Intercapacitance: Can it Cause 230 V Contactor to Latch Momentarily?

  • Thread starter Thread starter avrajesh1045
  • Start date Start date
  • Tags Tags
    Capacitance
AI Thread Summary
A pump failed to stop when the emergency push button was pressed, leading to concerns about intercapacitance affecting the 230V contactor. An electrical expert suggested that the distance of 30 meters between the contactor and the push button could cause momentary latching due to capacitance. However, others questioned this explanation, noting that AC systems typically wouldn't allow for such prolonged holding without mechanical issues. It was also suggested that the emergency stop button should be normally closed for safety, and that mechanical latching relays might be involved. The discussion emphasizes the need for a thorough circuit analysis and safety precautions before operating the pump again.
avrajesh1045
Messages
2
Reaction score
0
A pump did not stop when operator pressed the emergnecy push button. He ran towards another start/stop station and pressed the stop button. Even then the pump did not stop. After a while according to operator the pump stopped on its own. Electrical expert says that this can happen because of intercapacitance due to distance between 230v contactor and push button station. The distance was hardly 30 metre.
Can intercapacitance effect 230 V contactor to latch momentarily?

Rajesh
 
Engineering news on Phys.org
Before you can determine why the emergency push button did not work properly, you need to get a schematic of the circuit and the electrical properties of the components, and analyze it. Very roughly a cable has ~ 100 picofarads per meter of capacitance (depending on cable choice), or ~3 nanofarads for 30 meters. For safety reasons, the pushbutton switches should be normally closed (NC) and open when pushed. It would be safer if each pushbutton had a separate cable to the contactor, but they could be wired in series.

Bob S
 
You might question the 'expertness' of your expert.
Presumably the equipment runs on AC so it is hard to see how this 'momentary' holding-on could last more than 10ms (half a cycle of the mains). Also the time constant of any power circuit, loaded with an extra few nF is of the order of ns!
Could the delay be deliberately built-in for some reason?
It sounds to me that you could have something mechanically 'sticky' which is delaying the breaker from opening after the control current stops.
 
And since it is an emergency stop button that isn't working properly, I suggest the pump is not run until this is figured out. I hope nobody got hurt...
 
sophiecentaur said:
You might question the 'expertness' of your expert.
Yep!
 
It is possible that your pump is running on a mechanical latching relay, and not one that releases with a break in the relay coil circuit. See Fig. 3 in

http://www.eleinmec.com/article.asp?24

The relay shown in Fig. 3 is a SPST. You could use a DPST relay and use separate contacts for the holding circuit.

Bob S.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...