How Can Active Spatial Noise Control Reduce HVAC Noise in Meeting Rooms?

  • Thread starter Thread starter fooser-q
  • Start date Start date
  • Tags Tags
    Control Noise
Click For Summary

Discussion Overview

The discussion revolves around the challenges of using Active Noise Control (ANC) to mitigate HVAC noise in meeting rooms. Participants explore the complexities of noise propagation through ducts, the effectiveness of various noise cancellation techniques, and the potential for system instability due to feedback issues.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Fred describes the problem of HVAC noise entering a meeting room, highlighting both motor noise and duct vibration as sources of periodic noise signals.
  • Fred proposes using an "anti-noise" signal generated by an inverting amplifier to cancel out the noise, but encounters issues with oscillation due to feedback from the anti-noise signal.
  • Marcus suggests implementing passive noise reduction techniques before relying on ANC, such as using vibration isolators and duct dampening, arguing that these methods may yield better results across a wider frequency range.
  • Marcus emphasizes the need for the ANC system to produce sufficient power to match the noise levels and warns about the limitations of typical speakers in producing low-frequency sounds.
  • Marcus recommends low-pass filtering the sensor signal to reduce feedback issues, suggesting a specific relationship between filter cutoff frequency and the separation distance between the microphone and speaker.
  • Marcus notes that separating the microphone and speaker may help eliminate feedback but could also reduce the effectiveness of noise cancellation.
  • Fred indicates attempts to stabilize the system through various circuit configurations and filtering methods, but has not achieved success, leading to a consideration of digital signal processing (DSP) techniques.
  • A later reply questions the effectiveness of DSP, suggesting that understanding the source of feedback may be more beneficial and inquiring about the types of filtration and settings being used.

Areas of Agreement / Disagreement

Participants express differing views on the best approach to tackle the noise issue, with some advocating for passive solutions while others focus on active noise control methods. The discussion remains unresolved, with multiple competing strategies being proposed.

Contextual Notes

Participants mention various technical challenges, including the need for effective feedback management and the limitations of current filtering techniques. There is an acknowledgment of the complexity involved in implementing DSP solutions, which may not be intuitive.

fooser-q
Messages
2
Reaction score
0
Hello everyone,

I'm new to this forum, and though this question may be addressed already in another thread somewhere, I'm hoping to get some focused discussion about solutions going here.

Problem:
HVAC noise is propagating down the HVAC duct, entering a meeting room / boardroom. The noise source is two fold in that it is a result of both the motor itself and the vibration in the duct. These are periodic noise signals with frequencies that can reach up to about 6KHz (top end) from generally around the 60Hz or harmonics thereof. The focal point is to remove as much of the low frequency with Active Noise Control, and the high frequencies will have to be dealt with using conventional damping / insulative techniques.

Solution:
For the low frequency portion of noise, produce an "anti-noise" signal by measuring the source, using an inverting amplifier, and outputting the phase-shifted through a speaker mounted in the duct to cancel the incoming noise waveform. I implemented this in a small scale using a loudspeaker to output a single/mixed tone signal to simulate the noise and used an electret condenser mic to measure the noise, and another loudspeaker to output the anti-noise.

New Problem:
The anti-noise now has a little bit of the desired effect of canceling out the original noise, but the microphone now is picking up the "anti-noise" and feeding that back into the system. This is causing oscillation and eventually system instability (ie: loud audio feedback squeal).

How do I solve this problem of removing the oscillation? Will I have to implement a whole new system using DSP with FIR filters? Should I use a noise gate on the measuring mic? Will I need to physically move the "anti-noise" speaker further away from the mic? Even if it cancels out the noise at the point where the "anti-noise" speaker resides, will that noise be destructively interfered with further down past the speaker in the duct?

Thanks for taking the time to read this lengthy post.

Regards,
Fred
 
Engineering news on Phys.org
Welcome to the Forums, Fred!

I am not at all an expert in HVAC, but I have implemented many electronic adaptive noise cancellers (ANC's) in radar, communications and instrumentation systems. The ANC is more complicated than your reversed-phase system, but may be something to consider if higher performance is needed. Here are some observations (opinions, actually):

1. Passive noise reduction should be implemented first. Mount the motor or entire HVAC on vibration isolators, use a rubber collar to connect the duct, use duct dampening, etc. Even if this is a large job involving equipment removal, do it! You'll achieve better results, over a larger frequency range, than any band-aid applied downstream. Done well, you won't need anything else. In this case, boring old-school beats exciting new.

Example: In a lab-space shuffle, my computer gear was once moved into a previously unused small room that had a large fume-hood duct running through it. The hood ran 24/7, and the noise could be heard up and down the hall. In fact, you could literally see the sheet metal sides of the duct vibrate and jump, so intense was the noise. The solution was to build a stout box of 1" plywood around the duct, pack it full of sand, and seal it. The room was quiet and nearby occupants up and down the hall were delighted that their rooms were quieter, too.

2. Your system must put out as much power as the noise. If the duct is vibrating, for instance, then your speaker and amp must be sized to produce equal duct vibration in order for cancellation to occur. Beware that even big speakers usually don't produce well below about 10 - 20 Hz. You need to broadcast full power at all noise frequencies.

3. Try low-pass filtering your sensor signal. You only get feedback when there's a 180 degree phase shift between sensed and injected signals, which won't happen at low frequencies where the wavelength is long.

If fc = filter cutoff frequency, v = speed of sound, and d = separation between mike and spkr, you want

d << v/(2*fc) = 1/2 wavelength.

Roll off at 55 Hz if you have 1 foot separation. You'll then need to use other techniques to cancel higher frequencies.

4. Separating the speaker and microphone will eliminate feedback but will also reduce cancellation since antinoise is injected at a different spot than measured noise. An ANC is the answer--it uses sophisticated digital signal processing to determine the antinoise waveform that results in optimal sound cancellation at the microphone. Here's an article on the concept:
http://en.wikipedia.org/wiki/Adaptive_filter"
This is a last resort, since such systems are expensive and require an expert.
 
Last edited by a moderator:
Thanks for your reply Marcus!

I have tried low-pass filtering input and output, reconfiguring the circuit and various polarity changes in an attempt to stabilize the audio output, but with no success. Near as I can figure, I need some sort of Echo cancellation filtering. We are likely going in a new direction along the lines of DSP with digital filtering to make this work.
 
If you aren't getting understandable results the easy way, then DSP (which is even less intuitive) may work even worse. I'd try to understand where your feedback is coming from. What kinds of filtration are you using? What settings? Are there other, hidden, feedback paths (ground loops, etc.)?
 

Similar threads

Replies
3
Views
2K
Replies
17
Views
6K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
4
Views
2K
Replies
11
Views
6K
Replies
16
Views
3K
Replies
3
Views
4K
Replies
138
Views
26K