High frequency from AC tig welder affects digital ammeter?

AI Thread Summary
High-frequency AC TIG welders can cause inaccuracies in digital ammeters, as indicated by a serviceman's findings that showed a discrepancy between digital and analog readings. The digital ammeter recorded over 150 amps, while the analog meter indicated only 105 amps under similar conditions. The high-frequency signal may not be a pure sine wave, potentially confusing clamp meters and leading to erroneous readings. Despite the engineer's insistence on the digital reading's accuracy, the discussion suggests that the analog meter may provide a more reliable measurement. Ultimately, the issue remains unresolved, highlighting the complexities of measuring current in high-frequency welding applications.
paceplane
Messages
2
Reaction score
0
I need a solution to the question, Which clamp-around-the-cable ammeter (digital or analog) can be trusted in measurement of current draw by a high-frequency AC tig welder? High-frequency AC is a requirement of welding aluminum, and an electrician measured 150+ amps at full power welding aluminum. A serviceman brought into find the problem told us, after checking the machine, that high frequency creates error in digital ammeters and his analog meter indicated 105 amps in a duplicate situation. We might have left it at that but are being told (by an engineer) that the digital reading was correct and we have to take the welder offline. Help!
 
Engineering news on Phys.org
This has nothing to do with analog and digital. Both can be constructed to show the correct current. Did you check the specifications of your meter.

If the serviceman is from the welder's company I would tend to trust him.
 
The power supplied to the welder can be measured for a limiting result, which I hope will satisfy the engineer.
 
The Wiki Current_clamp page has some interesting info.

If you are running AC for Al, with a high-freq starter signal, I'd bet the high-freq is not a sine wave and might confuse the clamp meter a bit. It could also induce more signal due to being coupled better than good-ole-60hz. But it should only run at startup and not affect a continuous reading. It's possible that your welding AC is not a sine wave as well, so you would have to adjust the reading to the waveform. In fact a square wave might give you 1.4 the reading you'd expect from a sine.

If your other reading was made with an in-line meter calibrated for real RMS, I would trust it a bit more.

However I don't follow why the equipment should be taken out of service. Is it welding correctly as set, or can't you "dial it down"? Is it fully automated and not current limiting as it should?
 
There's so much noise around one of these machines, you may have to fall back on a very fundamental measurement.
First, I'd attempt to get through the applications help people at the equipment manufacturer. Behind the thin line of question answer's is a group that have had to address this issue.

If that doesn't work, I'd try wiring in a current shunt with a non-electronic meter.
 
Thank you for the answers. High frequency does remain past the start because of stabilization ([URL="[URL]http://www.lincolnelectric.com/knowledge/articles/content/alum2.asp"] and I believe due to the difference in exhibited measurements it is a digital meter issue. Sure we can dial it down, the test was done at maximum power in an attempt to register a spike or overload on a recording ammeter at the building entrance. While we may not have a definitive answer to the question, the ammeter did not see it out there. Indications seem to be that the digital meter was incorrect; but the engineer is not accepting it. Sense and politics are often at odds. Thank you all for your input and help.
 
Last edited by a moderator:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...

Similar threads

Back
Top