How to find ampacity of 1/2 by 4 copper buss bar

  • Thread starter Thread starter Crazyhorse2882
  • Start date Start date
  • Tags Tags
    Copper
AI Thread Summary
To find the ampacity of a 1/2" by 4" copper bus bar, the correct interpretation of the NEC formula is crucial. The formula indicates 1000 amps per square inch, so with 2 square inches of copper, the bus bar can carry 2000 amps. Confusion arises when misreading the formula as division rather than multiplication. It's important to ensure unit consistency in calculations to avoid errors. Understanding this concept clarifies the ampacity rating significantly.
Crazyhorse2882
Messages
20
Reaction score
0
How to find ampacity of 1/2" by 4" copper buss bar

I have a question about finding ampacity of buss bar. I have a 1/2" by 4" copper buss bar and the only formula I can find in the NEC is 1000/in^2 but when I use this formula I come up with 500 amps and I'm being told that 1/2" by 4" copper bus bar is good for 2000 amps. Can somebody help me please and explain what I'm missing. Thank you
 
Engineering news on Phys.org
As far as I know, 1000/in^2 is merely a "rule of thumb".
 
http://www.stormcopper.com/design/ampacity-tables.htm
 
Am I missing something here? You have 2in^2 of copper bus bar(4*.5=2) and 1000 A/in^2 should be 2000A.
Correct? And ,yes, as per NEC (US) {250A/(1/4 in^2)} is acceptable. So 1000A/in^2 is correct.
 
I tell you why I'm confused, I read 1000/in^2 as 1000 divided by inches squared. I think the NEC would be right to rewrite that so it looks like multiplication
 
From ABB Switchgear Manual Table 13-4 Continuous current carrying capacity [AC up to 60 c/sec]
For indoor installation at 35oC.copper bar max.temp. 65oC.Continuous load.
10*100 mm [0.4”*4”] 1810 A
10*120 mm [0.4*5”] 2110
 
Crazyhorse2882 said:
I tell you why I'm confused, I read 1000/in^2 as 1000 divided by inches squared. I think the NEC would be right to rewrite that so it looks like multiplication

Your interpretation would imply that the larger the buss bar the less current it could carry, that should clue you in that somethings wrong.

Read it as 1000 amps per square inch for 2 square inches. (Driving 1000 miles per hour for 2 hours = 2000 miles).
 
Last edited:
Do the math with the units...if your math ends up with the wrong units - you have the formula wrong:

A/in^s * in^2 = A... amazing how many people do not use this simple check of their thinking.
 
Back
Top