inequality: for real heat pumps \mathrm{COP} = \eta \frac{T_h}{T_h-T_c} with \eta &lt; 1 and itself a function of T_h and T_c.

Thanks.
But what happens to COP when Th closes to infinity?
 
  • #10
Thermolelctric said:
But what happens to COP when Th closes to infinity?
The ideal COP approaches 1 as Th approaches infinity.
 
  • #11
DaleSpam said:
Please show your calculations for this claim.

This is what I am working on.

We have cold reservoir, and hot reservoir. We are pumping from cold to hot.
Lets assume we have a COP=5
Mehanical work into the pump=1kW
Heat output to the hot reservoir=5kW

So now we let 2kw go back to heat the cold reservoir.
This leaves us still 3kW output to hot reservoir, this heats the hot reservoir, but we do not let the hot reservoir temperature increase, the exess heat is conducted away. So Th=const.
But added 2kW to cold reservoir will increase the cold reservoir temperature. And this increases the COP by formula COP=Th/(Th−Tc). So now we get even more output heat because of increased COP. And the cycle repeats. The COP is increased to infinity.
We have perpetum mobile!
 
  • #12
Thermolelctric said:
So now we let 2kw go back to heat the cold reservoir.
This leaves us still 3kW output to hot reservoir, this heats the hot reservoir, but we do not let the hot reservoir temperature increase, the exess heat is conducted away. So Th=const.
But added 2kW to cold reservoir will increase the cold reservoir temperature. And this increases the COP by formula COP=Th/(Th−Tc).
Even with the increased COP it still takes work to move the heat back up. You seem to think that the heat that leaks into the cold reservoir is somehow free to move back to the hot reservoir.
 
  • #13
Thermolelctric said:
Thanks.
But what happens to COP when Th closes to infinity?
\mathrm{COP} \sim 1

Consider the following hypothetical situation. An ideal (Carnot engine) heat pump installed between a hot sink at T_h and a cold source at T_c, and functions with a constant consumption of electrical energy (W = \mathrm{const.}). Both sources are connected such that heat can flow from hot to cold to maintain the hot source at T_h (imagine that we have a demon that can do that so that we don't need to worry about entropy here). The temperature of the cold source will vary according to
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{Q_h}{C} t <br />
where T_{c0} is the initial temperature of the cold source and C its heat capacity. Since Q_h = W+Q_c, we have
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{W + Q_c}{C} t = T_{c0} + \frac{W}{C} t<br />
so the heat pump is basically heating up the cold source as would a perfect electrical heater. No "over unity" or other violation of the laws of TD.

Note that the initial value of the COP is of no relevance. This will work even if it is initially < 2. The value of the COP grows towards infinity during the process, but so what?

Hope this helps.
 
  • #14
DaleSpam said:
Even with the increased COP it still takes work to move the heat back up. You seem to think that the heat that leaks into the cold reservoir is somehow free to move back to the hot reservoir.

This is what I'm trying to prove. That this COP formula is incorrect.
 
  • #15
Thermolelctric said:
This is what I'm trying to prove. That this COP formula is incorrect.

But the COP formula is just
<br /> \mathrm{COP} = \frac{\textrm{benefit}}{\textrm{cost}} = \frac{Q_h}{W}<br />
 
Last edited:
  • #16
DrClaude said:
By the COP formula is just
<br /> \mathrm{COP} = \frac{\textrm{benefit}}{\textrm{cost}} = \frac{Q_h}{W}<br />

Not that one!
 
  • #17
Thermolelctric said:
Not that!
I derived the COP in terms of temperatures above. If you can't find any fault with the derivation, then both are equivalent.

Thermolelctric said:
So now we get even more output heat because of increased COP.
Or you just need less W for the same Q_h, which makes sense: the heat pump requires less work if the sink and the source are close to the same temperature.

Thermolelctric said:
The COP is increased to infinity.
We have perpetum mobile!
No, you reach T_c = T_h and you don't have a heat pump anymore! Or, see my previous post, you just continue heating the cold source as would a electrical heater.
 
  • #18
DrClaude said:
\mathrm{COP} \sim 1

Consider the following hypothetical situation. An ideal (Carnot engine) heat pump installed between a hot sink at T_h and a cold source at T_c, and functions with a constant consumption of electrical energy (W = \mathrm{const.}). Both sources are connected such that heat can flow from hot to cold to maintain the hot source at T_h (imagine that we have a demon that can do that so that we don't need to worry about entropy here). The temperature of the cold source will vary according to
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{Q_h}{C} t <br />
where T_{c0} is the initial temperature of the cold source and C its heat capacity. Since Q_h = W+Q_c, we have
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{W + Q_c}{C} t = T_{c0} + \frac{W}{C} t<br />
so the heat pump is basically heating up the cold source as would a perfect electrical heater. No "over unity" or other violation of the laws of TD.

Note that the initial value of the COP is of no relevance. This will work even if it is initially < 2. The value of the COP grows towards infinity during the process, but so what?

Hope this helps.

Thanks, we are getting closer to the solution -- proving the maximum efficiency of the air to air, building heating, heat pump.
 
  • #19
Thermolelctric said:
This is what I'm trying to prove. That this COP formula is incorrect.
It is correct, your perpetual motion argument is wrong. You should post your argument in full.
 
  • #20
DaleSpam said:
It is correct, your perpetual motion argument is wrong.

What do you mean wrong. Is the formula COP=Th/(Th−Tc) wrong, or is there something else wrong?
 
  • #21
Thermolelctric said:
What do you mean wrong. Is the formula COP=Th/(Th−Tc) wrong, or is there something else wrong?
The formula COP≤Th/(Th−Tc) is correct. Your argument that COP>2 → perpetual motion is wrong.
 
  • #22
DaleSpam said:
The formula COP=Th/(Th−Tc) is correct. Your argument that COP>2 → perpetual motion is wrong.

Can you point out what exactly is wrong?
 
  • #23
Thermolelctric said:
Can you point out what exactly is wrong?
No, not until you post the whole argument in detail. Please show in detail why you think COP>2 implies perpetual motion.
 
  • #24
DaleSpam said:
No, not until you post the whole argument in detail. Please show in detail why you think COP>2 implies perpetual motion.

Lets analyse the example I posted about COP=5 first.
 
  • #25
DrClaude said:
\mathrm{COP} \sim 1

Consider the following hypothetical situation. An ideal (Carnot engine) heat pump installed between a hot sink at T_h and a cold source at T_c, and functions with a constant consumption of electrical energy (W = \mathrm{const.}). Both sources are connected such that heat can flow from hot to cold to maintain the hot source at T_h (imagine that we have a demon that can do that so that we don't need to worry about entropy here). The temperature of the cold source will vary according to
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{Q_h}{C} t <br />
where T_{c0} is the initial temperature of the cold source and C its heat capacity. Since Q_h = W+Q_c, we have
<br /> T_c = T_{c0} - \frac{Q_c}{C} t + \frac{W + Q_c}{C} t = T_{c0} + \frac{W}{C} t<br />
so the heat pump is basically heating up the cold source as would a perfect electrical heater. No "over unity" or other violation of the laws of TD.


Hope this helps.

[STRIKE]How would be the good way to describe the point when the pump begins to heat the cold source instead of hot reservoire as intended? This is the point from where where Qh/W≠Th/(Th−Tc). Simply saying the heat is not pumped any more to the hot reservoire but instead goes to the cold reservoire[/STRIKE] . Sorry, stupid question. Let's just stick to analysing the COP=5 example, for now.
 
Last edited:
  • #26
Thermolelctric said:
How would be the good way to describe the point when the pump begins to heat the cold source instead of hot reservoire as intended? This is the point from where where Qh/W≠Th/(Th−Tc). Simply saying the heat is not pumped any more to the hot reservoire but instead goes to the cold reservoire .

Well, that is what the "demon" has been doing all along. By moving the heat from Th to Tc, you are basically just heating Tc.

If you want to imagine a more realistic situation, take a heat pump connected to two finite reservoirs, which can also exchange heat directly between each other. This direct exchange will depend on a thermal conductivity between the two and the difference in their temperature. As the heat pump works, heat from the cold reservoir will flow to the hot one, but a part will come back to the cold one. Both will slowly increase in temperature, up to a point where Th = Tc = Tf. At this point, you can calculate that the total energy consumed by the pump will be equal to the amount of energy needed to bring Th to Tf and Tc to Tf (conservation of energy). In a real situation, the heat pump itself stops working here because Tc = Th, but you could imagine that compressors are still working, etc., such that both Th and Tc will increase beyond Tf as the electrical energy continues to be converted to heat.
[Edit: I am assuming here that at all times the heat going back to the colr reservoir is > Qc]
 
Last edited:
  • #27
@Thermolelctric: All equations for heat pumps assume two reservoirs - heat is pumped from the cold reservoir to the hot one, and the required work goes to the hot one as well (this is just a convention). Neglecting engineering issues like thermal conductivity and heat capacity of the materials, there is no difference between outside air and outside ground.

Thermolelctric said:
This is what I am working on.

We have cold reservoir, and hot reservoir. We are pumping from cold to hot.
Lets assume we have a COP=5
Mehanical work into the pump=1kW
Heat output to the hot reservoir=5kW

So now we let 2kw go back to heat the cold reservoir.
This leaves us still 3kW output to hot reservoir, this heats the hot reservoir, but we do not let the hot reservoir temperature increase, the exess heat is conducted away. So Th=const.
But added 2kW to cold reservoir will increase the cold reservoir temperature. And this increases the COP by formula COP=Th/(Th−Tc). So now we get even more output heat because of increased COP. And the cycle repeats. The COP is increased to infinity.
We have perpetum mobile!
You pump 4kW of power out of the cold reservoir, and let 2kW flow back. You will cool the cold reservoir, so COP will go down.
If you would heat the cold reservoir in some way, COP would go up. So what?
 
  • #28
DrClaude said:
Well, that is what the "demon" has been doing all along. By moving the heat from Th to Tc, you are basically just heating Tc.

If you want to imagine a more realistic situation, take a heat pump connected to two finite reservoirs, which can also exchange heat directly between each other. This direct exchange will depend on a thermal conductivity between the two and the difference in their temperature. As the heat pump works, heat from the cold reservoir will flow to the hot one, but a part will come back to the cold one. Both will slowly increase in temperature, up to a point where Th = Tc = Tf. At this point, you can calculate that the total energy consumed by the pump will be equal to the amount of energy needed to bring Th to Tf and Tc to Tf (conservation of energy). In a real situation, the heat pump itself stops working here because Tc = Th, but you could imagine that compressors are still working, etc., such that both Th and Tc will increase beyond Tf as the electrical energy continues to be converted to heat.

Both will slowly come to the temperature Tf, near the Tf the COP will be very high. But this do not reflect the real coefficient of Performance, because the heat goes to heating the low temp resevoire, we need to subtract the heat that goes to heating the cold side from Qh. Could this be the difficulty of calculating the COP and current cause of difficulty of thinking?
 
  • #29
Thermolelctric said:
Both will slowly come to the temperature Tf, near the Tf the COP will be very high. But this do not reflect the real coefficient of Performance, because the heat goes to heating the low temp resevoire, we need to subtract the heat that goes to heating the cold side from Qh. Could this be the difficulty of calculating the COP and current cause of difficulty of thinking?

I don't get why the COP being high bugs you so much. What is the problem with a device that, by using 1 W of electricity, can transfer 1000 W from a cold reservoir to a hot reservoir? All the 2nd law tells you is that, to do that, you will need both reservoirs to be very close in temperature.
 
  • #30
mfb said:
You pump 4kW of power out of the cold reservoir, and let 2kW flow back. You will cool the cold reservoir, so COP will go down.
If you would heat the cold reservoir in some way, COP would go up. So what?

This is good observation. As long as the cool reservoir is below the ambient(outside temperature) it can absorb the heat from the ambient. So Tc < ambient temp. This brings in new reservoire.
It seems good idea to describe the pump as a system of 4 reservoirs: Input reservoir, pump cold reservoir, pump hot reservoir, and output reservoir. And try to calculate heat pumped from input reservoire to the output reservoire, and the work done to pump.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 6 ·
Replies
6
Views
1K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 15 ·
Replies
15
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 6 ·
Replies
6
Views
13K
  • · Replies 1 ·
Replies
1
Views
2K