Engineering How am I susposed to find the active power here?

  • Thread starter Thread starter sylent33
  • Start date Start date
  • Tags Tags
    Power
AI Thread Summary
The discussion focuses on calculating reactive power compensation for a halogen transformer with specific parameters. The user successfully calculated the active power and reactive power without compensation, determining the necessary capacitor value to achieve a desired power factor. However, they encountered difficulties when calculating the active power for a series connection of the capacitor, leading to confusion about the correct formulas and units, particularly regarding reactive power (var). Clarifications were provided on the definitions and significance of var and its usage in electrical engineering. The conversation highlights the importance of understanding both active and reactive power in AC circuits.
sylent33
Messages
39
Reaction score
5
Homework Statement
Multiple questions
Relevant Equations
AC Power
Hi everybody;

With a halogen transformer with the data U = 230 V, f = 50 Hz, I = 1.5 A and cos ϕ = 0.35
a reactive power compensation can be carried out with a parallel capacitor Cp. ¨
(a) Calculate the value of Cp to achieve a power factor cos ϕk = 0.9.

I did that like this;

First I calculated the active power without compensation ; $$ P = U \cdot I \cdot cos \phi $$ and the reactive power without compensation $$ P = U \cdot I \cdot sin \phi $$ and I get ;
P = 120,75 W and Q = 323,15 var

Now the active power remains the same with or without compensation,so I used that to calculated the new current that will flow when we add the capacitor to the circuit;
$$ I_{new} = \frac{P}{U \cdot cos \phi_k } $$ and it should be; I = 0,583A than I calculated Q with compensation; Qcomp = 58,44 var

And we can use this equation ; Qcomp = Qc+ Q to get the Qc value,that should be Qc = -264,71 var

$$Qc = \frac{U^2}{Xc} $$ we can find Xc out of that to be equall Xc = -200 Ohm and now;

$$ Xc = \frac{1}{\omega C} $$ we can find C to be ## C = 15,3µF ##

b)Represent all relevant powers with and without compensation graphically (correct angles) in the complex plane and state the scale used for thisDidnt really have any problems with this one;

c)
The capacitor Cp calculated in point (a) is wrongly connected in series with the halo gentrafo. Calculate the active power P of this arrangement.
Hint: If you cannot solve point (a), use Cp = 10 µF.

Now here is where I am having problems;

I tried calculating the Impedanz as ## Z = \frac{U}{I} ## where the I is the 0,583A I calculated in A. I am assuming that the voltage remains the same because its a series connection. Z comes around to be 394,5 Ohm. Now I tried calculating R and maybe trying to find P that way but that didnt work.I calculated R like this;

R = |Z| cos phi = 355,05 Ohm

And than ## P = \frac{R}{I^2} ## but that gives me the wrong result;

P should be (when we use 15mF) equall to 470,3W.

Any help would be appriciated (part a) I think is correct since that is the solution in the book)

Thanks
 
Physics news on Phys.org
halo gentrafo? What is var? ##P=\frac R {I^2}## ?
 
If I am not mistaken var should be the unit for the reactive power, (volt ampere reactive).
 
  • Like
Likes hutchphd
As arhzz stated var is just the unit for the reactive power,thought that wasnt anytinh too out of the ordinary.halo gentrafo is the halogen transformator from a),I guess in the translation google ate some words and it came out like that.

And the quation was a latex error I wanted to type in ## P = I^2 * R ## but it just came to my realization that this only works for DC.
 
arhzz said:
If I am not mistaken var should be the unit for the reactive power, (volt ampere reactive).
Thanks. Never seen that unit (and I'm old). I believe I can live without it !
 
hutchphd said:
Never seen that unit (and I'm old). I believe I can live without it !
The real watt is the VA where Volts and Amps are in phase.
The VAR is the voltage multiplied by the Reactive current (in quadrature), which can have no real power, only circulating energy.
There is still W = I²·r heat generated in the resistance, r, of the circuit by the vector sum of the real and reactive currents.
VA and VAR should be capitalised.
 
  • Like
Likes berkeman
I looked it up. It is apparently common practice, and the capitalization is optional!

from Wikipedia:

Volt-ampere reactive [edit]​

In electric power transmission and distribution, volt-ampere reactive (var) is a unit of measurement of reactive power. Reactive power exists in an AC circuit when the current and voltage are not in phase. The term var was proposed by the Romanian electrical engineer Constantin Budeanu and introduced in 1930 by the IEC in Stockholm, which has adopted it as the unit for reactive power.

Special instruments called varmeters are available to measure the reactive power in a circuit.[6]

The unit "var" is allowed by the International System of Units (SI) even though the unit var is representative of a form of power.[7] SI allows one to specify units to indicate common sense physical considerations. Per EU directive 80/181/EEC (the "metric directive"), the correct symbol is lower-case "var",[8] although the spellings "Var" and "VAr" are commonly seen, and "VAR" is widely used throughout the power industry.

Live and learn.
 
hutchphd said:
... and "VAR" is widely used throughout the power industry.
The power industry tends to use MVAR on transmission line networks.
 
  • Like
Likes hutchphd
  • #10
sylent33 said:
With a halogen transformer ...
That is an electrical transformer that generates a low voltage for use in halogen filled incandescent globes.
The expired patent covers the maintenance of the partial pressure of a halogen gas in an excimer laser.
 