Investigating a faulty earthing in our house

  • Thread starter Wrichik Basu
  • Start date
  • Tags
    Earthing
In summary, there is a serious earthing problem in our house. The potential difference (PD) between neutral and earth is ## 50 - 60 ~\mathrm{VAC},## which should normally be ##< 2~\mathrm{VAC}## if earth is properly connected. I determined this with my multimeter after some appliances were giving electric shocks.
  • #36
Rive said:
Erm. I think that by throwing in DIY equipment for investigating a live line voltage electric network in unclear state we are treading on thin ice here.
Rive said:
I know that and I think I would be able to dig up mine from some boxes in storage: I'm myself also fine with extension cords with patched in current measurement (though I prefer clamps instead) but we are in the open here.
Please don't report the thread for high voltage safety issue. My multimeter probes are rated for 1000 V, 10 A max. I use proper safety precautions when measuring mains voltage.
 
Engineering news on Phys.org
  • #37
Wrichik Basu said:
I have a 15 W incandescent bulb. Connected it b/w earth and neutral. It didn't glow. (The 0.5 W LED bulb glows, however.)

PD before connecting lamp: 29.84 V
PD after connecting lamp: 30.12 V.

If you want me to get a bulb of lower rating, I will have to search for it.
Assuming the 15 watts lamp is not defective even though it does not glow indicates there is a significant leak someplace that is partially energizing the earth conductor since you measured voltage.
-
You didn't previously mention that the 1.5 watt was an LED bulb. These are not good for this type of troubleshooting.
 
  • #38
Averagesupernova said:
You may know that each earth pin is supposed to connect back to earth but do you really know the route? I would be familiar with how things are supposed to be done in the USA but what is the practice where you are at? In the USA the earth conductor is run in the same cable or raceway as the hot and neutral back to the source. If there is a broken earth wire in the raceway only devices downstream from that break will be affected. It's not spaghetti when done correctly. Based on your diagrams, I have to wonder about your system.
The earth wires from the rooms are joined to each other at the nearest junction boxes inside the house. These wires then finally meet at the main junction box, from where the wires descend downstairs. As I had said in post #11,
Wrichik Basu said:
It seems that the earthing wire(s) that go down from our house to the circuit board downstairs are somehow damaged or have got disconnected.
This is what the electrician will locate, if he concurs with my inferences.



Averagesupernova said:
You didn't say the 1.5 watt was an LED bulb. These are not good for this type of troubleshooting.
Please see post #11:
Wrichik Basu said:
Tried that with a 0.5 W LED bulb.
 
  • #39
In the USA, our answer would certainly be to leave this problem to a licensed electrician; trusting the electrician to follow codes. In India, that may be less practical.

However, I'm uncomfortable about recommending some of these DIY troubleshooting methods. I fear safety hazards. @Wrichik Basu is a valued member of PF. I would not want to see him hurt.

Is the advice given prudent?
 
  • Like
Likes Wrichik Basu
  • #40
anorlunda said:
In the USA, our answer would certainly be to leave this problem to a licensed electrician; trusting the electrician to follow codes. In India, that may be less practical.

However, I'm uncomfortable about recommending some of these DIY troubleshooting methods. I fear safety hazards. @Wrichik Basu is a valued member of PF. I would not want to see him hurt.

Is the advice given prudent?
Several things. @Wrichik Basu has been given sound advice here. Closing this thread will not likely stop him from continuing to investigate this. An electrician called in could potentially end with the electrician saying to replace the fridge, everything else is fine. You said yourself that in India getting an electrician may not be practical. That implies instead of @Wrichik Basu investigating this, someone less qualified does it.
 
Last edited:
  • Like
Likes Wrichik Basu
  • #41
artis said:
Well @Wrichik Basu , no offense but the pictures you provided show a rather dirty fuse box and the neutral and earth connections do seem oxidized and rusted outright, that can be a problem or part of it, but to know one would need to measure the contact resistance and visually inspect them thoroughly.
For the neutral, the company needs to be called. And they are least interested in these things. For the earth, I need to have a word with my neighbours. And I would shoot myself before trying to make them understand the issue.
artis said:
You could make a short cable with a wall type receptacle on one side and a wall type plug on the other side. Make it out of 3 wires, where you connect L to L, N to N and earth to earth, attach an ampere meter in series on each of the wires.
Then you can go around your house with all appliances disconnected and connect them to your ampmeter cable one at a time.
While a good way to find the defective device, I am a bit hesitant to follow this at this moment for the following reasons:
  1. My multimeter has a hall clamp (for both AC and DC), so I don't need to connect the multimeter in series. However, it's a lot of work, to be honest.
  2. I want to "preserve" the fault till the electrician comes in. If I rectify it, then I will not be able to point out that the earth is faulty.
  3. From my data in post #27, I believe we can rule out the refrigerator as a culprit, since there is not a lot of difference between the PD measured when it is plugged in vs. unplugged. (The fridge is also brand new, bought just a few months back…) All other appliances we own have a plastic body, so there is no chance of shock to the user (except that one immersion heater, which we unplug after use).
  4. Once the earthing is done properly, if some appliance breaks down by drawing excessive current into the earth and blows a fuse, let it do so. The house is well protected by properly rated fuses at different points. And it will be easier to locate it at that time.



anorlunda said:
In the USA, our answer would certainly be to leave this problem to a licensed electrician; trusting the electrician to follow codes. In India, that may be less practical.

However, I'm uncomfortable about recommending some of these DIY troubleshooting methods. I fear safety hazards. @Wrichik Basu is a valued member of PF. I would not want to see him hurt.

Is the advice given prudent?
I understand and appreciate your concerns. But in India, unfortunately, there is no such thing as a licence for being an electrician, let alone codes to follow. I really wanted to document the unsafe ways they adopt in their everyday work. Following advice from experienced users in PF is a lot better than letting them tear down each and every socket, trying to find a fault. I believe doing measurements with a multimeter (with safety measures adopted) and using a bulb won't cause a lot of harm. The rest is up to the mentors to decide.

I will be calling an electrician in the next few days, and hopefully, he will be able to solve the issue. Learnt a lot through this thread. Thanks, everyone, for your time and input!
 
  • #42
Wrichik Basu said:
From my data in post #27, I believe we can rule out the refrigerator as a culprit, since there is not a lot of difference between the PD measured when it is plugged in vs. unplugged. (The fridge is also brand new, bought just a few months back…) All other appliances we own have a plastic body, so there is no chance of shock to the user (except that one immersion heater, which we unplug after use).
I disagree here. If the appliance puts voltage on the earth conductor it should be considered defective. However, you may measure voltage that is capacitively coupled onto the earth conductor if it is not properly connected to earth. The same thing could happen if you toss a length of wire on the floor and measure the voltage on it relative to earth. BUT, that does not mean it can source any current. If it cannot source current, that means it won't shock you. Since you are getting shocked, something somewhere is defective. Having the bulb connected when doing the measurements indicated a voltage which means current can be sourced.
 
  • Informative
Likes Wrichik Basu
  • #43
Wrichik Basu said:
Please don't report the thread for high voltage safety issue.
I won't, but since we are in the open too many DIY ideas might leave no room for consideration for mentors.

Averagesupernova said:
If the appliance puts voltage on the earth conductor it should be considered defective.
Well, actually...

Many electronic appliances starting with an EMI filter like this:
Figure-2-EMI-Filter-and-Waveforms.png

With a broken PE connection this kind of filter will provide ~ half line voltage on the PE pin (and, consequently: on the chassis). Most common case is a PC hanging on a cheap, inconsiderately chosen extension cord, giving pricking sensation for any light touch.

With several appliances (on different phases) hanging on a common (broken) PE the voltage measured on the PE may be ... interesting.

I would prefer having a voltage measured between PE and water tap (if there are metal pipes for water there). With and without a (filament) bulb connected between them.
 
  • #44
Rive said:
I would prefer having a voltage measured between PE and water tap (if there are metal pipes for water there). With and without a (filament) bulb connected between them.
Let's not confuse this any farther. Measure the voltage between the points we know are not supposed to have voltage between them. I don't know if anyone here knows if plumbing is connected in any way in India or not. At least I don't.
 
  • #45
Averagesupernova said:
I don't know if anyone here knows if plumbing is connected in any way in India or not.
Old style (metal) water pipes usually works as reference. And with the official PE-ground connection in that shape (and without proper equipment) I see no other way to get an indication (not measurement! just indication) for the quality of the actual PE<>ground relations.

Ps.: honestly, based on the pictures, I feel like the pipes might be the most reliable stuff there 😨
 
  • #46
Averagesupernova said:
I avoid posting in threads like these because I always question the accuracy of the system as it is described.
Wrichik Basu said:
I am describing what the company had described to me the last time they came for an inspection (many years back, but nothing has changed since then).
Yes, but how do you really know that either they were correct or that nothing has changed? You (someone) needs to verify what's really there first.

I was an R&D EE at a company that made some complex high power electronic instruments. Occasionally I'd be asked to help troubleshoot systems on the manufacturing floor. They always fixed the simple stuff themselves, of course. I always started by asking them what was happening, what did they think, etc. Then I mostly ignored their observations and remeasured everything from the beginning. Almost always, they were assuming something that wasn't actually true, even though it should have been. Often the problem was simple once you got past the otherwise reasonable assumptions.

PS: sorry, I know that's what you are doing. But keep in mind the problem isn't so much the fix, the problem is understanding what to fix. It is so easy to lose sight of that. It was a frequent problem for me in the lab troubleshooting my own designs too.
 
Last edited:
  • #47
DaveE said:
Almost always, they were assuming something that wasn't actually true, even though it should have been.
Ding ding ding ding ding!
-
This is why we start troubleshooting at the place where measurements and function is working correctly and makes sense.
 
  • #48
When hot, the current through a 15 watt, 240 volt filament will be about 15 / 240 = 0.0625 amp. When cold, the resistance will be one tenth, so the current will be 0.625 amp. The cold filament resistance will then be about 240 / 0.625 = 384 ohms.

When Earth and Neutral are connected by the cold filament of 384 ohms, the voltage RISES from 29.84 V to 30.12 V. That is an increase of 0.28 volt.

I would immediately check the series connections in the Neutral supply.
How much of the E-N fault voltage appears across the Neutral fuse, and its poor connections?
 
  • #49
Baluncore said:
When Earth and Neutral are connected by the cold filament of 384 ohms, the voltage RISES from 29.84 V to 30.12 V. That is an increase of 0.28 volt.
Hmmm. I at first read this the opposite. But that does indicate a weak neutral. Unless @Wrichik Basu accidentally reported the readings to us reversed. I'd like a verification there.
 
  • #50
Averagesupernova said:
I'd like a verification there.
If it was a half volt drop, would it change the analysis?
 
  • #51
Baluncore said:
If it was a half volt drop, would it change the analysis?
Only if loaded/unloaded is repeatable.
 
  • #52
Wrichik Basu said:
... after some appliances were giving electric shocks...
Other than the immersion heater, can you list the appliances giving shocks.
And do they shock you if the immersion heater is unplugged?
 
  • #53
Baluncore said:
When Earth and Neutral are connected by the cold filament of 384 ohms, the voltage RISES from 29.84 V to 30.12 V. That is an increase of 0.28 volt.
Averagesupernova said:
Hmmm. I at first read this the opposite. But that does indicate a weak neutral. Unless @Wrichik Basu accidentally reported the readings to us reversed. I'd like a verification there.
The readings were fluctuating somewhat. But is 0.28 V really something you should be worried about? It may be a measurement error.
OmCheeto said:
Other than the immersion heater, can you list the appliances giving shocks.
And do they shock you if the immersion heater is unplugged?
My laptop is giving a tingling sensation. The metal parts of the refrigerator body are sometimes giving a tingling sensation. All other appliances are basically plastic or fibre glass body. I started investigating from the bathroom outlet, but later found that all outlets have this PD.

The immersion heater is giving shock independent of whether it is switched on or not. It simply has to be plugged in to the outlet, and you will start getting the shock.



My question, at this juncture, is, is it normal to have a > 28 V PD b/w earth and neutral at all times? When live-neutral measures 236 V, live-earth measures 182 V. Is this even normal?

You know what? I wouldn't be surprised if the electrician, at the end of the day, says, "That's very normal, I have seen it in other houses too."
 
  • #54
Wrichik Basu said:
My question, at this juncture, is, is it normal to have a > 28 V PD b/w earth and neutral at all times? When live-neutral measures 236 V, live-earth measures 182 V. Is this even normal?
It is not normal. It is dangerous.

Too much talk and not enough tests.
Measure the voltage drop across the fuse in the neutral line.

Somewhere nearby, the neutral will be earthed at a pole or a distribution transformer. Look for a bare copper wire running down a power pole. Can you find that place, or are the lines so unregulated that you cannot tell what has been done?
 
  • Like
Likes dlgoff and hutchphd
  • #55
Baluncore said:
Measure the voltage drop across the fuse in the neutral line.
It's negligible, ##\approx 0.003~\mathrm{VAC}.##
Baluncore said:
Somewhere nearby, the neutral will be earthed at a pole or a distribution transformer. Look for a bare copper wire running down a power pole. Can you find that place, or are the lines so unregulated that you cannot tell what has been done?
The wires pass under the ground, and they come up only at the local transformer and the houses. Other than, they are not visible anywhere, so I cannot visually see the link between the neutral and earth lines.

The PD between the neutral fuse (point D) and the earth lines (point E) is around ## 1.27~\mathrm{VAC}## (measured it today again).

Also wanted to mention one fact: if I connect the 15 W incandescent bulb b/w live and earth in our house, it does not glow at all. It's not faulty because it glows fine when connected normally between live and neutral, but does not glow when connected b/w live and earth or earth and neutral.

The 0.5 W LED bulb, however, glows when connected b/w live and earth, but with diminished brightness.
 
  • #56
Here are some more pictures of the region near our main fuse box (F1). Thought it might help illustrate the region more.



The wires as they enter our fuse box (F1).


The innards of the fuse box.

The PD between the joint on the side of the fuse box (where our green earthing wire joins with the second red wire) and the neutral is ##\approx 1.2~\mathrm{VAC}.##
 
  • #57
DaveE said:
Yes, but how do you really know that either they were correct or that nothing has changed? You (someone) needs to verify what's really there first.
The diagram I posted in the OP should be correct because, as I had noted, there are the electricity meters between the company fuse (A-C) and the fuses for each house (F1-6). I had omitted these meters for the sake of simplicity. Changing anything below and including the meter is illegal, and that is managed by the company only. We, as citizens, have the right to change things above the meter, i.e. from F1 and above that.
 
  • #58
Wrichik Basu said:
Also wanted to mention one fact: if I connect the 15 W incandescent bulb b/w live and earth in our house, it does not glow at all. It's not faulty because it glows fine when connected normally between live and neutral, but does not glow when connected b/w live and earth or earth and neutral.
By earth, you mean the PE line, right?

At this point it is just an assumption that PE is (still) properly connected.
Could you please make the measurement I requested from #43?
Be sure that during the measurement your computer is connected and working.
 
Last edited:
  • Like
Likes Lnewqban
  • #59
Rive said:
By earth, you mean the PE line, right?
What does PE mean? (Sorry, not accustomed to this acronym.) I meant the earth in the 3-pin outlet.
 
  • #60
Wrichik Basu said:
What does PE mean? (Sorry, not accustomed to this acronym.) I meant the earth in the 3-pin outlet.
That line is called 'Protective Earth' (PE for short). From the story so far I'm assuming that it's supposed to be connected to Earth at a specific point (and: to Neutral too), but that's only if the system is up to Code.

Since the system is clearly not up to any Code, to call it 'Earth' requires confirmation first.
 
  • Informative
Likes Wrichik Basu
  • #61
Rive said:
That line is called 'Protective Earth' (PE for short). From the story so far I'm assuming that it's supposed to be connected to Earth at a specific point (and: to Neutral too), but that's only if the system is up to Code.

Since the system is clearly not up to any Code, to call it 'Earth' requires confirmation first.
OK, so I took data at two different points, one in the kitchen and one in the washroom.

In the kitchen, the PD between the earth pin in the 3-pin outlet and the water tap was ##\approx 2.1~\mathrm{VAC}## while in the washroom, it was ##\approx 1.3~\mathrm{VAC}.## Note that these taps aren't directly touching the ground; they come down from the overhead reservoir.

For record, the neutral-earth PD at the time of measurement was ##\approx 14~\mathrm{VAC}.## Yes, previously I had been stating the value to be 28 VAC but it seems that the value deceases at night and again increases in the morning. I have noted this for two consecutive days. Edit: I was wrong. It later rose to ##31~\mathrm{VAC}.##

Also, does the fact that the incandescent bulb doesn't glow when connected b/w live and earth have any significance?
 
Last edited:
  • #62
Wrichik Basu said:
Note that these taps aren't directly touching the ground; they come down from the overhead reservoir.
Then this measurement was a dead end. Sorry.

The point would be to check the voltage on the PE line against some 'real' ground: against some metal pipes what comes up directly from ... ground.

If the PE line is properly connected, then no voltage is expected. If it is 'floating' then there will be some voltage due those EMI filters I mentioned somewhere before: but those EMI filters won't allow much current to flow, so the voltage would disappear when a bulb is connected.

For this measurement if the bulb lights up then the the whole network is dangerous and you should run and remove the fuses immediately, because not only the PE floating, but some faulty appliance actually feeding current to it - making the whole 'protection' of the network deadly.

Wrichik Basu said:
Also, does the fact that the incandescent bulb doesn't glow when connected b/w live and earth have any significance?
That experiment might also indicate a floating PE, but when executed with an actually floating PE, this experiment may create a life threatening danger through bringing PE (and all connected device chassis across the network) to line voltage.
 
  • Informative
Likes Wrichik Basu
  • #63
Rive said:
The point would be to check the voltage on the PE line against some 'real' ground: against some metal pipes what comes up directly from ... ground.
Unfortunately, I haven't got any such pipes inside my house. Such pipes are available in the basement, near the main fuse board. But there, I have already checked that the PD b/w neutral and earth connections is ##\le 2~\mathrm{VAC}.##
Rive said:
For this measurement if the bulb lights up then the the whole network is dangerous and you should run and remove the fuses immediately, because not only the PE floating, but some faulty appliance actually feeding current to it - making the whole 'protection' of the network deadly.
As I said, the ##15~\mathrm{W}## incandescent bulb doesn't light up, but the ##0.5~\mathrm{W}## LED bulb does. Probably if I can get hold of an incandescent bulb which is of very low rating, then that will light up.
 
  • #64
Wrichik Basu said:
...

Also, does the fact that the incandescent bulb doesn't glow when connected b/w live and earth have any significance?
I would say definitely yes.

Wrichik Basu said:
My laptop is giving a tingling sensation.
...
This is interesting, as I experience the same thing when I simultaneously operate my two metal cased MacBook laptops. One of them is less than a year old, and I seriously doubt there is an electrical problem with the other one. I may get out my O-Scope and see what's up with that.

And although I can't recreate it with my appliances, I remember that my mother's 1960's era stove and refrigerator gave the most entertaining 'tingle' when you touched them both at once, but not individually.

How old is your refrigerator?
 
  • #65
OmCheeto said:
How old is your refrigerator?
Brand new, bought a few months back. It doesn't always give the tingle as most of its body is made of non-conductive material, but sporadically, it does if I touch its back.
 
  • Like
Likes OmCheeto
  • #66
Wrichik Basu said:
I have already checked that the PD b/w neutral and earth connections ...
Please specify: did you check neutral to PE or neutral to ground?
Also, how sure you are that the PE in the basement is the same (=well connected) than the PE you have up?
 
  • #67
Rive said:
Please specify: did you check neutral to PE or neutral to ground?
Neutral to PE. If you refer to the diagram in the OP, point D to E.
Rive said:
Also, how sure you are that the PE in the basement is the same than the PE you have up?
Exactly. The PE wires in the basement give a potential difference of ##\le 2~\mathrm{VAC}## when measured against neutral (which is acceptable), but the ones inside our house have a different and much higher value. I believe something is messed up/snapped in the wiring between the basement and our house, and that is what the electrician has to find.
 
  • #68
Wrichik Basu said:
but does not glow when connected b/w live and earth
The neutral should be hard wired to the earth circuit somewhere. Enough to light a 15 W bulb. Or do I not understand British electricity? Comments please.
 
  • #69
hutchphd said:
The neutral should be hard wired to the earth circuit somewhere. Enough to light a 15 W bulb. Or do I not understand British electricity? Comments please.
According to wiki, Indian "Earthing is to be done with two separate connections."
My house here in the states has two separate connections.

Wrichik, what is your plumbing made of? Mine is a mixture of iron and plastic, with a copper jumper installed where a plastic piece fixed a broken '2nd earth section' iron pipe, many decades ago.
 
  • #70
OmCheeto said:
According to wiki, Indian "Earthing is to be done with two separate connections.
That's something interesting you found. So we do have some guidelines. That will be useful in the future.
OmCheeto said:
Wrichik, what is your plumbing made of?
Mainly metal pipes, but some joints have been replaced with plastic counterparts.
 

Similar threads

Replies
16
Views
2K
  • Electrical Engineering
Replies
13
Views
30K
  • Electrical Engineering
Replies
4
Views
3K
  • Astronomy and Astrophysics
Replies
33
Views
3K
  • Electrical Engineering
Replies
7
Views
11K
  • Electrical Engineering
Replies
9
Views
5K
  • Electrical Engineering
Replies
7
Views
3K
  • Electrical Engineering
Replies
2
Views
2K
Replies
33
Views
6K
Replies
10
Views
4K
Back
Top