How Does Discriminator Control Influence Reheat Requirements in HVAC Systems?

  • Thread starter Thread starter pinkcashmere
  • Start date Start date
  • Tags Tags
    Control
AI Thread Summary
Discriminator control in HVAC systems is a selection algorithm used to determine the optimal control variable, balancing supply air temperatures to meet the cooling requirements of different zones. In the context of a dual-duct constant-volume system, it aims to satisfy the warmer zone's cooling needs while minimizing reheat for the cooler zone. The discussion highlights the complexities of calculating reheat requirements based on design air flow rates and cooling loads for each zone. There is a request for clarification on basic conditions related to volumetric flow rates and damper positions for accurate reheat calculations. Understanding these principles is essential for effective HVAC system design and operation.
pinkcashmere
Messages
17
Reaction score
0

Homework Statement


A factory has two zones. Zone 1 and 2 are both maintained at 75FDB. The design supply air flow rates to Zone 1 and 2 are 320 and 200 CFM, respectively. At a certain hour in summer, the cooling loads for Zone 1 and 2 are 6,000 Btu/hr and 3,000 Btu/hr, respectively.

Assume dry air conditions and air density of 0.075 lbm/ft3 .

(a) If a dual-duct constant-volume system is used with discriminator control for both cold and hot air, what would the required amount of reheat (Btu/hr) be provided by the hot air in each zone at the hour? The design cold and hot air supply temperatures are 55FDB and 100FDB, respectively.

(b) If a VAV system with 20% minimum position is used with discriminator control, what would the required amount of reheat (Btu/hr) be provided by a reheater in each zone at the hour? The design supply air temperature is 55FDB

Homework Equations

The Attempt at a Solution


I just want to know what discriminator control is in the context of this problem. I can't find any example problems like these on Google.
 
Physics news on Phys.org
Welcome to PF!

I'm an HVAC engineer and this is the first I've heard the term. Googling, I found a Google books link to an old controls book that shows it as a selection algorithm for picking the control variable. In this case, that appears to be the maximum allowable supply air temperature to satisfy the warmer zone's cooling requirement without reheat...and at the same time, the lowest temperature to heat the cooler zone.

https://books.google.com/books?id=1...v=onepage&q=discriminator control vav&f=false

I say "appears" because this is an archaic control method (the dual duct part) that I'm not too familiar with.
 
russ_watters said:
Welcome to PF!

I'm an HVAC engineer and this is the first I've heard the term. Googling, I found a Google books link to an old controls book that shows it as a selection algorithm for picking the control variable. In this case, that appears to be the maximum allowable supply air temperature to satisfy the warmer zone's cooling requirement without reheat...and at the same time, the lowest temperature to heat the cooler zone.

https://books.google.com/books?id=1VZ-BgAAQBAJ&pg=PT180&lpg=PT180&dq=discriminator+control+vav&source=bl&ots=3r5Fj62Jld&sig=5nRiwlin8CAYWcOhspMU0k8sq7o&hl=en&sa=X&ved=0CBsQ6AEwAGoVChMI3bCxove_yAIVwxc-Ch3guAmV#v=onepage&q=discriminator control vav&f=false

I say "appears" because this is an archaic control method (the dual duct part) that I'm not too familiar with.

thanks very much for the reply!
I have another question

http://postimg.org/image/quz6smejb/full/
I don't really understand the basic conditions involving design/minimum volumetric flow rates to calculate reheat or to change the damper position. I was wondering if you could explain
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...