How Do Heater Contactors and SSRs Control Heating Elements?

  • Thread starter Thread starter ismat143
  • Start date Start date
  • Tags Tags
    Heater
AI Thread Summary
Heater control is achieved through contactors and solid-state relays (SSRs), with SSRs regulating output via pulses from a PID controller. When 440 volts is applied to L1, L2, and L3, the K3 contactor activates automatically. The voltage at terminals 4, 5, and 6 corresponds to the 440V line voltage, while terminals 7, 8, and 9 receive pulsed 440V. The discussion emphasizes the importance of understanding how heating elements are turned on and off based on these voltage inputs. Proper circuit configuration is crucial for effective heating control.
ismat143
Messages
10
Reaction score
0
1.jpg


1.If i apply voltage 440volts at L1,L2,L3 the K3 (contactor) will get on automatically?
2.How this SSR work and what should be the voltage at 4,5,6 and 7,8,9(X1 terminals)?

The main thing i want to ask is how this heating 1 and heating 2 gets ON and OFF and at what voltage?

Thank you.
 
Engineering news on Phys.org
Welcome to PF ismat. It looks like the heaters are being controlled by SSR (which is a silicon controlled rectifier, I think) and its ouput is controlled by pluses supplied to the + and - terminals. These pulses could be coming from a PID controller. And K3 appears to be contacts for a relay. Are there other parts of the circuit you are not showing?

The voltage at 4,5,6 is just your 440V line voltage. The voltage at 7.8.9 will be pulsed 440V.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...