HVAC Electrical Issue: Current Leakage from Furnace

Click For Summary
The discussion revolves around a current leakage issue from a newly installed furnace, with the user seeking help to diagnose the problem. After isolating the furnace and grounding it, a fluctuating leakage of about 20mA remains, raising concerns about potential faults within the unit. Participants suggest that the leakage could stem from components like an EMI filter or a fan capacitor, and emphasize the importance of dead testing to identify the source of the issue. They recommend measuring resistance between live and earth conductors and using a Megger insulation tester for more accurate diagnostics. The user expresses frustration with the furnace manufacturer’s refusal to provide electrical service despite the ongoing issues.
  • #31
I had a part-baggy of them, dating from final attempt to make some [REDACTED] WiFi range-extenders work for more than a week at a time without reset.
Ferrites are about the size of top finger-bone, two halves just clip together over 8mm OD 'Twin+E' flex. So, probably 9mm ID, with a range of sizes available.

Look for such under A**n's passive components, ferrite cores: They're about 2/$
I'd clipped one onto the Dyson 'hoover' lead, three onto the fridge-freezer lead, sundry else-where.

Yes, multiple turns through a toroid are much 'better' electronically, but such tight turns would put undue strain on the flex. Also, with many UK appliances having 'moulded-on' plugs, I'd have to cut such off...

I reckon culprit was the big fridge/freezer's 'stat' cycling, but never proved it: Partial correlation at best...
For a long time, other suspect was the kitchen's suspended ceiling, whose strip-lights became an endless race to keep up with their flickery tubes and blinky-blink starters. I've since replaced all such with pin-compatible LED strips, just needed to swap the blinky starters by supplied dummy 'place-holders'. So, with hind-sight, was not them....

FWIW, I abandoned those [REDACTED] WiFi repeaters, hard-wired Cat_5 cable to a couple of WAP/routers. After which, every-one was happy until BossCat, a BIG 'Spotty', figured how to un-latch patch-cables that lacked protective boots....
Poltercats !!!
 
Engineering news on Phys.org
  • #32
OK furnace finally failed. I didn't even get to start the dead testing yet.

Right now, when I switch it on and call for heat, I can hear it starting up and it reaches a steady hum but the fan won't start. I took out the fan motor capacitor which is a 5uF +-5% and tested it. The reading really bounced around a lot then settled on 4.62uF (just out of range) then dropped to 0 after that.

I noticed that there is a little rubber cap that is supposed to cover the contacts and it was not on, just dangling down the wires. I put the rubber cap back on and no stray current on the power line. So I am thinking that what @Tom.G . said may be the solution.


Just for your entertainment, enjoyment and for a little laugh on a Friday afternoon:

The company is really mad and says their techs insist that there is nothing wrong with the electrical but none of the techs did any sort of electrical diagnostics AT ALL and upon visual inspection they missed the fact that the ground lead was not connected in the electrical entry box inside the furnace. None of the techs that came even had the equipment to do electrical testing and the company is telling me that if I touch the furnace any more I will void my warranty. DO I laugh? DO I cry? DO I just buy a new capacitor and install it myself and pretend it was like that the whole time... One of the company representatives who I talked to on the phone tried to insist to me for a good long time that there was in fact NO fan motor capacitor inside my furnace for a while...

Is this incompetence?
Is it gas-lighting?
Is it a miscommunication somehow?
It's been easier to learn HVAC from scratch than it has been to deal with the "techs" and "experts."

--------OK Enough entertainment for now--------------

Anyhow this thread has been extremely useful and I have learned a lot. Thank you all for your detailed explanations and your troubleshooting ideas. I have actually become really fascinated with HVAC and hope to continue learning about it when this dumpster fire of a problem is done.

I will post updates when the company sends their techs again on Monday. Happy weekend!
 
  • Informative
  • Like
Likes DeBangis21 and Tom.G
  • #33
I would recommend that you avoid trying to troubleshoot this furnace if it is failing this badly under warranty. If the tech who responds to your warranty complaint sees that you've been taking it apart trying to troubleshoot it, they can deny service for cause.

(Full disclosure -- my wife works in the home warranty industry, and deals with DIY homeowner "fixes" on warrantied appliances regularly...)
 
  • Like
Likes UrbanFarmEngineer
  • #34
berkeman said:
I would recommend that you avoid trying to troubleshoot this furnace if it is failing this badly under warranty. If the tech who responds to your warranty complaint sees that you've been taking it apart trying to troubleshoot it, they can deny service for cause.

(Full disclosure -- my wife works in the home warranty industry, and deals with DIY homeowner "fixes" on warrantied appliances regularly...)

I know.
It is just so frustrating when you watch them fumble around and not even have the tools to diagnose.
You are right tho. It just makes things so much harder.
 
  • #35
OK I am back and this time I have some pictures. As we have now shifted from cold weather to hot weather I put on the AC and noticed same problem as with the furnace line. The dedicated AC line has net current on it.

Here's what is going on inside the Furnace:

Just learning the colors for HVAC here but condenser (AC) power enters the furnace from the AC and has black and white wire like what you'd see with AltCurrent wiring (except no green ground)

The main control board inside the furnace looks like this:

HVAC Control Board.jpg

From Top to Bottom:

C Terminal:
The black wire is coming from the condenser
and the blue wire is the fan wire from the thermostat being used as a common

R Terminal:
From thermostat of course

Y/Y2:
Black coming from thermostat and white coming from condenser
**Is that the problem here??*** Should it be white to common and black to Y/Y2??
(see below)

HVAC Control Board Labeled.jpg



Dedicated AC (condenser) line has net current (just like the furnace line):
AC line Ammeter Reading.jpg


Switch the Condenser black from common to Y/Y2 and the common from the condenser to C terminal?
 
  • #36
Ok, you are introducing a lot of things here. Simplify simplify simplify! Start by turning off the main breaker and ALL other breakers in your house. Measure the cable feeding your furnace. You may still have current showing. It's not uncommon for ground paths to carry current through the water system. It's not out of the question for it to show up someplace like this. If you do have current showing here there's likely little you can do about other than hunt around to verify the path.
-
Assuming the current has fallen to zero, start turning on breakers. Start with the main only. Watch your meter and turn on one breaker at a time while keeping an eye on your meter. Leave the furnace and A/C unit until last. Let us know the results.
 
  • Like
Likes UrbanFarmEngineer
  • #37
Nice! OK will do. I will post my results.
I am on an isolated ground for my home i.e., a grounding plate, my house it not grounded to the water system so we can scratch that off for sure.
Let me do those tests and then get back.

What about the pic of the wiring diagram? Does it look like the condenser common and hot are reversed?
 
  • #38
UrbanFarmEngineer said:
Nice! OK will do. I will post my results.
I am on an isolated ground for my home i.e., a grounding plate, my house it not grounded to the water system so we can scratch that off for sure.
Let me do those tests and then get back.

What about the pic of the wiring diagram? Does it look like the condenser common and hot are reversed?

Oh, and also since I last posted my electrician confirmed that the line to the furnace and the AC line are isolated so there are no shunted neutrals or anything like that happening here.

Just a Note: When I get the stray current on the furnace line and the AC line, ALL of it goes away when I turn off the furnace breaker.
 
  • #39
Ok, again, simplify simplify. We know flipping the furnace breaker makes the problem go away. Start on the other end. Disconnect things until the imbalance goes away. It's possible the current imbalance is from the low voltage source in your furnace. Colors on wires don't mean anything except for convention. This is important of course, but without knowing which color is hooked where on the other end, who knows...
 
  • Like
Likes UrbanFarmEngineer
  • #40
Yes, I have narrowed it down to inside the furnace playing with it and testing it over the past few months. OK will start with the furnace first. Maybe I should open the AC and see which color is the common and which is the hot (what do HVAC ppl call the 'hot?)?

Are the terminals in a typical condenser unit labeled? SO if I were to open it I could tell which color they've hooked up as the common?
 
  • #41
UrbanFarmEngineer said:
Are the terminals in a typical condenser unit labeled? SO if I were to open it I could tell which color they've hooked up as the common?
Likely.
 
  • #42
Averagesupernova said:
Likely.

OK good place to start I think?
 
  • #43
UrbanFarmEngineer said:
OK good place to start I think?
You need to be isolating. When the current imbalance goes away, you are closer to the solution. It's really no different than you flipping the breaker and noticed the imbalance went away. Divide and conquer I believe is one way of describing it. Remove low voltage wires at the furnace or the other end of them. Your choice.
 
  • #44
Averagesupernova said:
You need to be isolating. When the current imbalance goes away, you are closer to the solution. It's really no different than you flipping the breaker and noticed the imbalance went away. Divide and conquer I believe is one way of describing it. Remove low voltage wires at the furnace or the other end of them. Your choice.



OK so I have been working at it and traced it back to this:



Wiring Diagram Excerpt from Furnace.jpeg


Here is my question:
What should this look like practically:
  • Hot is coming into Molex terminal 1
  • Another wire leaving Molex Terminal 1 going to Blower Motor
What I have inside my furnace is this:
  • BLK Hot bypasses terminal 1 of Molex Plug on board
  • BLK Hot is put through a connector (heat shrink butt connector..?) and turns into a BROWN wire
  • BROWN wire is then put through another connector (spade connector..?) and comes out as 2 brown wires
  • One BROWN is looped back and attached to terminal 1 on the board
  • The other goes on to the Blower Motor

The pic below, hard to see, circled is one of the brown wires after the split being inserted into terminal 1 of the plug on the board.
Right or wrong?

Furnace Control Board Circled to Hilight.jpg
 
  • #45
So what you are saying is the diagram doesn't match the physical wiring? You need to draw something. I'm not going to try to decode your description. Make a schematic. It's unlikely that it is actually wired as the diagram shows. If the breaker is turned on, then the blower would run all the time.
-
Just exactly how did you arrive at 'traced it back to this'? Did you isolate the two units as I suggested? The idea is to shrink the number things involved until there is very little left.
 
  • Like
Likes UrbanFarmEngineer
  • #46
OK I will draw a diagram.

I traced the current imbalance and did continuity tests on the components along the way--everything was OK-and as I kept going I came upon this wiring error.

I will try to take a picture to better explain it's just way back in the furnace.
 
  • #47
You still don't seem to understand why you need to isolate. Of course you traced the imbalance to the place you circled. It's basically the first stop. Unless the current is leaking in the door switch, the amount of current around the place you circled will be them same as the hot wire on the way from the breaker panel.
-
It's likely not what you refer to as a wiring error. Not sure why they do this but there is likely a good reason.
 
  • Like
Likes UrbanFarmEngineer
  • #48
I did continuity testing on the whole furnace, section by section, piece by piece.
Everything else was OK
So I traced it back.... it is not that it is the first place it is just that the wiring is not as per the diagram in that spot and that spot only. That is why I am asking you guys if it is OK. Let me draw something and post it and you can tell me if it is a problem.

Sorry I am just extremely tired and not explaining this sufficiently.
 
  • #49
I tested everything components and even the wires themselves. I found one spot where a wire was pinched and had copper exposed and it was touching the cabinet and leaking some current onto it but that wasn't the main problem although it took some of the stray current off of the main line.

Sorry again I am just incredibly exhausted from work.
 
  • #50
Sorry I am just extremely tired and not explaining this sufficiently.
Aww, heck! Get some SLEEP. We, and the problem, aren't planning to go away. 😁
 
  • Like
Likes UrbanFarmEngineer
  • #51
Thank you. We ran into a last minute glitch in a formulation project that I was a part of and I haven't slept at night in a few days. haha I am half asleep and the other half crazy. Sleeping between 6:00 AM and noon makes it feel like time is melting.

I was working on the furnace for fun between project breaks.

The last thing that I can sensibly do or want to do right now (sorry @Averagesupernova ) is to make a diagram before I regain my sanity.

Can someone be so very kind as to tell me how you'd wire that little bit in the circle at contact 1 on the Molex so that I can start thinking about it during bout of semi-consciousness?

Also this is a noob question because I don't wire things for a living... what the heck is this type of connector called because this is what I have in the place where I believe there may be that wiring error.
Split Connector.png

 
  • #52
OK here is the best I could do on my Chromebook with the mental resources that I currently have access to:

Manufacturer's Diagram (Close Up of Relevant Section)


Selection.jpeg





The Wiring in my Furnace
(The Best I Could Do With What I Got)

Actual Wiring.jpg



Seeking your advice. You guys do this for a living and I don't but I can learn if you are willing to teach.
 
Last edited:
  • #53
How is it possible that the same amount of current is going to flow to contact 1 in the first diagram as in the second?
 
  • #54
UrbanFarmEngineer said:
Can someone be so very kind as to tell me how you'd wire that little bit in the circle at contact 1 on the Molex so that I can start thinking about it during bout of semi-consciousness?
How we would wire it is not relevant. You need to provide a diagram of how it IS wired. If you have in fact done so then I question the accuracy. The way it is shown would have the blower motor running all the time. This does not seem right.
-
UrbanFarmEngineer said:
How is it possible that the same amount of current is going to flow to contact 1 in the first diagram as in the second?
It doesn't matter what goes into contact one. It matters that whatever total current goes into the furnace assembly on the hot wire also comes back on the white wire. Wherever it branches off inside the furnace is not relevant.
 
  • Like
Likes UrbanFarmEngineer
  • #55
Most likely the current consumed from your thermostat to maintain sensor and general operation.

-JA
 
  • #56
OUcafe said:
Most likely the current consumed from your thermostat to maintain sensor and general operation.

-JA
Current is not consumed. What goes in has to come back out. The issue is that it's not. It's getting away someplace else. Leaking back through an alternate path. Or, one thing I've suspected is that the low voltage that goes to the outdoor unit is leaking off. This may go back through the ground of the outdoor unit and find it's way back through the ground on the furnace. This is why I've asked the op to isolate the two by disconnecting the low voltage wires between the two. I have apparently been unsuccessful in that.
 
  • Like
Likes UrbanFarmEngineer
  • #57
Averagesupernova said:
How we would wire it is not relevant. You need to provide a diagram of how it IS wired. If you have in fact done so then I question the accuracy. The way it is shown would have the blower motor running all the time. This does not seem right.
-

It doesn't matter what goes into contact one. It matters that whatever total current goes into the furnace assembly on the hot wire also comes back on the white wire. Wherever it branches off inside the furnace is not relevant.

The fan is always running you are right.
The fan cannot be turned off at the thermostat either.

The only way to get the fan to go off is to shut power for everything down at the thermostat.
 
  • #58
UrbanFarmEngineer said:
The fan is always running you are right.
The fan cannot be turned off at the thermostat either.

The only way to get the fan to go off is to shut power for everything down at the thermostat.
Ok. Now we're getting somewhere. I would not want it that way but whatever. I'd say your schematic matches your physical wiring.
-
Now we are back to unhooking the low voltage wiring that goes to the outdoor unit if you haven't tried it already. If you have, we haven't heard what any of your findings were.
 
  • Like
Likes UrbanFarmEngineer
  • #59
Averagesupernova said:
Ok. Now we're getting somewhere. I would not want it that way but whatever. I'd say your schematic matches your physical wiring.
-
Now we are back to unhooking the low voltage wiring that goes to the outdoor unit if you haven't tried it already. If you have, we haven't heard what any of your findings were.

Sorry I haven't posted results. I have been so busy and tired that I thought if there was nothin to see in a particular place I'd move on. But I see now that I should have answered your question to keep you in the loop since I am asking you for help after all!

OK here is what happens with the condenser:
  • When the AC is connected and running the net current on the dedicated AC line and the dedicated furnace line are equal. nfurnace = ncondenser
  • When I entirely disconnect the AC the net current on the dedicated furnace line is the sum of what the average AC line reading and the average furnace line reading.
 
  • #60
> I'd say your schematic matches your physical wiring.

Do you say that the diagram I posted is equivalent to the manufacturer' wiring?
Help me understand. I can't see that. Would the path of current flow be the same in both?
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
1K
Replies
18
Views
2K
Replies
12
Views
3K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 23 ·
Replies
23
Views
3K
  • · Replies 6 ·
Replies
6
Views
5K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 5 ·
Replies
5
Views
11K
Replies
12
Views
3K
  • · Replies 6 ·
Replies
6
Views
7K