How to know the VA rating of a transformer

  • Thread starter Thread starter piyushpandey
  • Start date Start date
  • Tags Tags
    Rating Transformer
Click For Summary

Discussion Overview

The discussion revolves around determining the MVA rating of a transformer when only the voltage (KV) is provided, without additional information such as power factor or current. Participants explore the relationship between voltage and power ratings in transformers, including the implications of using VA versus watts as a specification.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Meta-discussion

Main Points Raised

  • One participant notes that the KV rating alone does not determine the MVA rating, as transformers with the same voltage can have vastly different power ratings based on their current handling capabilities.
  • Another participant explains the formula for power (P = I x E) and suggests that the interview question may have been testing basic electrical concepts.
  • There is a discussion about why volt-amperes (VA) are used instead of watts, with some participants indicating that VA is relevant in AC circuits due to the power factor, which affects the actual power delivered.
  • A participant raises the question of why transformers are rated in VA rather than watts, prompting further exploration of the implications of power factor in AC systems.
  • Some participants express uncertainty about the interview question's intent, suggesting it may have been designed to assess experience rather than technical knowledge.
  • One participant mentions that transformers are standardized and that knowledge of common voltage levels and transformer sizes could be relevant in such interviews.

Areas of Agreement / Disagreement

Participants express a range of views on the relationship between voltage and power ratings, with no consensus on how to determine the MVA rating from KV alone. The discussion includes both technical explanations and personal experiences related to interview questions, indicating a mix of agreement on the complexity of the topic but disagreement on specific interpretations.

Contextual Notes

Limitations in the discussion include the absence of specific values for current or power factor, which are necessary for calculating MVA from KV. The conversation also reflects varying levels of familiarity with transformer specifications and their implications in practical scenarios.

Who May Find This Useful

This discussion may be useful for electrical engineering students, professionals preparing for job interviews in the electrical field, and individuals interested in the technical specifications of transformers and their applications.

piyushpandey
Messages
1
Reaction score
0
Hello to all


I am an electrical engineer and in an interview I was asked to tell the MVA rating of a transformer of few KV , and nothing was given means neither the power factor and nor the current , so I want to ask you people is there any way to determine the MVA rating of the transformer from the KV or vice-versa.


Please tell me with an example if possible.



Thank you
 
Engineering news on Phys.org
I am no transformer expert, but I think the KV in your case is only the voltage input or output of the transformer, You can have two transformer of the same KV in and same KV out but of totally different power rating. eg, if you take two transformers both 110V in and 12V out. One can be rated only 1A output, the second one can be 10A. Both has the same voltage but the second one can handle 10 times the power.

For MVA, is this Mega Volt Amp? That is a mighty big transformer! My understanding VA rating is power rating. eg. 100V at 1A is 100VA, so is 50V at 2A or 25V at 4A. They all 100W rating in my understanding. I have no idea why they rate transformer like this rather than just simply by Watts.

Don't trust everything I said, this is just my understanding.
 
P = I x E

to determine power you need to know volts and amps and that should have be on the nameplate of the machine. The interview process might have been testing you on this basic concept.
 
2milehi said:
P = I x E

to determine power you need to know volts and amps and that should have be on the nameplate of the machine. The interview process might have been testing you on this basic concept.

What is the reason people don't use watts as specification instead using VA if they mean the same thing?
 
yungman said:
What is the reason people don't use watts as specification instead using VA if they mean the same thing?

A volt-ampere (VA) is the unit used for the apparent power in an electrical circuit, equal to the product of root-mean-square (RMS) voltage and RMS current.[1] In direct current (DC) circuits, this product is equal to the real power (active power) [2] in watts. Volt-amperes are useful only in the context of alternating current (AC) circuits (sinusoidal voltages and currents of the same frequency).

http://en.wikipedia.org/wiki/Kva"
 
Last edited by a moderator:
What did you do?
The best answer would be to explain to them that the question isn't answerable.
 
dlgoff said:
http://en.wikipedia.org/wiki/Kva"

So real power in watts is the real part of VA?
 
Last edited by a moderator:
This image is worth a thousand words

Power_Triangle_01.png
 
Last edited by a moderator:
"What is the reason people don't use watts as specification instead using VA if they mean the same thing?"

In AC, Watts = Volts X Amps X (cosine of angle between them)
that cosine term being called "Power Factor"
see 2mile's triangle in post immediately above


If angle is not 0 , there's more amps than are necessary to deliver the watts.
The copper in the transformer has to carry those extra amps.
While those amps don't deliver power to the load, they do heat the copper windings in the transformer.

so they rate transformers in volt-amps not watts.
 
  • #10
I learn something today!
 
  • #11
Hmmm, some places toss out questions whose answers depend on experience. For example, I remember being asked about common part numbers during an interview. Without having worked in the business, the question was unanswerable...
 
  • #12
They could have been checking on your experience, as transformers are fairly standardized, and the voltages they interact with are very standardized (433V, 1kV, 11kV, 33kV, 66kV, 132kV etc). For example, 433V (which is slated for machines using ~415V and allowing for a voltage drop across the connecting cables) is predominant in mines with 1500kVA to 2500kVA transformers.

They could have been testing on the research you did regarding the company whom you were trying to get a job with (online and/or talking to people). Most company's have a rough operating range for transformer (power) size, i.e. 250kVA to 50MVA. This can be limited by the lifting capacity of the cranes they have, the expertise of the designers, the market they are aiming for or the voltages their equipment can handle.

If they don't give you any values then it can be safe to assume they don't want you to do any math.
 

Similar threads

Replies
4
Views
3K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
4
Views
6K
Replies
1
Views
2K
  • · Replies 13 ·
Replies
13
Views
17K
  • · Replies 27 ·
Replies
27
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K