The behavior of a transformer's secondary coil varies significantly under different circuit conditions: open circuit, closed circuit with a load, and shorted circuit. In an open circuit, the primary current consists of the exciting current, which includes magnetizing, hysteresis, and eddy current components, with the voltage ratio defined by the turns ratio. When the secondary is loaded, the secondary current is determined by the load and follows Ohm's law, maintaining a constant voltage if the primary is constant voltage driven. In a short circuit, this condition is suitable for current transformers but should be avoided with voltage transformers, allowing for safe current measurement across an isolation boundary. Understanding these distinctions is crucial for proper transformer application and operation.
herich
Messages
17
Reaction score
0
There are primary and secondary coils in a transformers. So, what hat are the difference between when the secondary coil is in 1)open circuit, 2)closed circuit with a load, and 3) shorted circuit?

When can the ideal transformer equation be used? It seems that not only is it related to whether the transformer is ideal or not, but also related to which case (1, 2, or 3 above) the secondary coil is in.

I'm much confused. Please help clarify my concept! Thanks.
 
Physics news on Phys.org
1) open circuit - primary current is the magnetizing current plus the hysteresis and eddy current components. The total is called "exciting current". Vp/Np = Vs/Ns, as the P & S voltages are directly proportional to the turns ratio. Open secondary should only be used with voltage transformers, never with current transformers.

2) loaded - secondary current established with load and Ohm's law. If primary is constant voltage driven, then secondary displays constant voltage behavior. Vp/Np = Vs/Ns, and NpIp = NsIs.

3) short circuit - must never be used with voltage transformers, but is ok with current transformers. NpIp = NsIs. This is used when measuring current across an isolation boundary. The secondary is isolated and allows connecting an ammeter so that large currents can be safely measured. If the turns ratio is 50 to 1, then 50 amp line currents can be measured with a 1.0 amp meter.

Does this help?
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...