I was changing a light pendant today

  • Context: High School 
  • Thread starter Thread starter Emanresu
  • Start date Start date
  • Tags Tags
    Light
Click For Summary
SUMMARY

The discussion revolves around an electrical issue where a user measured 140V on a light circuit switch turned off, with the expected voltage being 230V in the UK. The user turned off the lighting circuit at the consumer unit, which brought the voltage down to less than 1V. Participants suggested that the high reading could be due to high impedance in the multimeter, allowing for voltage readings from capacitive coupling or inductive coupling between wires. It was concluded that if the voltage remains high under load, consulting a qualified electrician is necessary.

PREREQUISITES
  • Understanding of AC voltage measurement techniques
  • Familiarity with household electrical circuits in the UK
  • Knowledge of multimeter operation and impedance
  • Basic principles of capacitive and inductive coupling
NEXT STEPS
  • Research the operation of multimeters, focusing on high impedance effects
  • Learn about electrical circuit troubleshooting techniques
  • Study the principles of capacitive and inductive coupling in electrical systems
  • Review UK electrical regulations and when to consult a professional electrician
USEFUL FOR

Electricians, DIY enthusiasts, and anyone troubleshooting electrical issues in residential settings will benefit from this discussion.

Emanresu
Messages
53
Reaction score
0
and considered doing this with just the switch turned off. After turning off the switch I checked the voltage with a meter in A/C mode. It was 140V which I thought a tad high. When I turned the switch on the reading was 230V as expected (in the UK). So I turned off the lighting circuit at the consumer unit which brought the voltage to less than 1V as expected. So what I can't work out is where the 140V is coming from ? All the lights work independently so I don't think it is a series wiring thing.

Any ideas or trouble shooting tips ? This is the electricians forum isn't it ?

E.
 
Science news on Phys.org
I am not familiar with the types of circuits used in the UK, but if I saw a similar thing in the US (i.e., say 60VAC on a normal 120VAC line), I would be deeply suspicious of the neutral. In any event, that sounds like you need an electrician.
 
I have a CCF light that dimly pulses (only visible at night) every several seconds when supposedly switched off but still plugged in, so I presume it must be the same problem (my multimeter has a flat battery just now though).
 
Emanresu:
after turning off the switch I checked the voltage with a meter in A/C mode. It was 140V
If the meter measures 140V there is 140V. The meter has a high impedance ( 1M - 10 M ), so you need very little Amps to sustain that voltage.

If you put a low resistance, say 10 KOhms, in parallel with the meter, youll probably get a very low voltage. If this is the case its all OK.

This current can come from capacitance or coupled inductance between the wires.
 
Household outlets should be able to provide quite a bit of current without a significant drop in voltage. When I run my microwave the voltage drop at the outlet is less than 5V. The microwave uses about 600W so its impedence is only about 24 Ohms. If you can repeatably get measurements at about 50% of what is the correct voltage for the outlet, then I'd agree with tvp45 and say you need an electrician.
 

Similar threads

  • · Replies 22 ·
Replies
22
Views
4K
Replies
24
Views
3K
Replies
21
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 19 ·
Replies
19
Views
2K
Replies
20
Views
3K
  • · Replies 3 ·
Replies
3
Views
1K
Replies
152
Views
7K
  • · Replies 8 ·
Replies
8
Views
3K