How to conduct continuity test for cable sized 250 sq. mm?

AI Thread Summary
Testing a 250 sq.mm cable for continuity can be effectively done using a digital or analog multi-tester, especially when the goal is to identify cable groupings. It is crucial that all power sources are disconnected during the test to ensure safety. One method involves shorting pairs of conductors at one end and checking for continuity at the other end to identify the cables. Alternatively, applying a voltage source, such as a car battery, can help determine which cables correspond to each phase by measuring the voltage at the far end. Proper adherence to safety guidelines and codes is essential during this process.
xiv_wolf
Messages
7
Reaction score
0
Good day everyone!

I would like to ask if it's ok to use a digital or analog multi-tester in testing a 15 meters, 250 sq.mm cable? We are tracing buried cables from the main circuit breaker to the concrete post. We are connected to Delta X'mer, 230 V, 4 wire w/ ground System. The x'mer will not be connected to the system while testing. I've attached the schematic diagram of the proposed method of testing. I appreciate any suggestions/recommendations. Thank you very much.

2lw86bp.jpg
 
Engineering news on Phys.org
If the purpose of the continuity test is to verify which cable is which, then a VOM (digital or analog) will certainly do the job. If you have known, or suspect issues with the integrity of the cables then you should consider more robust testing methods suggested and approved by a certified engineer. 500kVA is a lot of current, and demands rigid compliance with codes and safety guidelines.

Fish
 
Thanks for the reply Fish4Fun! We're conducting continuity test to verify which cable is which so that the provider of x'mer can connect the correct cable for each phase. When the provider initially connects all the 4 wires of each phase, the fuse cut-out of the x'mer tripped off. We are instructed to determine the correct groupings of the cable because all of the markings have been erased. The Electrical Engineer of the building has passed away and the blue print that left is quietly old.
 
ok You have stated ALL power is disconnected!

so you don't have to extend the meter leads between the far ends of the cables.
At the top of the post end in the first group of 4 conductors strap a pair of them together
at the main panel board end look for a s/c between a pair of cables in that group
you can then use that to identify the other 2 cables of the group.
Once those 2 cables have been marked you can remove the short between the the initial 2 you shorted together and identify them individually using a short between one of them and one of the 2 marked cables.
10 minute job ... piece of cake :)

Dave
 
Dave's idea seems pretty good. We did that once.

You could also try connecting the cables to a voltage source one at one side and measure the voltage on the other side. Maybe use a car battery. Two wires one to + and other to -ve terminal of battery. Measure the voltage on the other side and you'll have a match.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...