How Do You Calculate Induced EMF in a Single Phase Transformer?

Click For Summary

Discussion Overview

The discussion revolves around calculating the induced electromotive force (EMF) in a single-phase transformer, specifically a step-down transformer with given parameters. Participants explore various methods and equations related to transformer operation, including the effects of load, resistance, and turns ratio.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant presents a series of attempts to solve for the induced EMF, expressing confusion over parameters such as turns ratio (N) and magnetic flux (phi).
  • Another participant suggests the need for the transformer's rated load to compute mutual inductance, which is necessary for determining the EMF at the primary due to secondary current.
  • A different participant proposes an assumption of a rated load of 24 kVA for calculation purposes.
  • One participant emphasizes the definition of induced EMF in relation to the magnetic field produced by an inductor, contrasting it with voltage across a capacitor.
  • Another participant calculates secondary current and induced voltage, questioning the simplicity of their findings and whether they accounted for all factors.
  • Concerns are raised about neglecting the effects of primary resistance and reactance in the calculations, with suggestions to use equivalent circuits for a more accurate approach.
  • Participants discuss the implications of the turns ratio, with one calculating a necessary ratio of approximately 9.62 based on the need to deliver rated output voltage at rated load.
  • There is a debate over the interpretation of the turns ratio and its implications for the transformer's performance under load.

Areas of Agreement / Disagreement

Participants express differing views on the assumptions regarding the turns ratio and the rated load of the transformer. While some calculations are presented, there is no consensus on the correct approach or final answer, and the discussion remains unresolved.

Contextual Notes

Participants highlight limitations in their calculations, including assumptions about the turns ratio and the need for additional information regarding the transformer's rated load. There are unresolved questions about the mutual inductance and the effects of primary circuit parameters.

SPYazdani
Messages
22
Reaction score
0

Homework Statement


A step down transformer, 2400/240 V, 50Hz has the following resistance and leakage parameters.
Z1 = R1 + jX1 = 4 + j12 Ω
Z2 = R2 + jX2 = 0.04 + j0.12 Ω

The transformer is operating at 80% of its rated load. The power factor of the load is 0.866 leading.
Determine the induced EMF in the primary side

Homework Equations



E = 4.443 f N B A
Ni = Hl = R phi
phi = BA
E = N d(phi)/dt

The Attempt at a Solution


I don't know how to solve for N and phi. It's as if I'm leading nowhere.
So far, I've got

Attempt 1:
a = V1/V2 = 2400/240 = 10
i1 = 2400/(4 + j12) = 60 - j180 = 189.7 cis (-71.57)
but then if I try to use Ni=Hl I get stuck on finding H from B=uH

Attempt 2: Try solving for N with L
L = N^2/R
N = sqrt(LR)
R = 4 + j12
Substitute L = N^2/R into N = sqrt(LR) you just end up with N = N (nothing useful)

Attempt 3: Transfer Z2 from the secondary side over to the primary side

a= 2400/240 = 10
a^2 = 100
Z2' = 100 (0.04 + j0.12) = 4 + j12
Zeq = Z1 + Z2' = 2 (4 + j12) = 8 + j24
Then using Ni = R phi
i = 2400/(8+j24) = 30 - j90 A
R = 8 + j24
Then get stuck on finding phi...

Attempt 4: using V1/V2 = N1/N2
2400/240 = N1/N2
Assume 100 turns in N1, then N2 = 10 turns.
and let phi = i
then E = 4.443 (50) (100) (60-j180) = some massive number in MegaVolts

I've searched and searched in lecture notes for anything to do with the turns ratio, but can't find anything useful.

Please help.
 
Physics news on Phys.org
Need to know the transformer's rated load.

Then I would compute mutual inductance M which leads directly to emf_1 due to current_2.

There may be another way to do this using equivalent circuits, but keep in mind we want the emf at the primary generated by the current in the secondary.
 
Definitely we need to know the transformer's rated load.
 
Ok for the purposes of the exercise, I'll try 24KVA and if I get stuck, I'll post back. Thanks
 
Think 'out of the box' on this one.

Think about what "the emf induced in the primary" really means.

If I have a single coil L and apply a voltage V, what is the "induced emf"?

Hint: a voltage across an inductor is an emf. Why? Because the voltage across the inductor is produced by its magnetic field, so one form of energy (magnetic) is transformed into another (electrical). That is the definition of an emf.

By contrast, the voltage across a capacitor is not an emf.
 
Last edited:
Thanks rude man. I worked on this problem shortly after your last post and never got round to replying.
I found I2 = 24000(0.8)/240 = 80 Amps --> arccos 0.866 = 30 degrees --> I2 = 80/_30 Amps
Then E2 = V2 + I2Z2 = 240 + (80/_30)(0.04 + j0.12) = 237.97 + j9.91 Volts
E1/E2 = a = 2400/240 = 10
So E1 = aE2 = 10(237.97 + j9.91) = 2379.7 + j99.1 Volts

Was it really that simple?
 
Your answer is probably very close to right. But it seems you did not include the effects of R1 and X1.

As I see it, the voltage induced in the primary winding is just V1 - I1R1

so use your equiv. ckt. to compute I1 and you're home. The answer is going to be close to V1 which = 2400V, and therefore to your answer also.


My rationale is as follows:
Basic equations for a loaded transformer (load = ZL) are
V1 = I1(R1 + sL1) + sMI2
V2 = -I2ZL = I2(R2 + sL2) + sMI1

where s = jω for sinusoids, L1 and L2 are the open-circuit primary and secondary winding inductances, R1 and R2 are the primary and secondary winding resistances, and M = mutual inductance. I1 and I2 are defined as currents flowing into the respective windings and it's assumed that dotted ends face each other.

So the "voltage induced in the primary" by this picture is in my opinion
V1(induced) = sL1I1+ sMI2. Note that X1 and X2 are included in M.

There may be room for interpretation here as to what exactly is "the EMF induced in the primary side".
 
Last edited:
  • Like
Likes   Reactions: 1 person
SPYazdani said:
Was it really that simple?
Probably not. :smile:

In power engineering, there are conventionally accepted approximations. You need to be guided in this by worked problems you have encountered in your course.

I doubt that you can assume the turns ratio here is 10:1 because if it were then with rated supply voltage (24000V) the transformer would not be delivering rated output voltage (240V) at rated load (24kVA). The buyer would be upset at being short-changed on his voltage. :frown:

So when delivering full rated output (240V, 100A) the turns ratio must be such that it overcomes the voltage drops in the transformer model's non-idealities.

I calculate the necessary turns ratio to be 9.62 but I am rusty on this so that may not be exact. But it supports the intuitive expectation that the voltage divide across the turns must be less than 10:1 so my answer is around what I'd expect.

That completes half of the working, the hardest part.

You don't happen to know the answer, or have a worked example as a guide?
 
rude man said:
So the "voltage induced in the primary" by this picture is in my opinion
V1(induced) = sL1I1+ sMI2. Note that X1 and X2 are included in M.
How will you determine the value of M here?
 
  • #10
NascentOxygen said:
I doubt that you can assume the turns ratio here is 10:1

I didn't assume. The turns ratio is V1/V2 = N1/N2 = I2/I1 = 2400/240 = 10/1

because if it were then with rated supply voltage (24000V) the transformer would not be delivering rated output voltage (240V) at rated load (24kVA).

Where did you get 24000 Volts from? Do you mean 24000 VA? They are two completely different quantities

I calculate the necessary turns ratio to be 9.62 but I am rusty on this so that may not be exact.

Where did you get 9.62 from?

You don't happen to know the answer, or have a worked example as a guide?

Nope.
 
  • #11
SPYazdani said:
I didn't assume. The turns ratio is V1/V2 = N1/N2 = I2/I1 = 2400/240 = 10/1
That looks like an assumption to me.

Where did you get 24000 Volts from?
That's 2400V with a bouncy 0 key. :smile:

Where did you get 9.62 from?
I calculated it, on the basis that the rated voltage of a transformer must be delivered at rated load. You will get 240V out of a precisely 10:1 transformer only at zero load.
 
  • #12
NascentOxygen said:
That looks like an assumption to me.

Heh, that's what our lecturer taught us :smile:

That's 2400V with a bouncy 0 key. :smile:

:smile:

I calculated it, on the basis that the rated voltage of a transformer must be delivered at rated load. You will get 240V out of a precisely 10:1 transformer only at zero load.

Ok, I'm satisfied this problem is sufficiently solved.

Thanks guys.
 

Similar threads

Replies
21
Views
6K
Replies
1
Views
7K
  • · Replies 1 ·
Replies
1
Views
7K
Replies
10
Views
3K
  • · Replies 14 ·
Replies
14
Views
19K
Replies
3
Views
2K
Replies
2
Views
11K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 18 ·
Replies
18
Views
13K
Replies
5
Views
2K